Question about Exide POWERWARE FERRUPS 7KVA/5KW (fk100ac4a0a0a0a) UPS System
How about a ferrups 18kva? Can I lower the frequency required to 55hz? The panel only let you go to 57. Or bypass the low frequency? It's having a problem hooking up to a 48kw generator.The ups is running about 55% load
  • john785 Oct 05, 2009
    This is a Best Power UPS, before Powerware, before Eaton. My specs show a range of 57 - 63 hz only. You can input anything in this range, but no wider, even with the factory password. Someone should know a workaround I hope.
    Top Expert:
  • 79,077 Answers
You can't alter the HZ to anything other than the 57-63, this is hard wired into the system and no further adjustment is possible.
Posted on Oct 05, 2009
    President:
  • 1,653 Answers
The mfr spec for the whole range up to the 36kVA unit clearly shows that it accepts an input frequency of 45 Hz to 65 Hz to maintain a 50Hz or 60Hz output + 0.1% so I am surprised that you seem to be restricted to 57Hz on the control panel. Even with the normal standards on UPS they normally accept an input frequency variation of + 10% which would allow the 60Hz to go down to 54Hz. And up to 66Hz. This sounds as the controller may have an error and as such you should contact Exide or your maintenance company to ascertain why this should be so. Sorry I cannot offer any better information.
I have a "low A/C output" message. Is this related to a faulty DVR or another board?
From the user manual: http://lit.powerware.com/ll_download.asp?file=Eaton%20FERRUPS%20User%20Guide.pdf page 108.
The output voltage is below the alarm setting as determined by setup parameters 59 and 60.
Verify the output voltage using a voltage meter. If correct, verify setup parameters 59 and 60. If alarm condition continues, bypass the UPS and turn the UPS switch off. Call your service representative.
Mar 17, 2015 | Powerware FERRUPS FE4.3 - UPS - 4300 VA
Tip
Generator Not Producing Power - Engine Speed & Governor Control
There are 4 requirements that have to be met before a generator is able to produce power. Due to number of questions that have been asked, a Coleman PowerMate 1500-1850 with a Briggs and Stratton Engine will be used here.
1) The Engine has to be turning at correct speed
2) Field Winding (Rotor) on the alternator must be energized
3) AC Winding (Stator) must create a voltage in presence of magnetic field
4) Output passes through Safety Devices before it reaches an outlet.
This Tip will cover Engine Speed and Governor Control.
Sounds simple, but it actually goes beyond just turning. Most consumer generators are designed for an engine that turns 3600RPM for 60Hz operation. For every 600 RPM, the frequency changes by 1 Hz. Normal frequency range on a generator is about 63 (at no load) to 57 (Full Load). At half load, you should be pretty close to 60 Hz. Some generators will turn at 1800 RPM, and usually have two or more cylinders. Each 1Hz deviation is a 300 RPM change in engine speed
If you find that your engine is not turning as fast as it should, or is turning too fast, you can adjust its speed using the governor. Be careful in this area though! If you are adjusting faster, and you make too much an adjustment, the engine may over speed (red line) and be damaged. Always be ready to shut down the engine in case something goes wrong.
General Instructions on How to Adjust Speed:
It will almost be required that you have a digital multimeter that is capable of measuring frequency. You can use a AC powered clock, and compare the minute intervals with another clock, but the adjustment process will take a few hours.
Start your generator, let it run for a few minutes to warm up. Place your meter leads into the outlets, and record the frequency. This will be your No Load Frequency prior to any adjustments. Also record the voltage.
Note that depending on your meter, your voltage will likely read about 132 volts AC. If your meter is of the dollar store variety, the voltage may be reading higher (170) due to noise being present in the waveform. Don't worry about this - yet.
Now that the engine is warmed up, and your meter is indicating that the frequency is less than or higher than 63Hz, it is time to adjust the governor. Each engine will have its own method, you may have to find a owner's manual or service manual.
