Question about Goodman GMS90703BXA Heater
When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can hear it turning on and off. Sometime the main blower starts when the gas valve should turn on also. The troubleshooting led never blinks, it stays on constant.
  • 1,420 Answers
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Posted on Nov 20, 2009
Take a piece of emery cloth and clean the flame rod , see pic on goodman site. this is a regular problem with goodman/ easy fix too.
Posted on Nov 24, 2009
Turns on but no heat
From what I saw when I googled you furnace it has a hot surface igniter. It only gets hot when it's time to light the furnace. You should be able to see it glowing red when the furnace is trying to light. The furnace has a safety feature which shuts the gas valve when it doesn't detect a flame to prevent gas build up in the furnace. There are other safety features also. If the draft inducer motor isn't running the gas valve won't open. Overheat switches some of which have to be reset manually. Adjust the thermostat until it calls for heat then observe what is or isn't happening in the furnace. It will go thru a purge cycle first. The draft inducer motor will run to do this. After the purge the hot surface igniter should get hot a glow, then the gas valve will open and the burner will light. Let me know what you find.
May 04, 2010 | Goodman GMS90703BXA Heater
No blinks normal running igniter glows gas comes on wont run
Check for 24 volts across the gas valve when Ignitor is glowing. If no, bad board. If yes, bad gas valve or blockage.
Mar 05, 2010 | Goodman GMS90703BXA Heater
I have a Trane xe 70. The Heat is not turning on. The ignitor will glow but NO gas or blower. I turn on the fan and the blower does work but not when HEAT is selected on the t-stat. Also the LED light...
Check to see if you get 24 volts AC at the gas valve from the circuit board when the igniter is glowing. If yes, bad gas valve or blockage in gas train. If no, bad circuit board or broken wire
Feb 07, 2010 | Heating & Cooling
Have a Goodman GMT070-3B which the vent motor seems to be sticking. I took apart and cleaned the brushes and reassembled. The furnace will come on only after what seems like the vent motor comes up to...
The whole assembly must be replaced.
The sequence of operation is -
Combustion fan purges the heat exchanger. A pressure switch verifies combustion air fan is running. Usually a 30-45 second purge before the hot surface ignitor glows, or the spark ignition starts.
Gas valve opens after 10-15 seconds and main burners light. Control board monitors for flame and shuts gas valve after 2-3 seconds if main burner does not light.
If burner does not light, some boards repeat this for 3 tries, then locks out and is reset by cycling power.
Air blower comes on after another 30-45 seconds after main burner ignition.
Times may vary based on the specific controller board. A flow chart and timing sequence should be located somewhere on the unit, usually in the fan compartment.
Dec 16, 2009 | Goodman GMS90703BXA Heater
FURNACE COMES ON AND SHUTS DOWN WITHIN 15 SECONDS
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control). When all else fails, check the ground connection for corrosion.
Nov 23, 2009 | Heating & Cooling
I have a problem with an Armstrong SX90 gas furnace. model GUK100D14-2B serial number 8497G26541 The ignitor is not 'glowing' and therefore the pilot won't light. Everything seems to be sequencing...
Buy a new ignitor either from the ignitor store online, or your local distributer, Contracter, dealer.. they usually run from 15 dollars to 35. Their simple to change out and deffinite do it yourselfer... Oh and turn off power at breaker panel, you don't need any unexpected surprises!!
Dec 02, 2008 | Heating & Cooling
Goodman furnace
Check the roll out switch(s) and the lock out switches. They are a small disc looking about the size of a nickle, with with 2 wires attached on them. There will be a re-set button in the middle that resembles a small peg. Push this in to re-set. As the glow coil shorted out, the fuse on the control board may have blown. On the newer furnaces find the main board and look for a car type fuse. If blown, replace. You also have the symptoms of a bad limit switch, by the clicking noise (the heat fan relay) and the blower fan running instantlly.
Jan 05, 2008 | Heating & Cooling
Goodman GMS90703BXA Heater Logo
1,030 people viewed this question
Top Goodman Heating & Cooling Experts
Paul Carew
Tim Whalen
christian nielsen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others