It's cold out, and my Central Air kicks on every time my furnace kicks in. I get heat, but don't think my outside unit (fan) should be kicking in each time my furnace kicks on. Suggestions
  • 1 more comment
  • robwfwhite Nov 23, 2009
    It is a Rheem RAKA-024 JAZ, 10 Seer. I don't believe it is a heat pump as it says "air conditioner" on top. Could it have been modified regardless of the model? ... What does a heat pump look like vice a regular a/c unit?
    More on this ... First off, thanks for your replies. The unit is a RAKA-024 JAZ, Rheem Seer 10. I replaced the digital t-stat as I thought the guy I bought the house from hooked it up wrong, (as he did with most of the other renos he's done) but I have no experience with HVAC- other wiring yes.
    I've traced the wiring down to the furnace from my t-stat. There are 6 wires running to the stat into the wall, but only four come out the other side. Can you describe how the "C" terminal affects things?... Also I noticed both the "W" and "Y" wires being hook to the same terminal on the furnace. The "W" terminal has nothing hooked up to it, although the "C" terminal does.
  • D. Floyd Kolb
    D. Floyd Kolb May 11, 2010
    Are you sure that you don't have a heat pump unit that is heating your house. A heat pump is an airconditioner that works in reverse, the outdoor unit would then be running everytime you have acall for heat.
    President:
  • 1,515 Answers
Hi, If you have what is called a heat pump, the outdoor unit is supposed to run. It has a reversing valve which reverses the flow of refrigerant and the indoor unit becomes the condenser and the outdoor becomes the evaporator coil. Now, if you don't have a heat pump and the furnace is gas fired, then the control wiring or thermostat is calling for both to come on. Control wiring has to be touching together somewhere and bringing on both. Look over the exposed stat wire outside if you have a dog that may have chewed the wires, I have seen this happen. If all wiring looks good, then the stat is faulty and must be replaced. Make sure you don't have a heat pump first, as the fan, compressor, and all will run on heat and cooling. I hope this will solve you're problem, please let me know, I would like to hear back. Sincerely,
Shastalaker7
Posted on Nov 20, 2009
  • 2 more comments
  • Robert Horton
    Robert Horton Nov 20, 2009
    Hi, For a temp. solution only if it is gas, turn off the outdoor unit at the breaker. Heat pump leave on Until we get a solution.
    Shastalaker7
  • Robert Horton
    Robert Horton Nov 24, 2009
    Hi, to tell the difference in a heat pump from a regular a/c is if the indoor unit is gas fired, the furnace. The outdoor unit looks the same and it should say some where on it Heat-Pump. The model number you gave me shows that it is a 2 ton unit. As far as the wire terminations, on the gas furnace, you only need 4 wires. The furnace is wired wrong . W to W, Y toY, R to R and G to G. The C is the common, just leave it connected to c.If you have 4 wires to the stat, you should have rh and rc which should have a red jumper wire connecting the 2 together. The red from the wall will connect to either one as they are together. Then W to W, Y toY, and G to G. The stat you have should be a regular central a/c Heat T-stat. So, I am sure it is a 2-ton gas/elect unit and the reason the outdoor unit is runnig, is they way it was wired to the furnace. You say there is another wire connected to the C at the furnace? You only need the 4 wires since you have 4 to the stat. Same as the stat, R to R, W to W Y to Y and G to G. forget the common. The out door unit stat wire if it is not a heat pump will have only 2 wires connected to it. If you have 7 to 8 it would be a heat pump. Please, just follow the way I have told you and I am sure it is a gas furnace if you have burners. Wire it like I said with the 4 to stat and 4 to furnace to the designated terminals, and the out door unit should not run in heat if it is gas. Take your time and you can do this. Let me know, Best of Luck and you will be up and running correctly. Shastalaker7
  • Robert Horton
    Hi again, I looked this condensing unit up and it is showing it is not a heat-pump.Make sure the indoor blower unit is gas fired.
    Shastalaker7
  • Robert Horton
    Robert Horton Dec 17, 2009
    Hi, I am assuming the unit may be on-line by this time and hope it is. I was doing follow ups and this one popped up! I looked back on some of the solutions that I and other techs offered you. I looked where you said it had 6 wires but only 4 were terminated? Here is how it should be terminated. As far as 2 wire yellow and white on the same is wrong! Red to R, Green to G with is indoor fan, white to w only and alone! Yellow to Y for cooling. Now you will have to wires coming in from the outdoor unit that supplies 24 volts to the contactor coil. White would go to the Y terminal, and the other to common or c.If you connect Y yellow to the w terminal, both heat and outdoor unit will be energized.If C wasn't being used, connect only one of the 2 wires coming in from condenser. I hope you are up and running by now. Happy holidays, Sincerely,
    Shastalaker7
Coleman Evcon furnace blower runs w/ no call for heat. Temp is 5+ degrees above thermostat setting. (Programmable tstat)
When you say door are you referring to the front door or the furnace door? If the unit kicks on AND off by itself I would say it's in the tstat or the tstat wire. If it were internal I would think the blower relay or heat contactor/relay were getting stuck AND THE FAN WOULD NOT TURN OFF until you flipped the breaker. Good luck
Mar 21, 2017 | Coleman Heating & Cooling
Auto/On set to ON. Fan runs.
Sounds like the thermostat, the way to verify is to unplug indoor unit, remove thermostat, take pic of wiring with phone or label the wires as to the terminals. Carefully twist the yellow,(Y) Red (R) and the green (G) together. Plug the furnace back in, if the unit operates normally, replace the thermostat. I am basing this on the fact that the blower speed is changing. This could also be an anomaly within the circuit board in the furnace section, not likely though as the outside unit (condenser) is not controlled n by the indoor board unless this is a heat pump. hope this helps. D
Jul 21, 2015 | Dometic Rooftop RV Air Conditioner
When my outside unit kicks on it tries then quits? The inside fans still blow cool air, and the furnace can be turned on to emergency heat.
u may just have bad capacitor see if it looks swelled up if so theres ur problem if not u may have lost a leg of power or u may have a locked up compressor but it sounds like u have a bad capacitor or a bad contactor
Feb 24, 2010 | Ruud Central System Air Conditioner
Hello We have a Trane central air
Bad thermostat, improper wiring or bad circuit board in furnace. Turn off the disconnect outside.
Dec 30, 2009 | Heating & Cooling
A. c. unit not blowing air
Check Your AUTO FAN/BLOWER Switch In Furnace.
Jun 04, 2009 | Heating & Cooling
Fan running constantly in the house
Check t-stat and make sure fan is set to "Auto", that might be why fan is running all the time, or it could be a fan relay that is stuck closed. It sounds like you A/C is over charged or you have a bad high pressure switch, this was a common problem with this manufacture especially in the heat mode.
Apr 24, 2009 | Ruud Central System Air Conditioner
Furnace runs on heat, air conditioner does not
If you have a Gas furnace in the Attic then the answer is yes. The outside condenser will not run if in fact you have a gas furnace.
Feb 11, 2009 | Ruud Central System Air Conditioner
Heat Pump Stops Working only in the Early Morning
When the unit does what you say does the fan motor outside stop also , if it does that means it is in defrost mode and should kick back over to normal after the system heats up the coil enough
Nov 24, 2008 | Weather King 12AJA4801AH Air Conditioner
Blows cold air
Sounds like you have a problem upon start up of heat. Your safteys maybe shutting you down, and restting voltage to your curcuit board allows you to have another heating cycle. Honestly you may due justice calling a tech.
Dec 19, 2007 | Heating & Cooling
Heating & Cooling Logo
191 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen