Thermostat LCD is blank and a/c does not run--believe problem is loss of 24 vac from unit transforme. where is 24 vac transformer physical location and how do I check it with a voltmeter?
  • 3 more comments
  • mtsuo Dec 11, 2009
    this is a Goodman CLT48-1B central a/c unit with a Honeywell T8001C thermostat. In its configuration, there is no internal battery for the Honeywell thermostat, rather, this type draws it power from the 24 vac transformer on the system----somewhere???
    I need to locate the 24 vac power source---I think it is on the condenser--and check to see that
    the voltage is being delivered there.
    Can you help me by telling me where the pick-up point for this 24 vac source is physically located?
    And how do I measure its output using a multimeter(I know the basics of using one)
    thanks
    jyackle5
    according to the troubleshooting T8001 chart, NO DISPLAY indicates NO POWER TO THERMOSTAT. It says check that TERMINAL C is connected to system transformer
    I need to know where that 24 vac transformer is physically located.
    thanks
    jyackle5
    i took a multimeter to the thermostat mounting wallplate wired connections---there are 4 18 guage leads, and I measure the ac voltage across each pair of leads---each pair read 0.2 mV ac. so I don't think the thermostat is receiving power.
    i have to locate the 24 vac transformer---can you help me?
    I've locatd a GOODMAN wiring diagram for remote condensing units. In it there are shown connections to a 24VAC power source for both the outdoor control box and thermostat.
    Specifically, it says to connect the above to appropriate control circuit having min 40VA 24 volt N.E.C. Class 2 transformer; etc.
    I am seeking the location of that transformer.
  • mtsuo Dec 12, 2009
    well, I finally got an a/c tech out here and they located the problem and showed me where the 24vac transformer was located. and fixed a circuit with a poor connection---that did the trick.
    thanks for your more thorough explaination, I think I could have done the same as the tech, with it.
    President:
  • 1,515 Answers
Hi, if indeed it is the transformer and not the batteries in the thermostat, check first, Depending on if your furnace is a split system, or a package unit, the transformer is located just after where you're main or high voltage enters the unit. In a package unit as on the roof, it would be in the main control panel just after the Contactor.On the split system furnace and condenser split up, it is located in the furnace control panel where the 120.volts comes into the furnace. It is normally a square looking silver solid looking box with electrical wiring connects to both sides.The split furnace will have 120 volts going into it, 1-black and 1- white.The other end will have 24 volts coming out. It may have markings such as R, C, G, Y, and W, just like the thermostat. This is the 24volt side supplies voltage to stat and other components. Set meter to above the voltage you want to check.Check to see if you have 120 volts coming in across the black and white. If there is power to the furnace, you will have 120 volts to the transformer. Now check the the other end to see if you have 24 to 28 volts from Red to C. If you do have between 24 to 28 volts a/c coming out, then the transformer is good and you need to look for a small 3 to 5 amp fuse. Newer furnaces will have them plugged into the board. Check to see if it is just the fuse blown. Another thing to check is, some transformers will have a reset on them. If no power out, no reset, transformer is faulty. Most package units will be 220 volts into the transformer, stepped down to 24volts. Check the same way, volts in from main power would be 220 volts or above, and 24 volts coming out from the red wire to the white or black or Red to most other combinations of the stat wires or control wires. Very easy to check. Always look for the reset on the transformer, and a split furnace will be 120 volts in, and 24 out.Nothing out, faulty transformer. A roof top package unit, make sure there is power to the unit first, then check the high voltage in which is called the primary volts. Coming out is called the Low or secondary, 24 volts. I hope this has helped you in finding and checking the control transformer. Very easy to check, and to replace.Just remember, power coming in with nothing coming out 24 volts, no reset, bad transformer. Just follow my steps to the incoming power supply, and you will see the transformer. If you need more help, please contact me, and I will be here for you.Take you're time and it will go smooth for you.Please let me know the out come. Sincerely,
Shastalaker7
Posted on Dec 11, 2009
  • 1 more comment
  • Robert Horton
