I have a Goodman furnace and it has been giving me trouble. I have recently changed the pressure switch and ignitor, The thermostat just flashes and clicks but nothing happens!!! What should I do next?
  • D. Floyd Kolb
    D. Floyd Kolb May 11, 2010
    There are a couple of things that you could check yet. If this has a PVC vent, is there water built up in the vent pipe? If it is not PVC, is there a dead bird mouse or some other obstruction in the vent pipe that would stop or slow down the air flow? Also, I have seen blowers that come apart inside, or do not run to full RPM which causes a reduction in the air flow. The pressure switch today are vey sensitive to ANY reduction in air flow and will not let the furnace light or even be bouncing it on and off because of vent air flow issues. Good Luck and hopefully this will help you figure this out.
  • 614 Answers
You should have a contro Go to the W terminal on the board and check for voltage with tstat on. There should a light that blinks on the board. The number of times it blinks tell you the problem. check this and let me know. Rus
Posted on Nov 19, 2009
I have a goodman furnace GMP100-4 REV B..about a year ago it was not working. The fan would start but it would not ignite. We found out we need a new ignitor and it was a good quick easy fix. Now a ye
Any light flashin on the control board? If not then look for a small fuse blown on the board. See lights a flashing count them flashes
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Nov 29, 2011 | Goodman Heating & Cooling
I have a Goodman GMP 125-5 furnace. It had a 3 light code i replaced the presure switch now it is giving me a 1 light code please help
Oct 28, 2011 | Goodman Heating & Cooling
Suddenly not working im not sure if there even is a pilot to be lit
Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
Feb 03, 2011 | Goodman Heating & Cooling
Goodman 95 %furnace keeps saying low pressure is stuck. changed out low pressure switch and high pressure switch and still have same problem.
That thang might be sensing a lazy flame. In other words the flames took too long in the board's opinion to quit sensing the flame. Yall probably need to do pressure tap on the gas valve.
Here is a realistic look at goodman fault codes and what to check fer and I am assuming you are not a tech and don't know this already and am hoping it helps:
Now here is how it should all go down:
Bottom dollar: it all goes back to type of gas, the initial setup, the pressure tap. and how it is wired up to begin with.
This will give you an idea where to start I hope.
Dec 10, 2010 | Goodman GMS80903BNA Heater
We turned on our older Goodman furnace (model GMPN080-4) for the first time this fall, and... nothing. The fan works when the thermostat is set to "off" or when the temp setting is lower than the actual...
I googled Goodman trouble codes, and found 3 blinks is an open pressure switch. At the top of the furnace there is an induced draft motor. It forces the combustion gases, after ignition, through the flue pipe. Try giving it a little turn. You should be able to see the little fins, like a small fan blade. With it in the off position, no demand hot heat, try spinning that lil fan blade in either direction. And the try the heat. If that don't work, its likely the water leak, from the coil, has damaged the motor or control board, and you need a technician. Hope this helps!
Mar 22, 2017 | Goodman Heating & Cooling
Goodman furnace ignitor works, blower starts up but no flame, no heat ignitor glows then everything stops
sounds more like a pressure switch problem. If the pressure switch does not make, then the furnace will not attempt to light. Its a safety feature on residential furnaces.
Check the pressure switch and hose for obstructions. Clear any and attempt to re-light. If still not successful, its time to contact a local service company to check the gas valves and electronics.
Apr 27, 2010 | Goodman GMS90703BXA Heater
Hello I have a goodman gas furnace
On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Oct 18, 2009 | Goodman Heating & Cooling
Goodman furnace blinked 1 time
Furnace attempted to start but failed after so manay tries. This may help you.
Sequence of operation, Gas Furnace.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
This is why we technicians earn the big bucks!
Dec 05, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
109 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen