Question about Ruud UPMC036 Air Conditioner
Goodman Gaspack Does the hot surface igniter suppose to stop glowing after burners lites? can`t see model or serialĀ  gas valve has 96 stamped for a date code..
It is suppose to terminate.the deal though is when your ignitor, the heat from the burner flame will make it appear as though it is on.
do this.turn your gas valve knob off and turn the heater back on.observe the burner compartment.first you'll hear the flue inducer start.then your heat ignitor will glow.then you'll hear a click.that is your valve trying to open.then your ignitor will stop glowing.
Posted on Dec 30, 2008
    Problem Solver:
  • 9 Answers
YES.
Posted on Dec 30, 2007
Oven starts and stops
The oven safety valve
(also called the gas valve) is the part that ensures that gas is not released until the igniter has reached the correct temperature needed to ignite the gas. While this part can fail, it is uncommon. If the hot surface igniter does not glow you should first verify that you have voltage to the circuit. This is a live voltage check and should be performed by a qualified person. If voltage is lost at the valve terminals then you should verify the continuity of the bi-metal in the valve using a multi-meter.
The oven burner igniter
commonly known as the hot surface igniter is used in modern gas oven burners to open the gas valve and to ignite the gas. As the igniter draws electric current it will heat to a high temperature and glow, as well as cause the bi-metal in the oven safety valve to warp and open the valve releasing the gas to be ignited. This sequence normally takes about a minute. Igniters come in both flat and round styles and are very fragile. If the burner does not light then you should check the igniter first. If the igniter does not glow at all, then check for power to the circuit. This is a live voltage check and should be performed by a qualified person. If power is present then the igniter may be open circuit and can be checked for continuity with a multi-meter. If the igniter is glowing, but the burner is not lighting, the igniter may be weak and still be at fault because it requires a certain amount of current draw to open the valve. This check requires the use of an amp meter and should be performed by a qualified person. If the igniter is defective then it must be replaced.
Apr 02, 2014 | Kenmore Ovens
Ignitor work but burner do not lite
Feb 16, 2014 | Kenmore 30464 / 30465 / 30469 Gas Single...
Why will my carrier model 58PAV075-JV not light the burner when the hot igniter glows but will not start
Could be a weak igniter, it the igniter does not get hot enough it will not ignite the gas. Make sure the gas valve is opening to allow gas to the burners, if not the gas valve is the problem
Dec 15, 2012 | Heating & Cooling
Goodman GMP100-3 home furnace status lite is constant red
check continuity of hot surface igniter....open loop means replace igniter
Nov 04, 2012 | Goodman Heating & Cooling
Tempstar pilot turns off
Based on your model number this furnace does not have a pilot light,instead it uses a hot surface igniter.typically it glows and when it gets hot enough the gas valve will open and the burners will light.When the igniter starts to go bad it will glow but not get hot enough to open the gas valve.If your furnace lights and the quickly goes out the flame sensor maybe dirty.
Oct 07, 2012 | Goodman GMS90703BXA Heater
Maytag oven will not heat, no gas flow. Broiler works, clock and timer works.
You may even see the orange "glow plug" (called a hot surface igniter) glowing orange and so assume that it's OK. Not necessarily!! You have to measure the current/amp drawn by the igniter and compare it to this repair sheet before you can say it's OK or not. The gas valve has a bi-metal that open when a certain amount of current flows through it to heat it up. The igniter is wired in series with the gas valve. As the igniter gets older or weaker, it's resistance increases to the point where not enough current is flowing to the gas valve bimetal to open it up. As a result, the gas valve never opens up. BTW, a common symptom of the early stages of this problem is erratic temperature control in the oven due to delayed firing of the bake burner while cooking.
The hot surface igniter will not come on - check igniter with a ohm meter, you should have continuity through the glow bar, the glow bar can also crack = new igniter time. The glow bar comes on but the main burner will not light - you should have an amp probe to check properly, but often this is a hot surface igniter problem. The hot surface igniter often looses it's ability to get hot enough to open the gas safety valve. The safety valve can fail, but most times it is just a bad hot surface igniter. The hot surface igniter can also quit part way through cooking , in other words the oven may cycle a couple of times and then it just sits there with the red glow from the igniter. See this service sheet for the proper way and amp readings for the hot surface igniter system. Hot surface igniters do weaken and will eventually generate less heat than they normally could. When this happens they can still allow marginally correct current to flow to the oven gas valve for it to open but not get quite hot enough to ignite the gas burner immediately. When this happens, gas released into the oven can sometimes build up to the point where when finally ignited, the amount of gas lit can cause a small explosion inside the oven or cause an odor of gas with out the oven working. Yes, your glow bar igniter can glow orange-red and still be bad!! How a common gas valve works - click here.