    Robert Horton Dec 11, 2009
    Hi, if this is a split which has a remote condensing unit with the furnace / blower unit elsewhere, it is located in this indoor unit not the remote condenser.Where ever this furnace is, and the power coming into it, you will find the 40va, class 2, 120 volts X 24 volt transformer.If no batteries in stat, then yes it is powered by this transformer. I tried to give you the best description I could, just follow main power into the control section of the indoor unit.The outdoor condensing unit has a contactor, compressor, run cap.Transformer is always in the indoor unit on a split system with a remote condenser.Make sure there is power to the indoor unit.It will be mounted on the down end of main power. It is hard to give you the exact location, but you will see the 4 conductors from the stat coming from the 24 volt end. Red, Yellow, Green and, White. Check from Red to ground and it will show 24 volts if it is good and not open.If you can't see it, look at the diagram on this indoor unit and it will point it out. !20 volts in, primary side stepped down to 24 volts on the secondary side.Follow the 4 colored stat wires and they will take you to the transformer, as that is where they will terminate on most all furnaces. Could be terminated to a circuit board also, but look for it on the main voltage in side. That's where you will find it, not outdoors, only if it were a package unit all in one.I have faith you will find it, it could be setting atop a fan center with a cover over it. But, it will be easy to find if you will indeed follow the main conductors in, and they will take you to it as this is where they step down power to 24 volts, from the 120 volts in. I know you will find it. Please keep me posted. Sincerely,
    Shastalaker7
    PS, Focus on the indoor unit, as it is there :)
  • Robert Horton
    Hi, I just wanted to mention that the outdoor unit is supplied with 24 volts from the same transformer to control the contactor coil for cooling. This 24 volts closes the contacts energizing the compressor and outdoor fan.It ir fired by the thermostat. So once you locate the transformer and replace or check, you will be set for both heat and cooling. Remember to check for the fuse I mentioned. Good Luck and keep me posted.
    Shastalaker7
  • Robert Horton
    Robert Horton Dec 12, 2009
    Good morning, I am sorry that you had to call a tech out, and I know that in the search for the transformer you would have found it and been able to make the repairs, I was confident you would and could have. Thank you for you're ratings it was very kind of you. I hope you will continue using Fix ya anytime you may have a problem, and I look forward in helping you in the future.Happy Holidays to you and you're Family, Sincerely,
    Shastalaker7
  • 8,197 Answers
In side the thermostat there is 2 AA or AAA battery's that run the display. You might want to replace thous first before you go further. If you give me make and model # I will be able to help you more.
Good Luck
Fan not working
The fan relay is inside the unit. The thermostat switches 24 vac control voltage to the components like the heat strips, the compressor and outside fan as well as the inside fan motor. If the fan works with the heater and air conditioner then 24 vac is present. If not, then the 24vac transformer is bad. Sometimes you can find a fuse for the transformer, others have the fuse built internally and cannot be changed. If the inside fan is not working in the fan only mode then look at the thermostat as the problem.
Apr 26, 2016 | Heating & Cooling
Color code for theromstat
Wiring Examples and Instructions
How-To-Wire-It.com
Basic or Common Connection Points
Terminal Colour Signal-Type Description C Black 24 Vac Common Common side of 24 Vac Transformer See Diagram below R or V red 24 Vac Transformer Power Power side of 24 Vac Transformer See diagram below RH or 4 red 24 Vac for heat 24 Vac power before heat switch see diagram below Rc Red 24 Vac for cool 24 Vac power before cool switch see diagram below Y Yellow switched power (cooling) Signal to turn on cooling system see diagram below W White Switched power (heating) Signal to turn on heating system see diagram below G Green Switched power for fan Signal to turn on fan (forced air) see diagram below
Heat Pumps/Multi-Stage Units
Terminal Colour Signal-type Description Y2 Can vary Switched power (2nd stage cooling) 2nd stage cooling signal to compressor W2 Can vary Switched power (2nd stage heating) 2nd stage heating/ sometimes used as emergency heat E Can vary Emergency heat enable Dedicated emergency heat 0 Orange Reversing value Reversing dynamics of the heat pump ----
Nov 22, 2015 | Honeywell Digital Round Thermostat,...
