Question about Goodman Heating & Cooling
Replaced cracked heat exchanger on Goodman gas furnace( model# GMPN060-3) main limit trips constantly. Temperature at limit reaches up to 250 degrees. Downflow application, clean evap. coil and no return air restrictions, HELP
  • 1,420 Answers
It may help if you increased the blower speed. It sounds like you have a restriction in either the return air duct or in the heat exchanger. Does it help to open the blower door panel. If so, you have confirmed a restriction. How do the burners look? Are they good and blue or yellow? Are the correct orifices being used for the type of gas? I know I am asking more questions than you, but it may help us with the answers. Good luck to you Wade.
Posted on Jan 31, 2010
  • 149 Answers
Check for proper temp rise do you have any restrictions in supply or return is your filter clean. the temp you described is way to much as cheap as goodman units are may be be better to replace the whole unit i have replaced those heat exchangers before never again . it far more easier to replace the unit.
Why do I always have to hit the restart button to make my furnace run
not sure exactly what you have or what button you are pressing but if you have a gas fired furnace and you are pressing the little buttons inside the furnace to get it to run, then you should stop doing that and have a pro come out and inspect it. Furnaces have limits inside them that will trip when they get to hot. In the case of a gas fired furnace a cracked heat exchanger can allow the flame to come outside the firebox, which will trip the limit which is a safety device. Limits only trip if something is wrong. They do not operate in normal operation. A cracked heat exchanger will allow carbon monoxide in the house which can kill you. That is why limits are installed to protect you. if your furnace is over 10 years old this could be the case.
Sep 10, 2014 | Heating & Cooling
Dayton gas furnace model 3e385 works and lights but as soon as fan comes on the unit shuts off and lights again wondering what was wrong
Check heat exchanger for cracks or holes which will cause the fan to blow out the flames. The flame sensor on the pilot or burners has to be in constant contact with flame to operate normally. If the flame is put out by a cracked exchanger the exchanger or furnace needs to be replaced.
Nov 22, 2011 | Dayton Gas Furnace Heater
Goodman dependable 92,7years old. Furnace works sometimes. Checked out by qualified technican. no problem found. Constant checks shows troubleshooting light blinks three (3) times. Help please. 3...
This indicates a open limit switch on the furnace, the heat exchanger is getting to hot therefore the limit switch is opening and not allowing the furnace to work properly. Did the techinician check the limit switch on the unit?
Dec 30, 2010 | Goodman GMS90703BXA Heater
Rollout switch continues to trip
If you have a cracked heat exchanger this will cause the flames to rollout and trip this switch. Its meant to stop the furnace from running and putting carbon monoxide in your home. Watch the furnace as it tries to light if when the gas valve opens and flame is established it should go into the tubes heat the heat exchanger and then your main blower motor will come on. When your main blower comes on is usually when you see the flames rollout and trip that switch. If this happens you can either buy a heat exchanger or new furnace if its a older unit Obama still has that awesome tax credit til 12-31-2010.
Dec 13, 2010 | Goodman Heating & Cooling
I have an early 80's mobile home with an "intertherm gas atmospheric furnace" pilot light is lit but can't get the furnace to "fire". Seems as though the limit control is stuck open. ...
If your pilot light is lit then I would first check your thermostat. Make sure it is on heat setting and fan is on auto, turn stat up to where it should be calling for heat. If you don't get burner to light remove front cover from thermostat and see if it has a mercury switch, if it does move temperature selector up and down and see if you can see a spark in mercury switch vial. If y ou cannot see a spark remove screws that attach t-stat to base.Remove carefully and disconnect wires that go to r and w terminals on stat base. Temporarily connect these two wires together. This should make burner light if you have power to thermostat. If burner does light disconnect wires and replace thermostat. Also if you have a volt meter check across these two wires and see if you have power there. Should be around 24 volts a.c. If your thermostat has a fan on setting try that. If fan runs you know you have power to furnace The gas valve needs 24 volts to operate and inside the electric control box in furnace there is a transformer to step down 110-120 supply voltage to 24 volts. If transformer is working you should be able to hear a low buzz or humming sound. You can also check across gas valve terminals when t-stat is set for heat, you should read about 24 volts. If you have 24 volts to gas valve and it is not opening then you need to replace gas valve. The main purpose of the limit switches is to turn blower on when temperature in heat exchanger reaches fan on temp,shut off blower after burner shuts off and heat in heat exchanger reaches fan off temperature, and limit if temperature exceedes set point without blower coming on. I hope this helps you. Thanks
Nov 25, 2010 | Heating & Cooling
My goodman furnace model gms95 has gone ape. when the thermostate calls for heat, the furnace kicks on and starts to cycle but it wont stay on long enough to reach the set temp, before it kicks off. and it...
It sounds like your furnace is cycling off because your high temperature limit is tripping. This could be caused by a restriction of intake or outlet airflow. First thing to check is your intake air filter, clean or replace as needed. If that doesn't help, make sure your warm air registers are open, a rule of thumb is at least 60% of the total registers need to be open for adequate airflow. The high temp limits will reset themselves after they cool so that would explain it taking a few "cycles" to reach desired temperature. Good luck and please rate my answer if it was helpful.
Jan 05, 2010 | Goodman Heating & Cooling
Cycling on limit
could be a faulty switch limit or cracked heat exchangers get a tech to inspect
Jan 01, 2010 | Heating & Cooling
Main blower stays on, burner fan on intermitantly,
All gas furnaces have a fan control of some sort. Either a mechanical fan control where there is a temperature probe that reaches into the heat exchanger compartment thru a hole in the panel that separates the control part of the furnace(this would be the front of the furnace where all the controls are) from the heat exchanger. This type of control is either a small black plastic control about 4 inches by 2 inches and about 1 1/2 inches thick secured to the panel with 2 screws. Or it is a slightly larger silver colored control that should have a pull off cover. It may say Honeywell on it. Either way the control will need replacing.
The other type of fan control is a solid state control board. This will most likely be located in the indoor fan compartment. It should be located under a covered control box. The box with all the wires going into it. This board will also need to be replaced if your furnace uses this type of fan control. You will need to bring your furnace model and serial number to a dealer that sells your brand of furnace or go online to a parts dealer that carries parts for your furnace. Hope I was of help to you! Good luck!
Nov 28, 2009 | Heating & Cooling
Goodman furnace went out. Light blinks four times
Your main limit switch is activated. Maybe for good reason. This switch keeps the furnace from overheating. I have the same problem right now and I think my a/c coil may be blocked, limiting air flow through the heat exchanger and the furnace. Does your gas and main circulating fan come on for a few minutes before the switch activates and the light begins blinking?
Check your furnace filter and any return air ducts in your home - see if they are blocked or restricted.
Jan 14, 2009 | Goodman GMS90703BXA Heater
Rollout Limit Switch Keeps Tripping
have someone check the gas presure most likely too high no more than 11