Burner will not light but ignitor comes on, gas is on. Goodman furnace. Comments: Nov 11, 2009 - Thanks for the help, found that the top safety switch (relay?) was tripped, reset it and it fired right up, is this a sign of something else wrong and should I replace the relay?
  • 614 Answers
Sometimes the gas pressure is to much which causes th much heat. The limint switches do get weak. Just let it run and see what happens at least you know the safety works. If it is bad not hard to replace.Rus
Posted on Nov 11, 2009
I have a Goodman gas furnance. The furmance kicks on the glow rod lights and then the furnance shuts down after about 60 seconds it goes through the same cycle. The burners never come on. What's wrong?
Let's trouble shoot a few possibilities:
Can you confirm that your gas pressure/ supply is correct-- by lighting all of the range top burners at the same time-- Do they all light quickly, and burn to full height, without much of any yellowing at the flame tips? That should indicate you have god gas pressure and supply.
Now-- in the Oven itself-
When you light the BROIL burner-- does it's glow ignitor light up, and does that burner light off OK?
If it is only the main oven burner that is not lighting, are you able to remove the cover plate that covers it, and watch it light off? -- Any clues on whether or not the gas valve even open?
If NO gas flow, likely you need a new Main Oven Gas Valve-- Probably need to call your Gas Appliance service person.
Let us know if this helped
Mack B
Jan 23, 2011 | Goodman GMS90703BXA Heater
Inductor blower comes on and runs then the ignitor glows flame comes up and burns for approx. 10-15 sec then goes out then fan comes on. Model number is PBKMLB12N0B0F I believe this is a goodman furnace.
I cleaned the sensor that was at the the right further most burner on my Goodman and it worked. got the answer to my problem here at fixya. My burner flame only lasted 5 secs before it shut off. Thanks to all who took the time to send me a response.
Nov 13, 2010 | Goodman Heating & Cooling
I have a Lenox furnace. Before this igniter kicks off, there is a loud noise comes from furnace. Where is that noise from? Thanks.
This is what we call a "delayed ignition",(gas is not being ignited right away), gas builds up in the chamber and then lights causing a boom. The cause of this problem could be from having dirty burners or ignitor not position to ignite the gas right away or your ignitor may not being glowing enough to ignite the gas being released, check all, Good luck.
Jan 08, 2010 | Goodman GMS90703BXA Heater
Won't light
If you can see the ignitor coming on and the furnace will not fire, if you have a elect. meter, see if you have 24volts at the terminals on the gas valve right after the pilot lights or glow plug whichever. you should hear the gas valve click when pilot is on and have 24volts at the valve at that time. If you do, then the valve is bad.If you don't have 24 volts, then check the stat for 24 volts. A safety may have tripped also. Try these things first and let me know. Good Luck, Shastalaker7
Nov 07, 2009 | Heating & Cooling
My Goodman GPG1324 won't start up on the heat. Is there a pilot light that can go out? We had a new gas water heater installed this spring.
On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Oct 18, 2009 | Goodman Heating & Cooling
Hello I have a goodman gas furnace
I have a Goodman air heat unit that will not come on.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Jan 27, 2009 | Goodman GMS90703BXA Heater
FURNANCE WONT FIRE UP GOODMAN GMNT12-5D
Jan 07, 2009 | Goodman GMS90703BXA Heater
I have goodman gmp heater dose work for few mintes
Sequence of operation on your gas furnace may help diagnose your problem.
Most newer furnaces like yours will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Dec 10, 2008 | Goodman GMS90703BXA Heater
Goodman furnace blinked 1 time
Furnace attempted to start but failed after so manay tries. This may help you.
Sequence of operation, Gas Furnace.
This is why we technicians earn the big bucks!
Dec 05, 2008 | Goodman GMS90703BXA Heater