Honeywell VisionPRO IAQ Equipment Interface Module error codes 053- "faulty outdoor temperature sensor" and 089- "heating/cooling equipment missing". No heat after pipe above furnace broke and water may have dripped on the unit. Can I reset the system and get the heat back on without a technician coming out?
  • rleenknecht Dec 11, 2009
    Thank you. It worked.
  • Honeywell Master
  • 43,501 Answers
Yes you can manually get the furnace to start.
Find the control board for your furnace. Usually it is in the bottom return plenum area. If you just follow the low voltage wires from the E I M they will lead you to the control board.
On the board you will see a row of terminals labeled R, W, Y G and amybe some more letters depending on your unit.
With the power off to the unit Unhook the wires to the R terminal and the W terminal, The install a jumper wire from the R terminal to the W terminal.
Turn the power back on and the furnace will start. You will have to turn it off and on manually but you will at least have heat....
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Posted on Dec 10, 2009
I have a Honeywell VisionPRO IAQ thermostat. Heat won't kick on automatically, thermostat keeps saying 'wait. Can turn system off, back on and works. Is there something I can do to fix it?
Have you tried reseting the system by throwing the breaker waiting a minute then restarting? Turning it off and on at the keypad isn't the same thing. That has happened to me and the program glitched. I'm not sure what is being displayed on the screen, so am not sure what you have done, partially completed a scheduling program, etc. However, I found the manual online.
www.manualslib.com/manual/782319/Honeywell-Visionpro-Iaq.html?page=2#manual
You can look through it and see if there is something in there you aren't/are doing to keep it from working properly. There is also a 1800 number for assistance from Honeywell if your still stuck. Hope this helps.
Oct 18, 2017 | Honeywell Heating & Cooling
Tip
The Honeywell TH811U1003 thermostat is a universal programmable thermostat that...
The Honeywell TH811U1003 thermostat is a universal programmable thermostat that gives you electronic control of 24V AC heating and cooling systems. It also has the capability to be used on 750mV heating systems
One of the best features of this thermostat is it’s big clear backlit display. The current temperature, the set temperature and the time of day are displayed at all times. Simply touching the screen also activates the back light feature.
This thermostat has a menu programming guide the helps you through the process of setting up your schedule. You are able to select multiple days and customize the thermostat for any kind of unique schedule you may have. This thermostat also let’s you take it off the wall and still be able to program it. This lets you watch TV and program it at the same time.
There are built in backups that will hold the time for you if the power goes out. This t-stat will also update for daylight savings time. There are HOLD features that allow you to modify your program and hold it and then go back to the original.
Change reminders that are built in include the air filter, UV light, humidifier service and of course the batteries of the thermostat. The blower of you furnace can also be programmed to run extra to help increase the air quality in your home.
If you decide you want to know the outdoor temperature you can purchase an additional sensor and then hook it to you thermostat. The outdoor temperature will then be displayed on you thermostat. This feature also gives you the capability of using the sensor to monitor indoor temperatures remotely.
This thermostat will keep you very comfortable as the variation typically in temperature from set point is less than 1 degree F. The thermostat after a period of time learns the characterizes of the way the house or building heats and cools and then adjusts to get the most efficient operation of the heating or cooling system while maintaining a very close temperature tolerance.
By changing a few of the parameters in the thermostat this can be can be configured for either single stage conventional heat/cool systems or any single stage heat pump system.
Specifications of the Honeywell TH8110U1003 Thermostat
  • Description: VisionPRO Touchscreen 7-Day Programmable 1 Heat/1 Cool
  • Conventional and Heat Pump Thermostat
  • Application: Gas, Oil or Electric; Heat Pump; Millivolt
  • Programmability: Universal Programming from 7 Day to Non-Programmable
  • Changeover: Auto or Manual
  • Color: Premier White
  • User Interface: Touchscreen
  • Switch Positions (System): HEAT-OFF-COOL-AUTO
  • Switch Positions (Fan): AUTO-ON
  • Power Method: Battery or Hardwired
  • Terminal Designations: R, RC, C, W (O/B), Y, G, S1, S2
  • Dimensions (in.): 4 9/16 in. high x 6 in. wide x 1 1/4 in. deep
  • Mounting: Horizontal
  • Electrical Ratings: 20 to 30 Vac
  • Frequency: 60 Hz. 50 Hz
  • Setting Temperature Range (F): Heat: 40ª F to 90ª F. Cool: 50ª F to 99ª F
  • Setting Temperature Range (C): Heat: 4.5ª C to 32ª C. Cool: 10ª C to 37ª C
  • Differential Temperature (F): 1ª F
  • Differential Temperature (C): 0.5ª C
  • Stages: Up to 1 Heat/1 Cool
  • Outdoor Sensor: Yes, optional outdoor or indoor remote
  • Remote Sensor: Yes, optional outdoor or indoor remote
  • Sensor Element: Thermistor
  • Currents (Heating): 1.0 A running
  • Currents (Cooling): 1.0 A running
  • Currents (Fan): 0.6A running
  • Operating Humidity Range (% RH): 5 to 90% RH, non-condensing
  • Comments: Selectable to and Heat Only or Cool Only
  • Features: Screen lock
on Jan 15, 2010 | Hardware & Accessories
Tip
Th811u1003
Normal 0 MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman";} Specifications of the Honeywell TH8110U1003 Thermostat
on Jan 15, 2010 | Heating & Cooling
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
How do you change the battery on Honeywell Th9421C1004 Thermo
Hello Bob Compher,
It looks like GETTING that battery is the biggest challenge...
After that it simply unplugs (like a portable phone battery).
Your manual is listed (below)
For assistance with this product please visit or call Honeywell Customer Care toll-free at
1-800-468-1502
Homepage
Honeywell VisionPRO IAQ Installation Manual Page 8
Feb 24, 2017 | Honeywell Heating & Cooling
Why is it showing error code 90?
Sounds like a all the bells and whistles thermostat, why did you chose that one?
090 Data interface is continuously busy.
A log of error codes can be viewed at the end of the installer setup after the system tests. Active errors will be shown first. The Error Log will log the last ten errors (active and inactive).
Pressing the reset button will clear all inactive errors from the
error log; active errors can not be cleared until the condition has been remedially busy
Dec 27, 2015 | Honeywell TH9421C1004 VisionPRO IAQ Total...
Honeywell VisionPRO IAQ thermostat. No back light. Screen shows characters, but dim. When touched, back light fails to work. All other systems function okay.
this control has an option for back light display in the set up menu. if it has never worked this may be the problem. if it did work then quit you should replace the t-stat. there are many different models as they have advanced over the years. this is a great control. see if you can find the set up manual
Oct 12, 2013 | Honeywell YTH9421C1002 VisionPRO IAQ...
I am replacing a four year old Bryant thermostat (7 wire) that runs a Bryant heat pump and gas furnace. I connected the Honeywell EIM to the old wires using the same colort codes: W = W (o/b); Orange =...
Well you are naming 6 colors, where is 7?? I'm guessing you don't have a constant 24 going to the heat pump and there is no transformer outside. Send model number of indoor and outdoor, double check your wiring, double check your setup.
Aug 13, 2017 | Heating & Cooling
Thermostat
That thermostat must be used with a THM5421C1008 Equipment Interface Module. The thermostat communicates with the module and the module is connected to the HVAC components.
Feb 08, 2008 | Honeywell Electronic Programmable...
Heating & Cooling Logo
77 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
Paul Carew
vance jones
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others