Start by removing any access panels that you need in order to reach the governor assembly. This will be the arm that is attached to the throttle on the carburetor via springs and rods. Look carefully near the base of the governor arm, and you will see a spring that is attached to it, and the other end is attached to a tab. The purpose of this spring is to put tension onto the governor, as well as to allow adjustment. Inverter based generators will usually have an electronic governor. The throttle is actuated by a small servo motor which is driven by the inverter / controller. These types of governors are typically not adjustable beyond replacing mechanical linkage that is worn.
Using a pair of needle nose pliers, bend the tab slightly one direction or the other (toward governor, or away from governor). Note the change in frequency. The target here, without a load, is going to be 63Hz. Once you hit this target (frequency average is 63), take a look at the voltage. It should be near 132 volts AC. If it is much higher, then lower the voltage by bending the tab slightly. Be aware that this will also lower the frequency as well.
Now that the unloaded frequency is set, connect a load that is approximate half of the generator continuous rating. For an 1800 watt generator, the continuous load is 1500 watts. Half would be 750 watts. A couple of Halogen lights will work, as well a space heater that is set on Low. Your frequency should be very close to 60Hz now. Voltage will likely be around 125 volts. Adjust the governor very slightly to reach these numbers. Your half load frequency is now set.
If you are using a space heater for a load, turn it on (1500 watts), and note the frequency reading. Also note the voltage rating as well. Frequency will likely have dropped down to about 57 or 58. This is normal. Voltage should be down around 110 to 115. Don't make any adjustments as most generators are due not carry full loads for extended amounts of time.
Turn the heater back to low or fan only, and let it cool for a few minutes before turning it off. Unplug the heater, and check the frequency and voltage without a load being on the generator. Again, frequency with no load should be about 63Hz, voltage about 132. A little bit of difference is acceptable here. And now you are done.
If you are not able to obtain the numbers mentioned, then there are other issues going on. Especially if voltage is out of range. See other Tips.
If you intend to use the generator primarily with a certain load (heater, well pump, charger, etc) you can optimize performance of that load by setting the generator frequency with that load, and only that load connected. Just keep in mind that when you add additional loads, your settings may not be adequate.
on Sep 12, 2010 | Electrical Supplies
Need a part number for the fan. best ferrups 5.3kva
Suggest you give Eaton a call. They purchashed Powerware/Best Power and still sell and service the FERRUPS:
Toll Free: 1 800 356 5737
E-mail (Hardware): SinglePhaseTS@eaton.com
Mar 07, 2011 | Powerware FerrUPS 5.3KVA (fj340aa0a0a0a0a)...
Replaced old 12 V, 33 AH batteries for Ferrups 3.1 UPS. Within a min from starting the UPS, those two huge capacitors (situated on the Top Rear, when you remove the Cover, furthest when you see from the...
Mike Decamp is clueless. That is not a answer. The UPS has large DC capacitors. These do go bad over time. The capacitors are required to maintain a good DC Buss and helps in assisting when putting the UPS in bypass and back online. You can not turn on the inverter with out precharging the capacitors. Get the part numbers of the caps and replace. Make sure UPS and batteries are off or you will get shocked.
Jan 27, 2011 | Powerware Ferrups 3.1kVA L5-30P (3) 5-15...
I hooked up a compter to rgb-pc port and selected rgb-pc input and started computer the display comes up ok then it says invalid format how can i fix this russellwidmark@aol.com
CHECK YOUR GRAPHICS CARD DISPLAY PROPERTIES IE:
REFRESH RATE FREQUENCY 55HZ 75HZ ETC. YOUR TV MAY ONLY WORK WITH THE CORRECT REFRESH RATE AND COLOUR RATE CHECK YOUR USER TV MANUAL FOR SETTINGS
Aug 25, 2010 | LG 32LG30 32 in. LCD HDTV
My computer is not responding
dude just check the bios first !
it the bios works then check the cpu adn the ram
it has to be one of these normally !
Jan 29, 2010 | Biostar GF7050V-M7 nVIDIA GeFORCE 7050...