Let me know,if needed further assistance.
Hope i helped you.
Thanks for using ' Fixya ' and have a nice day!!
Aug 13, 2011 | Maytag Microwave Ovens
My goodman heater is a forced hot air gas heater and it will not fire up. the Glow plug lights up but I can not get a flame.
This sounds like the gas valve is either not opening, or you do not have gas at the unit. After the hot surface igniter glows, you should here another click a little bit afterwards. This click is the gas valve opening, then blows through the burners. Make sure there is gas to the unit first, and if so, the valve may need to be replaced. You could also have a problem with the control board or even the pressure switch sometimes. Hope this helps or at least points you in the right direction.
Nov 11, 2010 | Goodman GMS90703BXA Heater
Oven will not come on
This can be caused by a weak/inop hot surface igniter or a defective gas control valve. First you will need to verify that the hot surface igniter is coming on(you should see it glow in the burner compartment). If it is not glowing then you will need to verify that the wiring harness has voltage to it when the oven thermostat is on. Also check the igniter for any cracks or damage and if found then replace the igniter. If it is glowing then one thing that you can try(be very careful doing this) is to give the gas control valve a light tap with something hard like a wrench when the oven is turned on and the igniter is glowing but the burner is not on. You will need to remove the broiler/storage drawer at the bottom of the oven. Once you pull the drawer out you should see the gas control valve at the back of the range. Try turning on the oven and lightly tapping the valve housing after the igniter is fully on. This may loosen up any debris inside the control valve housing that might be causing the problem. If the oven burner comes on then try completely turning the oven on and back of several times. And when I say completely I mean turn it on after the igniter is not glowing and burner has shut off. This works about 30% of the time. If the burner control valve sticks again after trying this procedure then it could be the control valve and/or the hot surface igniter defective. The hot surface igniter would need to be disconnected from it's harness and tested with an OHM meter. Most igniters should have a 500 to 700 OHM reading. If you get a reading that is way off then the igniter is defective and replace it. If the igniter tests good then the gas control valve is suspect and replace it. Most appliance parts retailers will test your igniter for free. When the igniter is on it should glow very brightly. If it is dim then that is a sure sign it is bad. You can also verify that the oven run-away valve is not closed. This valve will be located at the back bottom of the range at the gas regulator. There will be a tab on the regulator housing where the gas pipe goes to the oven. This tab will lift up to close gas flow to the oven. Sometimes these valves can stick causing the oven to stop working. You can try moving this tab back and forth to see if it loosens any debris in the valve. Move the valve while the oven is on and you will be able to hear the burner come on after moving the valve if that was the problem.
May 07, 2010 | Whirlpool GS460 Gas Kitchen Range
When i turn oven nob no gas will go to oven burner to lite oven. took apart oven hose connections and did not smell gas. thanks
Hi, The problem is with the ignitor 9 out of 10 cases. On oven's with hot surface ignition the ignitor act's like a resistor, (not litrally, just an example to help) when it is good and glowing almost white hot, it will only then open the gas valve to lite the burner. (don't let the fact that it is glowing to a lesser degree fool you as often it does with do-it- yourselfers or even technician's not familiar with them) A common ignitor for Maytag ovens is 77001258 and usually retail at $40-$50. Check with your local part supplier or any number of on-line vendors using your model & serial number. Hope this help's, if so please take a second and rate the solution I provided for you here at fixya...and spread the word. Thank you and good luck. macmarkus :)
Dec 07, 2009 | Magic Chef Ovens
My Amana gas oven won't heat up gas smell strong
Sounds like a sticking gas valve or a defective hot surface igniter. Open the broiler drawer or remove the bottom cover in the oven compartment. The oven usually has a hot surface igniter or a spark igniter. Turn on the oven and watch for the hot surface igniter to start glowing. It should glow very bright. Once it is glowing the burner gas should come on. If you hear the gas come on it should light right away. If there is any delay shut off the oven and stay back. Let the gas clear out then inspect the area near the igniter and make sure the burner is not plugged(the little holes may have debris in them). If you turn on the oven and the igniter comes,glows brightly,no gas is heard but you can smell gas it is either a blocked burner orfice/assembly or sticking gas control valve. Try giving the burner and gas control valve a tap and see if it comes on. If you tap the control valve and it starts working then shut of the oven and try it several times. If it starts to come on and off now you may have cleared whatever debris was causing the problem. If it does it again then it could be the control valve or a weak hot surface igniter. The igniter can be tested with a ohm meter. Most of the time when I get this complaint it is the oven control valve that is sticking. Be very careful when doing these procedures....gas can build up in the oven compartment very quicky and flash if ignited. Always have the gas shut off valve at the back of the range within reach and the electrical outlet in case you need to unplug it.