Blower opperation on gas furnace
I have a model 58GP100JA the control board PT# HH84AA020 has just been changed for the second time. The A/C side of the unit work fine but when changed over to heat the burner will come on but the blower will not. When it appears that the high limit breaks the gas valve then the blower will come on. When the blower quits the burner will come back on. On the insert that comes with the control board it mentiones a jumper between Gas 1 and Gas 3 on the original board that needs to be placed back on the replacement board. There was no jumper on the board that I changed out so there is also no jumper on the new board. Would this jumper correct my problem.
  • 614 Answers
How long does the burner stay on before the limit takes it out. The board has a delay for the fan in heat and it may be to long. If your unit had cycled on high limit to much it may have a bad limit switch. The limit is so low it cuts out before the fan has a chance to come on. See on the board if has an adjustable time deley. Should 30 60 90 set to thirty. Keep in touch rus
Posted on Dec 13, 2009
I have a Bryant gas furnace model 394GAZ036125. After a heating cycle, blower motor shuts off, then cycles 2 times for approximately 2 seconds each cycle. What could be wrong ?
It's probably something going on with the limits. If the limits open, the control board assumes the unit has overheated, and brings on the blower to cool it down. Check all limit connections. As well as the connections on the board. Limits are the least expensive so you are right in changing them first, and there should be more than 1/ see schematic. If not the limits then it may be the control board but in 15-16 yrs I've not seen that. Might try(safely), wiggling the control wires at each limit, or tapping them with the end of a plastic handle, and trying to simulate a fault. Hope this helps!
Oct 19, 2017 | Bryant Heating & Cooling
"On" position blower shuts off when gas turns on, replaced control board, no change.
Really need more info but with what you have stated: many furnace blowers are set up to simply run the blower after a set time.
Yours is not doing that and is in a very unsafe condition. Only thing keeping your furnace from burning until it glows red hot is the over temp safety.
With the info provided I would suggest you replace the furnace control board and the abused safety. Verify blower operation before you call it fixed.
Sep 12, 2017 | Heating & Cooling
Furnace wont work
Have to know the model and serial of the furnace.
locate code list usually inside or on the back of a door.
Operation sequence= call for heat--inducer blower motor--makes pressure switch--signals board to bring on hsi--after a set time gas valve opens and you have ignition--main blower motor comes on after a set time
Feb 14, 2014 | Coleman 7990-319p Evcon Gas Furnace...
Coleman evcon furnace
How old is your furnace? Does it have a circuit board that controls everything, or are there separate controls for each function?
Nov 19, 2013 | Heating & Cooling
Thermostat calls and from time to time won't ignite
I would first look at any wire connections both at the furnace and the thermostat. Then I would replace the thermostat. Check the units control board when it does not start for an error code. There should be a small viewing port to look into the furnace cabinet to see the control board.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Feb 12, 2010 | Goodman Heating & Cooling
Model #GMPN100-4 Goodman furnace. Vent fan
The sequence of events for furnace operation is -
Fan purge for 30-45 seconds. During this time, a pressure switch is actuated by the running of the purge fan, proving the control board the purge fan is running.
After purge and purge prove, the hot surface ignition and or spark begins. After a few second delay, the gas valve will open. The control board then monitors for flame prove through another sensor located near the burners. If there is no flame within 3-5 seconds, the gas valve closes. It will repeat this process, usually 3 times, before it shuts the system down, which requires a power down of the system to reset.
I have seen trash get into the hose between the purge blower and the purge switch. But you could be having other problems.
Dec 17, 2009 | Goodman Heating & Cooling
Central heat gas furnace lights and works for 10 seconds , does t
replaced flame sensor and still had same problem so I had to replace main control board 350$ and it is working great.
Jan 15, 2009 | Central Dual Temperature Heat Gun Kit...
Goodman GMP075-3 ignition problem
bad board,i have had several board failures on goodman
Dec 18, 2008 | Goodman GDS80904BNA Open Flame Heater
Blower works but no heat
If in fact you have the above listed furnace, you do not have a pilot but electronic ignition. You will need to remove the front cover on the furnace, tape down the door safety switch and then have someone help you by turning up your thermostat to a very high setting. Watch and listen inside the furnace. There should be some blinking going on at the control board followed by a small blower fan starting up. Then after 10-15 seconds there should be a click followed by an orange glow viewed thru the viewing window to the burner section. In a few seconds the gas valve should click and the burners will ignite. There is a safety switch that will sense flame and then keep the gas going to the burners. If it does not sense it, it will shut it off within 10 seconds. If all is well so far, your blower will turn on in about 90 seconds after flame. There is a diagnostic code chart on the back side of the access door if you get an error code (blinking) on the control board.
Always check little things like air filter, condensate drain and broken or loose wires.
Nov 05, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
67 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Mack Baxter
Marvin
Marvin