I have the Sony XS-L120B5D subwoofer with enclosure: sensitivity-89db RMS-600 watts Peak-2000 watts impedance-4 ohm frequency rangh-20hz-2000hz its hooked up to an Arc Audio ks 300.2 amp: class-g/h power...
Do you have the crossover switched to "low pass"? and the frequency control below 80hz? Do you have the manual? If you need more help, post a comment and I can walk you thru it. Hope this helps
Jun 24, 2009 | Sony XS-L120B5D Dual 12" Ported Enclosure
I have replaced that batteries in a Ferrups FE7 UPS system. The charger kicked on, all voltages are correct, but "Low Battery" alarm is still active - how do you reset it?
wwright3 has no clue. There is no "On" button. Push "Control"(Red Button) then #2 (Auto button) Enter and Enter to confirm. Then is't online. Make sure the battery breaker is closed if you have that option.
Apr 27, 2009 | Powerware FERRUPS FE7 UPS System
Ubuntu Monitor
It's a monitor design quirk causing that.
You got the message because Ubuntu read the info your monitor fed back to your videocard and somehow understood it could run the monitor at a higher or lower frequency than the monitor can really work with; say, 120Hz rather than 70 or 55Hz refresh rates.
 If you don't even get the first logo menu, try hitting either down-arrow, then enter, or F4.  Those correspond to menu choices to boot in failsafe graphics mode or get the menu in such a mode.
Sep 10, 2008 | Canonical Ltd. Ubuntu
Diagnal Interference Lines
the diagonal lines represent some low frequency interference (close to the supply frequency - 60 hz). Try to keep the unit away from other appliances, especially the left back zone - where the tuner is. Also, you have to do some experiments on the cable connections: disconnect other cable devices (internet modem, home phone, other tv/tuners), one of them might inject these signals into the cable. Keep me posted
Aug 25, 2006 | Toshiba DR4 DVD Recorder
Open Questions:
Toshiba Virus Removal ' Remove Toshiba Virus - DataAlign ' Call +1888784-9316 Toshiba Corporation is a Japanese multinational company that is headquartered in Tokyo. It produces products and services like information technology, communications equipment and systems, electronic components and materials, power systems etc. Toshiba products are innovative and cost efficient which provides best solutions for home or business use. Toshiba has become the world's seventh largest IT Company which launched its first laptop in 1985. All Toshiba products have the best qualities like high efficiency in very affordable pricing, innovation at its best, ultra- portability with faster working laptops and desktops. As known by everyone, every Toshiba user require good Toshiba Customer Care and thus requires a good customer support. Likewise, Toshiba laptops also require a reliable support for the proper working of Toshiba laptops and desktops over a longer period of time. Dataalign provides best in class Toshiba Tech Support exclusively for the Toshiba customers. Dataalign tech support is provided by the highly knowledgeable and expert technicians who have years of working experience in this field and these tech support engineers have been particularly trained to be able to solve the issues related to Toshiba products. Toshiba Support of Dataalign has following features: 1. Slow speed issues are resolved. 2. Toshiba support technicians of Dataalign analyze the issue very carefully and follow proper trouble shooting steps to get to the real cause of issue for properly suitable resolution. 3. Blue screen of ***** and other errors are resolved. 4. Issues like virus, malware, spyware is resolved accurately. 5. Tech support experts providing Toshiba Support to the Dataalign customers have years of experience in the field of providing helpful assistance to customers with accuracy. 6. Dedicated staff with lots of knowledge makes the support team of Dataalign the best. 7. Customer satisfaction is taken care of every time. 8. Highest productivity is ensured after services to Toshiba laptops. 9. Resolution is provided over remote access so that Toshiba customers can witness the issue and the overall process of resolution applied. 10. Toshiba Customer of Dataalign works 24/7 and 365 days a year. For any kind of help in Toshiba products contact on the Toshiba Tech support number of Dataalign :- +1888784-9316
May 23, 2018 | Toshiba Computers & Internet