HI i think my split system compresser has locked up when the outdoor unit enguages it hums then the fan cuts in for 2 sec then it drops the curcit breaker i disconected the power wire to the compresser and the fan ran fine didnt trip out so im prity sure it th compresser is there away of unlocking them or could it be somthing else? and what causes them to lockup.
Anonymous
Level 2:
Novelist:
  • Expert 117 Answers
  • Posted on Jan 25, 2010
Anonymous
Expert
Level 2:
Novelist:
Answers
117
Questions
0
Helped
35012
Points
261
If your compressor is showing signs of seizing up or locked as its commonly known, the first thing you want to check is your start components. Be sure that your start components are operating properly.
Check your start capacitor as well as any start relays. If the capacitor is weak or the relay will not disengage after start-up, these could cause a breaker to trip or a compressor to draw LRA (locked rotor amps)
If your compressor is locked up and drawing LRA, you can attempt to break it free by the use of a start capacitor, a hard start kit, or a 5-2-1 kit. The hard start kit and 5-2-1 are the most common practices in the field.
A compressor locks up for a few reasons. The most common issue is lack of oil. This could be caused by a failure within the compressor itself. It could also be caused by a refrigerant flow issue, whether it be a low charge or pressure problems caused by failed metering devices.
Some compressors are weak, especially in the colder weather. And the use of a start component is required for start-up. While this is a rare problem, it does happen.
The use of an amp meter will tell you where to start looking. LRA ratings can be found on the unit dataplate.
Testimonial: "Thanks mate!"
Terry Rodgers Jr.
Level 2:
Scholar:
  • Expert 131 Answers
Terry Rodgers Jr.
Expert
Level 2:
Scholar:
Answers
131
Questions
0
Helped
36561
Points
336
Its quite possible it could be the start cap,(if the unit was running fine before) Your gonna want to check the connections to the cap first,(with the disconnect turned off first) If the connections are fine,you can install a booster capacitor To see if that won't kick it off.
Testimonial: "thanks"
H5 ERROR CODE IN BLUE STAR SPLIT INVERTER AC
The H5 error code in a Blue Star split inverter AC typically indicates that there is a problem with the outdoor unit. The outdoor unit is the part of the air conditioning system that is located outside the building and is responsible for releasing the heat absorbed from the inside of the building to the outside.
There are a few possible causes of the H5 error code:
  1. The outdoor unit's compressor might be malfunctioning. The compressor is the most important component of the outdoor unit and is responsible for compressing and circulating the refrigerant.
  2. The outdoor unit's fins might be dirty or obstructed. The fins are the thin metal blades that are responsible for releasing the heat absorbed from the inside of the building to the outside. If the fins are dirty or obstructed, the heat exchange process will be impaired, resulting in the H5 error code.
  3. The outdoor unit's fan motor might be malfunctioning. The fan motor is responsible for turning the fan blades that circulate the air over the fins. If the fan motor is not functioning properly, the H5 error code will be displayed.
To troubleshoot the H5 error code, you should start by checking the outdoor unit for any visible signs of damage or obstruction. If you do not see any obvious problems, you may need to call a professional HVAC technician to diagnose and repair the issue.
H4 error code is shown on AC display what can i do to slove this problem
Full list of Gree Air Conditioner Mini Split Units Fault Codes. When error codes appear on the Gree air conditioner indoor display, this tells the user there is an issue with the Gree AC unit. The error code displayed will inform you of the issue or problem that is occurring with the air conditioner. Knowing what the error code means and its definition will help you to understand and troubleshoot the exact Gree air conditioner part that needs to be fixed, cleaned, repaired, or replaced. You can then clean, fix, or replace the Gree part yourself and save money. See below for all error codes that can occur on Gree Mini Split AC's.
Gree Mini Split Air Conditioner Error Codes - How To Fix
Gree Viero AC Mini Split PDF Owners and Troubleshooting Manual
GREE DUCTLESS AIR CONDITIONING & HEATING SYSTEM INSTALLATION MANUAL
Gree Mini Split Air Conditioner Part Names and Locations
INDOOR AND OUTDOOR UNIT
The Gree Air Conditioning Vireo System has onboard error code diagnostics. The outdoor unit will provide status indicators and the indoor wall unit and remote control will display error codes. The following is a summary of the codes with explanations...
GREE AC DIAGNOSTIC ERROR CODES
Gree Vireo Mini Split Air Conditioner Error Code F0
Refrigerant Leakage Protection
1) Refrigerant leak(s).
2) Indoor coil temperature sensor not calibrated.
3) Refrigerant flow is restricted (ex. valve, exv, debris)
Outdoor Unit Red Light Indicator - 9 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E1
System High Pressure
1) Over charged with refrigerant.
