47

Where vent motor is there is usually a hose coming off which oressurizes when vent motor comes on, take hose loose **** or blow in it, take tooth pick and stick in all ports where hose connects (could be clogged) when sucking on hose you shoul hear pressure switch click each time you pull a vacumme, if fan has switch on back of fan as some Goodmans have the vent motor may need to be replaced.

2 Related Answers

Anonymous

  • 22 Answers
  • Posted on Nov 24, 2009

SOURCE: getting 3 blinks on error code LED, checked

i take it the flash code 3 blinks refers you to the pressure switch...see the schematic. If this is what you are saying than lets move on... the voltage across the pressure switch should read 0 if the furnace is running and calling for heat. you dont need to check each wire to ground but across the two quick connect tabs. you will either read 0 or 24 volts (or there about). if you read 0 the switch is closed and functioning as designed. if it reads 24 volts it is open and there is not enough negitive pressure to close it. this can be due to a leak in the rubber tubing or a clog in the pressure switch, tubing, or induced fan housing connection nipple. the flue pipe may also be clogged or an improper cap is used at the termination. last is the wiring could be faulty going to and from the pressure switch. Hardly ever have we found a broken or faulty switch but it could happen. trust the board in most cases.

Ad

Anonymous

  • 1515 Answers
  • Posted on Aug 02, 2010

SOURCE: pressure switch stuck open

Hi, yes you can. The pressure switch is just stuck open causing the unit not to fire up. Find the small inducer motor that should be running, if its not and you have the panel off, you have a switch for the panel to kill the power when you take it off. You will have to tape it down with duct tape to restore power.You will see a clear plastic air tube coming from the motor and goes to this pressure switch. Pressure from the motor is what opens and closes the switch. Unplug it at the motor and blow through it several times. You will hear it click. Do this back and forth and it will break it loose. This will solve the problem. Kill power to reset unit. Start it up and your done. If it continues to do this, get a new pressure switch at a appliance parts house. Let me know the out come and please be kind when you rate me as I know you will. Good Luck,
Shastalaker7
A/C, Heating, & Refrigeration Contractor

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

York Diamond 80, controller is blinking Code 3 (Pressure switch stuck open).

sounds like u nee a new pressure switch. check 1\4 inch tubing going to pressure switch, remove it make sure no condesation in it., blower will only come on once flame is establised, ventor motor comes on closes pressure switch, brings on ignitor then gas the blower, make sure no blockage in vent pipe
0helpful
1answer

Coleman Evcon Furnace. Why do I keep getting three flash code?

You might try viewing this YouTube video which shows a way to unstick the pressure switch. https://www.youtube.com/watch?v=Wc_oFIL2aRY
0helpful
1answer

Lp furnance ignites for 3seconds then shut off.

A pressure switch code means there is an unsafe condition that should be looked at by a competent service tech. Sometimes there is a switch failure, but most of the time there is an unsafe condition.
0helpful
1answer

Amana Air Command 90 furnace LED light blinks 3 times pause 3 times

TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.

2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.

3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.

4 BLINKS Open limit switch Verify continuity through rollout switch circuit.

5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.

6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.

8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.

9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.

10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.

12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
0helpful
1answer

We have a Carrier Infinity 96 furnace in our home, which was installed brand new in our house we built 5 years ago and this thing is a nightmare. We've had the code blinking away and and the technician in...

EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST DIGIT DETERMINED BY THE
NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY THE NUMBER OF LONG FLASHES.

43 LOW-HEAT PRESSURE SWITCH OPEN WHILE MEDIUM-HEAT PRESSURE SWITCH IS CLOSED - Check for:

- Low inlet gas pressure (if LGPS used).

- Plugged condensate drain.

- Improper pressure switch wiring.

- Water in vent piping, possible sagging pipe.

- Stuck open low-heat pressure switch.
- Disconnected or obstructed pressure tubing.

0helpful
1answer

I have a 1997 goodman 3.5 ton outside gas, self igniting heater. the led beep is 1 then a 2 then a half second delay.

I am sure you have gotten this fixed by now. A 1 code is a general lockout meaning it tried to light 3 times and did not. A 2 code is for a stuck closed pressure switch. That pressure switch is normally open. If unit is off, and you remove the wires and using a multimeter, ohm across it, it should be open. If not, it needs to be replaced.
2helpful
1answer

Getting 3 blinks on error code LED, checked voltage at the pressure switch, and it is getting ~24v from both wires. What else could cause a "pressure switch stuck open" error code?

i take it the flash code 3 blinks refers you to the pressure switch...see the schematic. If this is what you are saying than lets move on... the voltage across the pressure switch should read 0 if the furnace is running and calling for heat. you dont need to check each wire to ground but across the two quick connect tabs. you will either read 0 or 24 volts (or there about). if you read 0 the switch is closed and functioning as designed. if it reads 24 volts it is open and there is not enough negitive pressure to close it. this can be due to a leak in the rubber tubing or a clog in the pressure switch, tubing, or induced fan housing connection nipple. the flue pipe may also be clogged or an improper cap is used at the termination. last is the wiring could be faulty going to and from the pressure switch. Hardly ever have we found a broken or faulty switch but it could happen. trust the board in most cases.
7helpful
2answers

Furnace code light flashes 3 times /pressure switch stuck open

Check the intake and exhaust plumbing for any obstructions. I had same issue, turned out to be ice in the air intake plumbing on outside of house. This may be the problem. The pressure switch can be tested by pulling hose from purge motor that goes to switch and applying a small amount of suction. The switch should make a clicking sound.
Not finding what you are looking for?

3,274 views

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...