Question about Goodman GDS80904BNA Open Flame Heater
Goodman gmp075-3 gas furnace and the flame cycles
I have a Goodman gmp075-3 gas furnace and i replaced my control board (b18099-13) because of flooding , with a replacement board (made by icmcontrolls ) icm280c and the flame cycles for 4 sec then goes out i replaced the flame sensor but no help. as a last resort i have 2 zone heating and took the board out of the second one and everything works perfect. so i called were i bought it from and they sent a replacement. put in replacement and same problem 4 sec flame on and cycles over and over. is this board also bad or is this brand not compatible with my system
  • 66 Answers
You need the same board. the one you have is not compatible with your unit
Greg
Posted on Dec 15, 2009
My goodman GMVC95 furnace circuit board is flashing On 6 I replaced the flame sensor but it's still flashing. Does it have to be manually reset?
Alright, have you checked the low voltage fuse on the circuit board in the blower compartment? Make sure you check the roll out switches as well. If all of these issue appear to be fine then you may have a bad circuit board. There has been a bad batch of circuit boards going around many of the popular furnace brands this winter. Trane Gas Furnaces and Goodman Gas Furnaces have been effected. We sell both brands and have had to replace many circuit boards on new furnaces. Trane Gas Furnaces Installed Goodman Gas Furnace Installation Gaithersburg
Feb 03, 2018 | Goodman Heating & Cooling
Goodman GMP Furnace problem. Original problem is
Good one! Is the flame getting to the flame sensor within the few seconds? Maybe a good cleaning of the burners or flame tray would help. 1.3 ma is enough for the flame rod to tell the board to stay on. Re-do all the ground connections both at the board and furnace cabinet to be safe. Check the polarity of the power going to the furnace. What are the chances the second board is bad?
Jan 15, 2010 | Goodman Heating & Cooling
Model #GMPN100-4 Goodman furnace. Vent fan
The sequence of events for furnace operation is -
Fan purge for 30-45 seconds. During this time, a pressure switch is actuated by the running of the purge fan, proving the control board the purge fan is running.
After purge and purge prove, the hot surface ignition and or spark begins. After a few second delay, the gas valve will open. The control board then monitors for flame prove through another sensor located near the burners. If there is no flame within 3-5 seconds, the gas valve closes. It will repeat this process, usually 3 times, before it shuts the system down, which requires a power down of the system to reset.
I have seen trash get into the hose between the purge blower and the purge switch. But you could be having other problems.
Dec 17, 2009 | Goodman Heating & Cooling
Goodman gmp075-3 gas furnace and the flame cycles for 4 sec
JUST SAND THE FLAME SENSOR LOCATED IN FRONT OF THE LAST GAS PORT.
Dec 02, 2009 | Goodman GMS90703BXA Heater
Furnace starts properly, then shuts down, led flashes 8 times
The first thing to look at is the flame sense rod.
Shut off power to the furnace, remove, clean sensor with steel wool or sandpaper then reinstall the sensor. Reapply power and it should run properly.
Jan 10, 2009 | Goodman GMS90703BXA Heater
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
induced draft blower
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
Nov 23, 2008 | Goodman GMS90703BXA Heater
Goodman gas furnace
Sounds like it coud have been a flame sensor. the limit switch is usually near the top of the heat exchanger.
Nov 02, 2008 | Goodman Heating & Cooling
Goodman GMP075-3 ignition problem
Oct 01, 2008 | Goodman GDS80904BNA Open Flame Heater
Heating & Cooling Logo
419 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others