Question about Honeywell Programmable Thermostat Heater
Honeywell thermostat TH6110D1021. Blower comes on
Honeywell thermostat TH6110D1021. Blower comes on when heat is called for and furnace ignites 10 seconds later. Call for heat should turn on burner motor, ignition in 10 sec. then blower in 75 sec. is the way it should run. How to set thermostat to get blower to come on after the 75 seconds instead of before ignition. Have checked system type 1 as 0 and 3 as 0.
    President:
  • 1,515 Answers
Hi, You are right, fan is on a time delay in the heating cycle, and after burners fire that is when this delay comes into play. You have a preset factory temperature that determines the cycle on time for the fan, and the off time after the burners shut down also. This will not be in the thermostat, but in the fan/limit control the is mounted on the face of the furnace, with a probe inserted into the fire box.Depending on how old or new this unit is, will depend on the type control you have.It may be just a high limit switch, or the 1st I mentioned.If so, It rotates in the burner as the temperature rises, to turn the fan on and off.Disconnect power, remove cover, and 2 screws.Slowly remove the control and gently clean the probe. Turn the dial if this one has it and you will be able to hear it click. This click is contacts closing to start fan operation.Reinsert and try again. If problem continues, you will have to replace it.They do tend to stick closed/on, in the heat cycle from time to time and a cleaning sometimes will solve this problem. Not knowing how old this furnace is and type, make it difficult to give you a correct diagnosis, so check this fan control as I have explained, and if your system is of a different type, please let me no so I can correct this problem. Sincerely,
Shastalaker7
Posted on Dec 11, 2009
Honeywell thermostat won't turn on
There could be a number of issues associated with this issue. #1 bad thermostat, #2 no low voltage from the furnace or air handler, #3 if gas furnace, no pilot(standing pilot units or bad ignition system). If you have a fan switch on the thermostat turn it to on and see if the blower comes on. I would also check to make sure the breaker is turned on. Over the years I have found many things that all have the end result you are seeing. I just named a few things you can try.
Feb 14, 2015 | Honeywell T87K1007 The Round...
When i turn the heat up sometimes it takes a long time for the gas furnace to start ..why?
Watch your furnace when you turn the thermostat up...make sure to record everything that it is doing. If you have an induced draft, forced air system, then the heat sequence of order should go like this... Initial call for heat from tstat, Inducer vent motor turns on-pulls in the pressure switch, circuit board sends power to igniter whether it is spark or hot surface, then gas valve opens. Flame sensor senses flame, burner stays on, and blower motor kicks in to heat the space. If you notice any variance from this, then something needs to be checked by an HVAC Service Tech.
Dec 14, 2013 | Honeywell Programmable Thermostat Heater
Replacing Goodman Furnace B18099-26 with ICM286 fails
decouple the output of the pcb ,put a 10-100nf between the two connectors
Nov 06, 2013 | ICM286 Furnace Control Board
I JUST INSTALLED HONEYWELL TH6110D1021 THERMOSTAT FOR A STEAM ZONE VALVE. I SET THE THERMOSTAT FUNCTION BY PRESSING THE UP ARROW AND FAN BUTTON. THEN CHANGING THE RIGHT NUMBER TO 2. NOW I WANT TO CHANGE...
Hi and welcome to FixYa. I am Kelly.
Suprizingly enough there is an abundance of manuals for your Honeywell Programmable Thermostat. Use this link and at the bottom of the page you can download any of the manuals.
http://customer.honeywell.com/Honeywell/ProductInfo.aspx/TH6110D1021
Just note that pop ups must be enabled to download the manuals
Printable Quick Reference Sheet (after download)
http://customer.honeywell.com/techlit/pdf/PackedLit/69-1778ES.pdf
Thanks for choosing FixYa,
Kellly
Oct 15, 2010 | Honeywell Programmable Thermostat Heater
I installed a honeywell CT87N thermostat. The
the burners light? if the burners dont light than it's working right the blower on the furnace comes on with the a\c
Jun 19, 2010 | Honeywell Electronic Programmable...
Furnace cuts off before reaching set temp.
You can make sure it is not the thermostat by crossing or jumping the R and W terminals (or associated wires) together. This will keep the furnace calling for heat. As it is approaching set temperature, get in front of the furnace and inspect the air filter to make sure it is clean, watch the control module for any error codes that may be turning off the system prematurely.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 07, 2010 | Honeywell Programmable Thermostat Heater
No heat after installing honeywell thermostat H8110U
hook up the blue wire in the furnace cabinet where the blower section and the other thermostat wires are connected to the furnace. the thermostat you have uses a common wire from the thermostat to the furnace and this needs to be hooked up in the furnace otherwise you will have the problem you are having.
Dec 07, 2009 | Honeywell Electronic Programmable...
New thermostat honeywell RTH7400 cycles oil furnace every 10 min.
rth7400 maintains a 1 degree differential in temp so 10 minute cycles are not unusual.
Vinnie
Jan 02, 2009 | Honeywell Programmable Thermostat Heater
Furnace comes on and off
If fan is set to auto mode that's how it will work.Fan would only run when heat is on
Feb 18, 2018 | Heating & Cooling
Heating & Cooling Logo
357 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
Paul Carew
vance jones
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others