Question about Goodman CLQ36AR49 Air Conditioner
GOODMAN Air & Heating unit installed. After one and half year the heater would not egnite. Exhast fan starts but no ignition? Can anyone help?
  • 334 Answers
Either the pressure switch is not closing (probably clogged) or the ignitor is bad.
Verify that 24 v is coming out of the pressure switch, after the draft inducer motor comes on, then look for the ignitor to glow.
Do you see the glow from the ignitor? If not, replace it.
Posted on Jan 31, 2010
Goodman heating system
It really depends on the type of system you have. You will either have a furnace, high efficiency furnace, heat pump system, heat pump with gas or electric back up heat. All these systems operate differently and the problem that you are having could be caused by multiple issues, depending on which system it is. More info will be greatly appreciated. Make sure to check all filters and air flow first before going any further. The system could be over heating and tripping a limit, causing the system to stop producing heat until the unit has cooled back down.
Dec 06, 2013 | Heating & Cooling
I have a goodman unit with a copeland compressor Its in Montana and I only ran it three time since the install. Some times it starts right away and sometimes it try's three or four time before...
When you say Montana the first thing I thought was, does it have a crank case heater? Is it actually working? May need a start cap installed, need to check amps at start up, possibly nearing locked rotor. Fan works every time?
Dec 04, 2017 | Goodman Heating & Cooling
Goodman model gmt090-3b ignator is staying lit all the time cause them to burn out .have changed board same problem.
Hi cannot find the problem for this but go to www.goodmanmfg.com
you can e-mail and ask them from the web page hope this helps
it could be the presure switch playing up
Jan 23, 2010 | Goodman GMS90703BXA Heater
Heat kit on Goodman AC unit was working fine for past two years on occasional cold days. Just stopped working recently, clicks on but no fan on ''auto'';on ''on'' fan runs for a half minute then shuts off....
Disconnect the wires at the indoor air handler unit.
Make sure you remember where they were attached.
Put a jumper between R and G Terminals. Put covers
back on unit and turn power back on, the fan should
run.
If this does not happen and you have an electric meter, check to see that you have 220V at the
transformer,if you do then check to see if you have
24 volts on the secondary side of the transformer.
If you do-then.
On some units they have what looks like a car fuse
I think its 5 amp. Check to see if it is not blown.
These are installed in the circuit to help protect
the transformer in case of a direct short or an
overcurrent condition. I think this is probably your
problem if you cannot get anything to happen at the t-stat
Jan 09, 2010 | Heating & Cooling
Heater keeps going off on its on also fan not
Please provide more info. When it goes off does it come back on by itself or do you have to flip a breaker? Is the furnace gas or electric? If it is not moving enough air across your heat exchanger in a gas furnace or across electric heating elements this will trip a safety switch that will stop heating but not fan. Low air speed is most likely from inexperienced or improper duct design/ installation. Duct sizing is very important to move enough air. Don't believe me try breathing thru a straw. If your unit is a gas furnace it has a flashing code that will tell you what is wrong codes listed inside unit door. Could be lots of things. Reply with more info.
Dec 04, 2009 | Goodman Heating & Cooling
15 year old goodman heater is cycling. heating element glows red and the burners turn on for 20 seconds and then goes out. fan is in the on position . after the first light the element turns red but...
Sounds like the flame is either not traveling to the flame sensor or the flame sensor is dirty or bad. Look to the far left of the burner box for a probe near a burner. Lightly scrape and debris from the probe. The probe will have only one wire going to it. Do not touch the igniter or it will break.
Dec 09, 2008 | Goodman GMS90703BXA Heater
Amana ac/heating unit model PGD60C1152E
I need more info. Is this a split system, packaged, or ptac. Heat pump or electric heat strip?
Nov 18, 2007 | Amana Haier AP125HD Air Conditioner
No heat, trouble shooting light has continious flash.
There is a vacuum sensor on most units tied from the exhaust gas fan to the sensor. Does the unit try to start? If the unit's exhaust fails to pull the switch it will turn off after about 30-45 sec after starting. "IT" thinks it's not exhausting and stops to keep from overheating. Do you have this exhaust fan and rubber hose to sensor? Can you see if that fan is turning on start?