I have a 3 ton cooling only unit that will only work down to 0 degrees F. I know this is the factory limit but the problem is the unit cools a server room. I need to make this unit run at a colder temp. I was thinking of interupting the outdoor air thermister with a 75 k ohm resistor. Will this work?

Posted by on

  • HVAC TECH 1 Jan 17, 2008

    This unit is aou36clx



1 Answer

  • Level 2:

    An expert who has achieved level 2 by getting 100 points


    An expert that got 10 achievements.


    An expert that got 5 achievements.

    Vice President:

    An expert whose answer got voted for 100 times.

  • Expert
  • 236 Answers

75k ohms resistor is lower than 0 degrees F in equivalent temperature may be compressor cannot operate because the maximum setting of thermostat. is from 17 to 18deg. C. You can use 11 to 12k ohms the temp. for this is about 23 to 24 deg. C. The resistor resistance is fixed so the compressor continue running without cut out. The only problem for this is the compressor, because the design of the compressor is for high temp. Continue running of compressor can produce icing in suction and evaporator coil and cause damage of compressor due to liquid slugging.

Posted on Jan 17, 2008

  • Felizardo Erilla
    Felizardo Erilla Jan 18, 2008

    Thats why the coolest setting of the thermostat is 17deg. C because the design of is the for the compressor is for the the high temp. Even the chillers or centralize air conditioning the lowest setting temp. is 42deg.F or 5.5deg C setting the temp. lower than this can damage the compressor.

  • Felizardo Erilla
    Felizardo Erilla Jan 18, 2008

    Actually you can bypass your themistor with resistor, but its still useless because running the unit lower than 0deg. C can form icing in your evaporator.You can use 11 to 12k ohms the temp. for this is about 23 to 24 deg. C.
    The resistor resistance is fixed so the compressor continue running
    without cut out.



1 Suggested Answer

  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

A 6ya expert can help you resolve that issue over the phone in a minute or two.
Best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
The service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
Good luck!

Posted on Jan 02, 2017


Add Your Answer

Uploading: 0%


Complete. Click "Add" to insert your video. Add



Related Questions:

1 Answer

Model ZFSB26DNA SS Side by side / refrigerator and freezoe not able to get cool enough. Refrigerator side temp 49 freezer temp 7

refrigerators run from 5 to 10 degrees C so your machine is on the upper limit of 9 degrees c
the freezer is at minus 13 degrees c and most work down to minus 20 degrees c so that is in limits
Get a technician in to check the thermostats and in the mean time check the condition of the door seals as they will loose the cold very easily is cracked or not sealing properly

Nov 04, 2015 | GE Refrigerators

1 Answer

What size coil fits this

The 70 stands for 70,000 btu and the 16 stands for 1600 cfm.. Air conditioning requires 400 cfm per ton, so the blower is capable of delivering enough air for a 4 ton a/c unit. However, the blower is is amultispeed and has a 'blower chart' in the manual that will give you an idea of air flow delivered on all 4 (usually) speeds. You wouldn't want to deliver 4 tons of air across a 3 ton coil. That would effect the temperature drop across the coil and also effect humidity removal.

4 tons of a/c is a considerable amount of cooling, so unless you have a large space or extremely high average summertime temps, I would ask a local contractor to do a heat load calculation to properly match a system to your specific needs.

Every area has a 'design temp' around which a system should be designed. Here in the St Louis area, the design temp for the winter is 5 degrees and for the summer its 95 degrees.

70,000 btu in gas equates to 20 kw in electric heat for what its worth.

Jun 15, 2014 | Comfortmaker G8MXN0701716A 66,000 BTU 80%...

1 Answer

Rheem split system condenser high pressure limit/safety needs resetting frequently before it reaches the set temp of 76 degrees faren. what's wrong and what do i need to check?

Is the outdoor fan running? The fan cools the coils and compressor, therefore keeping the high pressure low enough to run. Either the fan is not working or its not spinning fast enough. Check the capacitor, or just replace it.

Apr 18, 2017 | Heating & Cooling

2 Answers

2002 chevy malibu heats up when running at low speeds


Jan 19, 2012 | 2002 Chevrolet Malibu

3 Answers

We have had this unit for 3 years. We have had it serviced with freon and cleaned each year. The problem is that the air blows out of the vents but it is not cold. Well, for example, it was only 78 outside...

Hello, it is possible that the unit may be undersized for you home and not being able to keep up with the indoor heat load. The only way to determine thia have a hvac contractor do a cooling load calculation on your home. I have seen many units undersized that cause this problem.