Where is the low voltage 24 vac transformer located?
The transformer is located in the furnace. You might want to check to make sure the furnace door is on correctly brcause theres a swich that will open for safety . Also some have a fuse on the solid state board.
May 26, 2014 | Rheem RASL024JEC-RHPNHM2421JC 2 Ton 18.50...
Carrier thermostat blank lcd display
Like have a clogged drain and the float switch is tripped. Check the drain line near the indoor unit for a piece with two wires. Remove switch and check for water or look in emergency pan under unit for water. DO NOT LEAVE SWITCH OUT, must vacuum clog free or blow out with compressed air.
Aug 09, 2017 | Carrier Heating & Cooling
I have a programmable White Rodgers thermostat. I noticed that the room was getting warm and when I checked the thermostat the display was blank. there are no batteries. I believe it runs on 24 volt...
Hello, the thermostat reveives 24 volts from the transformer located in tne furnace via the R terminal. If there is no display on the thermostat either you are not getting power from the transformer, the thermostat itself is bad. If you have a multimeter check for 24 volts at the r and c terminals on the integrated control boatd on the furnace with the door switched taped down, if no 24 volts then the transformer is bad. If you have 24 volts then most likely your thermostat is bad. Also, if there is. 5 amp fuse on the control board check it out, sometimes they go out if there is a short in the thermostat wiring.
Jun 12, 2011 | Heating & Cooling
We have a Carrier Heat pump. Today the heat pump and (gas) furnace turned off completely and the thermostat is blank. We've checked the fuses and they seem to be fine and everything else is working...
Is the thermostat battery powered or powered by the transformer. If it is powered by the transformer then the transformer may have gone out. Turn the thermostat to off. Use a multimeter to check for 24 vac between R and G on the thermostat. If you don't have it there, locate the transformer in the air handler and check for it at the transformer secondary. If you don't have it there check for 120 vac at the transformer primary. If you have voltage on the primary but not the secondary then the transformer is bad and needs to be replaced. Let me know what you find and I can offer more advice.
Aug 15, 2010 | Heating & Cooling
Can not get readings on unit but there is power an changed fuse
I would check voltage to the transformer and from the transformer. Either 120 or 240 VAC to the transformer and 24 VAC from the transformer. The co ntrol panel runs on the 24 VAC. The transformer should be located in the junction box on the heater where the external power is connected.
Jun 24, 2010 | Hayward 250kbtu Ng Pool Heater - Inground
I tring to change thermosat I can not remeber what color go where
Typical Thermostat Wiring for 4 or 5 wire Heat/Cool Thermostat (not heat pumps)
4 Wire Termostat
R = Red One Side of 24 volt Transformer
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
with one transformer for both units
Rc One Side of 24 volt Transformer
Rh Jumper Rc to Rh
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
With 2 transformers one for indoor unit
And one for outdoor unit
Rc = Red One Side of (outside) 24 volt (outside transformer)
G = Green Blower (outside transformer)
Y = Yellow Cool (outside transformer)
Rh = Blue One side of (inside) 24 volt (inside transformer)
W = White Heat (inside transformer)
COOLING ONLY Thermostat
G = Green Blower
Y = Yellow Cool
HEATING ONLY
R or Rh One Side of 24 volt Transformer
W = White Heat
Feb 09, 2010 | Heating & Cooling
How do you wire a honeywell round mechanical thermostat
What are you trying to wire up?
4 Wire Termostat
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
Rh Jumper Rc to Rh
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
G = Green Blower
Y = Yellow Cool
HEATING ONLY
W = White Heat
Feb 09, 2010 | Honeywell CT87B ROUND HEATING&COOLING...
Trying to figure out thermostat wiring diagham on a split system
4 Wire Termostat
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
Rh Jumper Rc to Rh
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
G = Green Blower
Y = Yellow Cool
HEATING ONLY
W = White Heat
Jan 05, 2010 | Heating & Cooling