Question about Intertherm P3RA-048K Air Conditioner
Ive replaced the limit switch and fan switch but fan continues to cycle on and off in 30 sec. cycles
  • 81 Answers
Bad condsr motor
Posted on Dec 11, 2009
Furnace blower cycles on and off every 30 seconds .the flame stays lit. Already changed both fan limit switchs Made no diffrence
check pressure switch and hoses .Check air filter is clean check for any loose connections
Feb 21, 2018 | Heating & Cooling
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
No ignition
Restart the unit as soon as you see the inducer fan on jump the 2 wires the pressure switch. Your burner should stay on and go through it sequences. If it go through it that pressure switch need replace and make sure your inducer pull under the vaccum of the pressure switch.
Feb 04, 2014 | Goodman GMS90703BXA Heater
I have 2 hvac units running an electric heating element for the heater. Both limit controls are set the same. One is ignited the flames and continuing with flames for close to 3 min. The other is taking...
Hi, these Honeywell combination fan/limit controls are used for turning the fan on after the combustion changer reaches the factory setting on the round dial that you see when you remove the cover. The high limit will turn the fan on when it reaches this temperature, and off when the stat is satisfied. If the blower motor fails due to a burn out or short, it shuts the main burners down on the high limit setting. These controls can be removed and you can clean the probe which has a set of contacts at the end. Sometimes this will fix the problem. Check the settings on the dial to see if they are set right to come on, the time it takes between cycles, and the temperature they are set to shut off. This sounds as though you need to check your thermostats also. They could be a problem. You say electric heat, but then you are saying flames? If these limits have the manual fan button, make sure they are on auto. Long delays could also mean you have a dirty flame sensor located by the pilot. You can clean the metal tip with steel wool or fine sanding cloth. Short heating cycles may be your thermostats like I said before. You shouldn't have to replace the fan/limits as I told you what they control. These will cause a fan to run and not shut off after the stat is done, so check to see if they are dirty. Please keep me posted.
Shastalaker7
A/C, & Heating Contractor
Feb 12, 2011 | Honeywell L4064B2236 Fan/Limit Control...
Starts up and runs for 30 sec. and stops.yes it has fuel
find the high limit switch an replace or see if fan runs if fan runs then the limit is bad replace
Mar 15, 2010 | Reddy Heater-30-55,000 BTU Variable
Maytag dryer ldg7500 - gas continually turns on & off, no heat
Could be a number of things....
The ignitor is bad and it will not keep pulling enough current to hold the gas vavle on.
The dryer cycling thermostat is bad and is cycling it too often...ie, shutting the gas valve down too soon before it can run long enough and then turning it right back on.
The vent is blocked or plugged and the air gets too hot to fast.
The high limit switch has gone bad doing the same thing as if the cycling stat goes bad.
Fan/blower is bad and bot moving enough air...same symptoms as blocked vent...
Need to start eliminating the possiblities one by one...
http://www.fixya.com/support/r3907570-buy_appliance_parts_online
Heatman101
Jan 20, 2010 | Dryers
Honeywell thermostat TH6110D1021. Blower comes on
Hi, You are right, fan is on a time delay in the heating cycle, and after burners fire that is when this delay comes into play. You have a preset factory temperature that determines the cycle on time for the fan, and the off time after the burners shut down also. This will not be in the thermostat, but in the fan/limit control the is mounted on the face of the furnace, with a probe inserted into the fire box.Depending on how old or new this unit is, will depend on the type control you have.It may be just a high limit switch, or the 1st I mentioned.If so, It rotates in the burner as the temperature rises, to turn the fan on and off.Disconnect power, remove cover, and 2 screws.Slowly remove the control and gently clean the probe. Turn the dial if this one has it and you will be able to hear it click. This click is contacts closing to start fan operation.Reinsert and try again. If problem continues, you will have to replace it.They do tend to stick closed/on, in the heat cycle from time to time and a cleaning sometimes will solve this problem. Not knowing how old this furnace is and type, make it difficult to give you a correct diagnosis, so check this fan control as I have explained, and if your system is of a different type, please let me no so I can correct this problem. Sincerely,
Shastalaker7
Dec 11, 2009 | Honeywell Programmable Thermostat Heater
Dishwasher problem
If the cycle doesn't complete, check these:
1. Water-heating cycle
2. Timer
Water-heating cycle
Many dishwashers heat the wash and/or rinse water to a higher temperature, as the cycle calls for it. In these cycles, the dishwasher pauses after it has filled with water, waiting for the water to reach the pre-set temperature. What happens next, depends, as follows:
On some units, the pause is timed and the unit continues after the allotted time.
On others, the cycle can't continue until the water reaches the higher temperature. If you have this type of dishwasher and the water isn't being heated (say, because of a problem with the heating element or thermostat), after the unit stops at the heating cycle, it never continues. When you repair the heating-system problem, the "cycle problem" is fixed too.
Timer
Timers don't often fail. But if every other part of the dishwasher seems to be working properly and the timer knob seems to be stuck in one place--doing one function continuously--the timer may be at fault. Dishwasher timers can't be repaired. If yours is defective, replace it.
 thanks for using FixYa
Feb 10, 2008 | Kenmore 65924 Electric Dryer
Turns on...ok for 30 sec, then turns itself off
Lampmay be going out. Look down inside of lamp, if there is a foggy look it may be going out. Also check to see if the fan is working.
Jan 15, 2008 | Hitachi 50V500 50 in. HD-Ready LCD...
Ptac fan keeps blowing
Try setting the fan control to "AUTO" this will cause it to cut out with the compressor.
May 02, 2007 | Amana PTH123B25AJ Heat Pump Air...
Intertherm P3RA-048K Air Conditioner Logo
62 people viewed this question
Top Intertherm Heating & Cooling Experts
Dennis Boxerman
Bill Long
Rachid Ayachi
Rachid Ayachi