Powerware 9120 BUS Unbalanced error display
Got an Powerware 9120 and displays constantly ''BUS Unbalanced'' and when the external power cuts off, there's no electricity anymore... it won't work.
Do I have to replace batteries? some cap toasted?..
Help please?
Thanks a lot
    Scholar:
  • 39 Answers
The user's Guide for the PW9120 handles 700-3000va - this is the complete range for the PW9120. It does not list a possible alarm of "'BUS Unbalanced''. Unless your unit is a European version, it will be 120 input and output and will have only one inverter internally.
Get the manual or download the full manual from the Powerware site. Go through the UPS settings to ensure they match the factory settings. (By the way, the factory setting for the Input Voltage Frequency should be +/- 5%).
If all the settings are correct, you have may have dead batteries. What does the display show you for battery charge % and battery backup time? If your individual battery voltages are less than 11 volts, your batteries are dead. Test at the battery output connector at the back of the UPS. 9120-700 2 batteries, 9120-1000 3 batteries, 9120-1500 4 batteries - all in series, so the 12 volt battery bus voltage is additive. Use PowerSonic PS-1290 F2, rated at 9.0 Amp. Hr. for the best battery replacement.
Posted on Feb 08, 2011
  • 4 Answers
I've had this same issue what it boils down to is that the Power IN is not being distributed properly across the Power Outlets.
Step 1. unplug everything from the unit and power the ups down. If the alarm clears itself the UPS is mostly likely fine. if it doesn't not clear send it in for repair
Step 2. If step 1 cleared the alarm try distributing the decives across the outlets differently.
There are two inverters so two output if everything is plugged into one side (ie a power bar with 10 things plugged into it) and nothing on the other side this could cause the alarm.
hope this helps
Posted on Feb 18, 2010
  • hellwigg Oct 06, 2010
    The 9120 does not have two inverters. There are two sets of input terminals and one set of output terminals. It has one rectifier and one inverter.
    I have had a bus unbalanced alarm a few times and output power is lost. It has nothing to do with two inverters.
I got charger failure alarm on display.
Unless new and hardly used - check the internal batteries. They might be worn out and fail to hold a proper charge. This to be able to deliver power when AC mains cuts out.
Jul 04, 2011 | Powerware 9120 UPS System
I have a powerware 9120 (6kva) and about 1 week i replaced all 20 batteries after the UPS failed. but its displaying battery disconnected when i try to power it. i cant seem to figure the problem. i tried...
Did your UPS display "Battery disconnected" or did it display "Battery Failure"? If it was "Battery Failure", for some reason the Powerware 9120 will take almost 18 hours after plugging in to power after battery replacement to correct the Battery Failure indication. Charger has to charge up the batteries, followed by an automatic battery test by the UPS. If the indication was "Battery Disconnected", you will need to check the internal fuses to see if they are blown. If the UPS keeps blowing fuses, it will require a board repair.
Jun 12, 2011 | Powerware 9120 UPS System
When i power on the ups it show site fault on the display,i checked the earth wire is ok . what can it be a problem?
Hi, here is the documentation page for the 9120 where you can find the manual: http://powerquality.eaton.com/Products-services/legacy/9120-info.asp You can also contact customer support 800 356 5737 or SinglePhaseTS@eaton.com. You may recognize the product as the Powerware 9120 but Powerware was bought by Eaton a few years ago. The customer support team is most ex Powerware and are familiar with the 9120.
Oct 14, 2010 | Powerware 9120 UPS System
My ups has is faulty i need a circuit diagram to fix it
I had a DC bus fault error displayed.
So I unplugged battery, then turned on UPS. It said Batt disconnected of course.
So when I plugged in the batt while the UPS was on, and held the power button for a few sec, the UPS displayed Batt testing.
After a few moments it was back online and had no faults!
Worth a shot.
May 20, 2009 | Powerware 9120 UPS System
The UPS dont go to on batteri
Replace the batteries with new one then power the UPS without load for three hours or more so that the batteries can be charged. Then disconnect or switch off power to the UPS and observe if it will till be on using the batteries. If it will be ON then your problem is solved but if it goes off then your UPS is on BYPASS
Apr 09, 2009 | Powerware 9120 UPS System