2) Blocked or dirty outdoor coil.
3) Extreme outdoor ambient conditions
Gree Vireo Mini Split Air Conditioner Error Code E2
Indoor Anti-Freeze Protection
1) Low return airflow.
2) Indoor fan speed is too low.
3) Indoor coil is blocked or dirty.
Outdoor Unit Yellow Light Indicator - 3 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E4
Compressor High Discharge Temperature Protection
Please refer to the malfunction analysis (discharge temperature, overload) in service manual.
Outdoor Unit Yellow Light Indicator - 7 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E5
Overcurrent Protection
1) Supply voltage is unstable.
2) Supply voltage is too low and system load is too high.
Outdoor Unit Yellow Light Indicator - 5 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E6
Communication Malfunction
1) Communication cable is wired incorrectly between indoor and outdoor units.
2) Indoor or Outdoor control board malfunction.
Outdoor Unit Yellow Light Indicator - Continuous On
Gree Vireo Mini Split Air Conditioner Error Code E8
High Temperature Resistant Protection
1) Incorrect refrigerant charge level.
2) Refrigerant metering device malfunction.
3) Compressor malfunction.
Outdoor Unit Yellow Light Indicator - 6 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code EE
EEPROM Memory Malfunction
Control board malfunction.
Outdoor Unit Yellow Light Indicator - 11 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code C5
System Configuration Malfunction
1) No jumper cap inserted on the control board.
2) Incorrect or damaged jumper cap on control board.
3) Indoor and outdoor units are not compatible.
Gree Vireo Mini Split Air Conditioner Error Code Fo
Pump Down or Gathering Refrigerant Status
Optional Service Mode
Outdoor Unit Yellow Light Indicator - 17 flashes and 1 sec Off
NOTE: All of the Gree Air Conditioner Model Numbers below are applicable for the error codes on this page...
Gree AC Vireo Models: VIR09HP115V1A, VIR12HP115V1A, VIR09HP230V1A, VIR12HP230V1A, VIR18HP230V1A, VIR24HP230V1A, VIR30HP230V1A, and VIR36HP230V1A.
Gree Mini Split Air Conditioner Error Code Charts
Gree Mini Split AC Remote Control Button Names
Gree Mini Split AC Remote Control Icons Display Screen
Gree Mini Split Air Conditioner Air Filter Cleaning Procedure
Need help with error codes on your Gree AC? Please leave a question below and we will be happy to help.
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Cond fan motor runs for about 10 sec then cut off
sounds like it is getting hot need get a can of conpressed air and blow it out.
1helpful
2answers
F95 error code - outdoor high pressure rise protection
This depends entirely on the environment you have your unit situated in. I would suggest getting a properly qualified and licensed technician to check your unit and see if it is working correctly in the environment you have it in. Maybe some adjustments for your climate are required.
2helpful
2answers
I have a samsung split system it's just shows error 6 and dosen't work .. It's the perpendicular style.. Please answer my question ...
Fault code. 6. From what I have read 1 of 2 items. The unit has completely lost freon charge. Or 2, outdoor has overheating problem, ie. condenser fan motor not running
Hi, I have a Daikin Model FTXS35D with RXS 35D 3VNB outdoor unit. Until this year it was excellent, now does not cool as before. Have cleaned filters etc. Could it be a sensor problem. When I...
Your unit should cool 15 to 20 degrees. 75 return air temp should be below 60 degree supply air temp. If you are not in this range you likely have a refrigerant problem.
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
Hi i have a lg split system air con model number lst243h-2 its nice and cold when i first turn on then its just like the fan is on its not cold at all
How long before it goes from cold to hot. The compressor could be not running and going out on overload. The condeser fan could have failed. Did you check the outdoor unit. Is it running? Is the fan running on the outdoor unit. It could be low on charge which would cause ice. Are you getting excessive condensation? Let me know and i can help you out more. Grab the large copper line outside that is insulated and tell me if it is cold. It should be cold like a Pepsi out of the fridge!
Unit is running, but is no longer cooling. Fan is blowing, but air is not chilled (or cold). Unit has been running fine until a couple days ago. It has been turned off for the last 12 hours and tried...
not sure if it is a package system or a split but this is what you do.go outside where your outdoor machine is, after it has been shut off for awhile, and you should hear 2 distinct noises.1 is the outdoor fan, you should see it spinning.the other is a comppressor hum.some compressors have noise bags on them so listen closely thru the fan noise.if you hear no hum listen for a hum about every 2 to 5 minutes.if you hear this hum every so often, chances are you compressor is seized or stuck.the only thing to do there is get a tech and try a big boost to get it going.
Top Heating & Cooling Experts
Paul Carew
john h