Question about Aprilaire 600 Humidifier
Low Voltage to Solenoid
Hello--
I am having trouble with my AprilAire 600. I originally thought that my solenoid was failing but I took it apart and it seems fine. I then used a multimeter to test the voltages across the different connections.
I found that the power from the furnace was coming in at 24V but the voltage going out to the solenoid and sensor were around 6V. I'm pretty sure the solenoid needs 24V in order to open. Any thoughts on why my voltage is coming out to the solenoid so low? I touched the solenoid to the contacts coming into the panel and the solenoid opened right up no problem.
Thanks!
Paul
  • 1 more comment
  • short_thumb Jan 18, 2008
    I don't think my furnace is a multispeed and I'm pretty sure it is a downdraft furnace.
    The funny thing is that the humidifier worked for two seasons, then I didn't use it for two seasons because our winters were so mild, and then I tried to start it up this season and it didn't work. I have not changed the wiring at all so I'm assuming it is wired correctly.
    There are three pairs (black/red) of leads going into the controller--power from the furnace (which is only supplied when the furnace is running), a line going to the solenoid, and a line to the sensor.
    I expected to have the voltage to the solenoid go up to 24V when I turned the dial to "test" but it just stays at 6V. I turn up the furnace to ensure that it is running whenever I perform these tests.
    At this point, I'm inclined to think that the controller is bad.
    Paul
    Thanks for the help! I know the voltage with the solenoid disconnected is 6V and I'm pretty sure the voltage is the same with it connected. I'll test it tonight and will let you know.
  • Rob Robinson May 11, 2010
    Is your funace a multispeed? Is it a downdraft? The only thing between your furnace and humidifier should be the controller. Have you verified correct installation of wiring?
  • 38 Answers
The controller is faulty. The previous question was hopefully to help determine why it faulted. The switching for the solenoid is a solid state device that is allowing the 6v through but not getting turned on hard enough to supply the current to operate the solenoid. I am assuming that you checked the voltage with the solenoid connected. If you disconnect the solenoid and look at the voltage it will probably be 24v. If you are not comfortable troublshooting down to the component level a new controller will be your best bet. It may be that the transistor that drives the solenoid could just be replaced. You would have to look at the signal that drives it to determine if it is being turned on with adequate signal.
Posted on Jan 18, 2008
After a few hours my Aprilaire 400 makes a constant clicking sound that won't stop. Is it the solenoid?
This is either the solenoid or a loose low voltage wire. Make sure all the wiring connections are tight, if they are the solenoid if bad and will need to be replaced.
Dec 14, 2012 | Aprilaire 400 Humidifier
Aprilaire 550 not turning on
Hello, apply power directly from transformer to solenoid valve, it it does not turn on the solenoid valve must be replaced. If there is no voltage to the solenoid then follow the wires back and see where there is no voltage.
Nov 18, 2011 | Aprilaire 550 Humidifier
I have an AprilAir 600 humidifier, I don't see water running to the filter. It's very dry, I have a combination termometer and humidier and shows the humydity at 16%
Hello, check to see if you are getting 24 volts to the solenoid valve, if you are and the solenoid does to click to let the water in it must be replaced. If you are not getting 24 volts start at the transformer and work your way toward the solenoid valve to find where the voltage stops.
Mar 08, 2011 | Aprilaire 600 Humidifier
I have a Aprilaire 760. I have already tested the brown wires. The fan is still not running. I have power to the unit.
Hello, are you getting 24 volts to the solenoid vlave? If you are and the solenoid does not open it must be replaced, the 24 volts opens the solenoid and also energizes a small relay to turn on the fan. If you are not getting 24 volts to the solenoid valve then start at the transformer and work you way toward the solenoid and see where the voltage stops.
Feb 26, 2011 | Aprilaire 700 Humidifier
Have Aprilaire 600. Water will not flow thru unit
Hello, most likely the solenoid is bad and must be replaced. If you are getting 24 volts to the solenoid and it does not open replace the solenoid valve.
Feb 13, 2011 | Aprilaire Humidifiers
Humdifier not working after replacing filter. Have replaced before without a problem. It has been installed for over 6 years.
Hello, check to see if you are getting 24 volts to the solenoid valve. if you are and the solenoid does not open to let water through the solenoid is bad and must be replaced. It is also possible that one of the low voltage wires may of came loose when you were changing the filter, check to make sure that the wires are all tight. Let me know what you find.
Feb 11, 2011 | Aprilaire 600 Humidifier
Aprilaire 600 problem
It sounds like you got it...
The solenoid will not open with only 13 volts to it. Jump or apply the full 24-27 volts to the solenoid and see if it clicks and opens and allows water to flow.
If the valve still won't open or pass water, start looking for a plugged inlet solenoid inlet screen or a faulty solenoid valve as well as a faulty humidistat.
Jan 06, 2010 | Aprilaire 600 Humidifier
Solenoid won't open--voltage drops when connected to humidistat
The coil may shorting out the 24vac supply to the solenoid. Recommend replacing soleniod.
Normally you should be able to read the 24vac across the solenoid when energized.
The other option is to get a 120vac to 24vac transformer and test the solenoid. This way you will know if the solenoid is the cause or the 24vac source is the problem.
Feb 22, 2009 | Aprilaire 600 Humidifier
Solenoid on Aprilaire 600
solenoid valves dont just burn up just like that you have a recurring restriction due to bad water.Check the saddle valve at the water heater first then check for postive water flow at inlet to the solenoid valve,if you have water flow the valve is clogged with sediment.
Dec 13, 2008 | Aprilaire 600 Humidifier
Aprilaire 600 not getting a Solenoid click and no water flow at all
Your solenoid may have seized. The best way to check is remove the cover off the humidifier pad housing, remove the rubber tube of the distribution tray and see if water comes out while in the test mode. If you have a volt meter you can test to see if you have 24volts at the two wires connected to the solenoid. If you have 24volts there but no water ,the solenoid is bad if not you may have a bad humidistat or humidifier transformer depending on how it is wired.
Feb 10, 2008 | Aprilaire 600 Humidifier