Apr 09, 2011 | Goodman CPLE24-1 Air Conditioner

2 Answers


Hi, sounds as though for this to be its 2nd compressor for such a newer unit, the superheat was not right when the compressor was installed. I don't know what freon you are using the new R-410A or the regular R-22. There's a big difference in pressure, but now I see your pressure reading and its R-22 for these readings.For a 2 ton unit, you would use the superheat charging method for a unit that doesn't use a thermostatic expansion valve ( T X V ) and not the sub-cooling. A 23 degree super heat at that outdoor ambient temperature is way to high for that unit, you will loose the compressor again!!. Super heat killed the compressor is the saying and that's a fact. Suction pressure should pull down just as quick as the head pressure unless the valves are going and weak, or you have a scroll compressor that has a valve plate that is going, or you are low on charge. With a ambient of 95*, you should be at around 270p.s.i. on your head pressure as 210 to 200 is way low. Suction line temp should be around 68 to 70, with a suction line temperature of 50 to 51 degrees, which would give you a 10 to 12 degree F super heat. I don't know when the second compressor was installed, but it has to be low on charge to be such a low head, and high super heat and you will loose this compressor again, its only a matter of time before you have a burnout. It was either under charged when installed, or has a very small leak at one of the joints. I hope the liquid line drier was replaced also. It shows me you have some knowledge on a/c operation, so you need to get that superheat down to between 8 and 10 degrees for this unit to cool properly, and leak check it also. Did you buy a extended compressor warranty? Lets get the head pressure up and superheat down and you should be OK unless the valves or valve plate is weak. Once you loose the valves, you will have a lower than normal head pressure and a high suction pressure. Compressor just won't pull down anymore. I hope I have been of help to you and ask of you to be kind when rating me. I will be here for you if and when you need me for anything.
A/C & Heating Contractor

Jul 02, 2010 | Weather King 10AJA6001AH Air Conditioner

1 Answer

Air condition jsut 10 month old ... not keeping up whith cooling

If it's only 92° outside and the unit won't cool the house, then the unit is either to small or it's low on refrigerant. They are designed to cool a house with outdoor temperatures up to 115° to 120°.Usually you need one ton a/c for every 400 square feet of house, but, you have to take into account for average outdoor temperature and humidity, windows, doors, especially sliding glass or patio doors and which side of the house they are on, insulation in walls and attic.
The air leaving your duct work going into the rooms should be about 20° lower than the room temperature, if you have a 80° room then the air leaving the duct should be around 60°. if it is then the unit is probably to small if, everything is working properly.

Jun 07, 2010 | Goodman CLQ36AR49 Air Conditioner

1 Answer

Anybody there?

It depends on the room varables, If it has an attic, tile ceiling, what type of walls, where in the building is the room and so on? The biggest problems is all ways the power. Get a free estaimate from an A/C company. Everyone and myself needs to see the room before they give you an recomndation that can truly be applyed to your situation. But to give you some ideas, I would put a 2.5 ton - 3 ton unit just for over kill. Go with a straight cool package unit. If your company tight on cash just get a mini split system with a 30,000 BTU to 36,000 BTU cooling capacity. Cost for something thats going to last 20 years, avg. is $4,500- for the package unit and as low as $3,000 for the mini split.

Oct 17, 2009 | Frigidaire FAA055N7A 5200 BTU Room Air...

1 Answer

Compressor size

Square footage is how you determine what size of an AC you need, say two bedroom house with 1500 square feet would require a 3 ton unit but I would go to a 4 or 5 ton depending on brand and what you may do in the future, Like adding a bedroom or bathroom and how many people will be living in the house, a heat pump normally last longer the bigger it is and is more efficient than a smaller size. Just think like this, a 3 ton will run 30 minutes to an hour longer to cool the same space as a 5 ton so if the five ton does it 30 minutes faster it will not run as long. And when it has to pull down the temperature again it will do it much faster. So less run time means faster heat or cooling and less energy is used. I have found that the bigger units are made better and last longer as a general rule. And to understand the 3-ton and 5 ton let me say that it means how long it takes 3 tons of ice to bring the temperature down 10 degrees, the old BTU’s British thermal units. However the bigger the unit the more well built it is normally and the less maintenance required. 5 tons of ice would get it cooler faster. But one thing to keep in mind a heat pump is only good for 20 degrees temperature range, for instance if the high range is 80 then the low side would be 60 in order for it to be efficient so if you have it set in the house at 72 degrees on the high side and low side would be 52 degrees. But the larger the unit the less time it would take it to recover from the heat differential.

Jul 22, 2009 | Ruud UAKA042 Air Conditioner

4 Answers

Room temperature has not changed since hooking up new portable a/c

This may sound dumb but ( 1) Do you have the warm air from the unit to the exterior of the space? If the condenser is in the space your putting the heat your trying to remove right back into the space. ( 2 ) There should be an air supply and an air return in the space only. With that there should be a temperature difference of 16 to 20 degrees between the supply and return. ( 3 )A 1 ton unit usually will cool approximately 400 square feet. ( 4 ) It may take a while to pull the space temp down due to pulling the heat and moisture from the ceiling, walls, and floor. This could take 6 hours or more the first time you use the system in a space.

May 18, 2008 | Danby Portable Air Conditioner

Not finding what you are looking for?
Fujitsu 36CS Air Conditioner Logo

138 people viewed this question

Ask a Question

Usually answered in minutes!

Top Fujitsu Heating & Cooling Experts

Fotis Papastamatiou

Level 2 Expert

109 Answers

Bill Long

Level 3 Expert

588 Answers


Level 3 Expert

77932 Answers

Are you a Fujitsu Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides