Have Coleman-Evcon heat pump system. Model DRHS0421CB. Condensing unit has intermittent no run condition. I replaced the contactor, as it was a few years old. I eliminated the thermostat from the equation by twisting together the RYO wires at the thermostat sub panel. This makes the air handler run and MOST of the time also makes the condensing unit come on as well. When it does run together, it cools great. Suction and discharge pressures are normal. The float switch is ok and no water present in pan. But after about 10 minutes, the condensing unit cuts off (ie fan and compressor)with the air handler continuing to run. Upon inspection, I find that the contactor is not pulled in, due to the fact that the 24 volt supply has been lost somehow. I found a loose wire on the defrost timer board, which when jiggled, clicked a relay. I thought I had surely found the problem. The unit ran normally for 10 minutes then lost the 24v to the contactor again. Jiggling did not do the trick this time. When the contactor is pushed in manually, the comp/fan kicks on.
  • 788 Answers
Elimate the items not needed to test the unit.
Disconnect the defrost power board and set air handler to run.
Disconnect the thermostat and hold contactor switch in closeing connections to the compressor and condensor fan.
If the unit shuts down while these connections are closed, it could be one of two things.
First, do you have high and low pressure cutoffs..???
Second, Their is a thermo by-metal cut off at the base of the compressor. This unit will open circuit to keep compressor from over heating.
I would remove the board with loose connections and have it repaired.
Next, I would look at the board and see if relays are opening and closeing correctly.
Last of all, have you checked your pressure switches ?? High ab nd low side pressures ?
It looks like you know what you are doing, so give it a shut, but I had to ask. !
Get back to me and let me know what you have found.
Hope this has helped you.
Posted on Oct 05, 2009
Coleman electric furnace
You don't say whether you replaced the blower but that could be the next thing to check
Jul 23, 2013 | Heating & Cooling
I have a heat pump. it stays on i have to turn it off by the breaker. also my ac only blows out warm air what is my problem
You may have a bad thermostat, keeping the unit on,or the compressor contactor in the condensing unit outside seized shut. When contactors get older they can kind of melt the contacts together.This would also cause it to run in heat mode.
Jan 08, 2011 | Coleman Heating & Cooling
I have a evcon eb12b heat pump, it works intermitantly on heat, ihave replaced the contactor, and have 24v at the contactor, come times the heat pump will come on sometimes it wont, The hvac repair guy...
does this unit have a capacitor that is hooked up to the motor, as it may be the capacitor or motor, of course this is just a guess as I am not there to see it. I guess you can push in the contactor a few times and make sure all is coming on like it should, might be the control board. Just a matter of pluck and chuck. Good Luck Tim
Oct 24, 2010 | Heating & Cooling
My Coleman Evcon heating and air unit will not blow air
bad blower motor. recommend a new blower motor and capacitor.
May 28, 2010 | Coleman Heating & Cooling
Coleman Evcon BGU12520A won't ignite
check the ignitors condition is it cracked broken burnt out etc , ifn so then it will need replacing , or check the pressure switch is working try jumping it out and see if the ignition glows ,
Apr 09, 2010 | Heating & Cooling
No heat at night
You have a poor low voltage connection from the thermostat or a bad contactor.The contactor is the main relay control inside the condensing unit. The incoming voltage wires connect to it.
Contactors are inexpensive. I would change that first.
Check all your low voltage wires in the condensing unit for loose connections.
Dec 11, 2009 | Coleman Heating & Cooling
I have a Coleman Evcon Heat Pump Model DRH50481CB runs for a couple of minutes then shuts down.The pressure readings are good when it shuts down.If I wait for 15-30 minutes it will run and do the same...
Sometimes there is float switch inside. It open when you have stopped up drain. It could be tripping and slowly draining and bringing the unit back on. Check this first. Evcon did not put low pressure controls on there units. Could be bad capacitor also but check float switch first. Russ
Jul 19, 2009 | Heating & Cooling
Air conditioning runs all the time
I assume this is a manufactured home, this is probably a two transformer system, either your contactor is welded in the on positon or wyou have control wiring issues, (could be the thermostat)
Jul 12, 2009 | Coleman Heating & Cooling
I have a coleman/evcon heat pump. When the thermostat kicks on the contacts kick in and hum but the compressor nor the fan run. Is this probably my capacitor has gone bad?
I would check the hig voltage power supply to the unit. Check the main breaker and make sure it is on. Check the disconnect and make sure there is power at that point to the condensing unit. The contactor will kick in from the low voltage in the control circuit.
Jul 11, 2008 | Coleman Heating & Cooling
Heating & Cooling Logo