The outdoor unit will turn on and run for about 30 sec, shut off
The outdoor unit will turn on and run for about 30 seconds and then shut off, it keeps repeating this, all the while the blower inside will continue to run. any idea why outdoor unit is doing this?
    Sergeant:
    Champion:
  • 232 Answers
Low on freon, cycling on low pressure switch
Posted on Oct 05, 2009
My unit stop working I turn power off and on the unit ran for obout 5 second blower didnt turn on The air only option works on thermastate and blower airI check unit outside and was real hot .
I don't understand. It sounds as if your outdoor fan is not running and is shutting down on thermal overload. Check capacitor in outdoor unit. Good Luck.
Apr 29, 2017 | Heating & Cooling
I have a fujitsu air con which is flashing 3 times on the timer. It runs for 10 seconds and then shuts down and then flashes 3 times. Model is a AOTR09LCC
Serial signal (reverse) error, during operation.
Try turning power off at isolator for ten minutes and then switch back on. If error code persists, you will probably need a new controller PCB in the outdoor unit.
When the indoor unit does not receive the signal for 10 consecutive seconds during the operation >Permanent stop after 30 seconds.
[Diagnosis Point]
Check the indoor /outdoor cable connection (in order). If the cable wiring is not abnormal, measure the voltage of the outdoor
unit terminals and diagnose the defective location.
(Refer to the after mentioned [Serial Signal Diagnosis] for the voltage measuring method and diagnosis method.)
Feb 19, 2015 | Fujitsu Heating & Cooling
Daikin code e9 expansion valve ?? How do you test ?!
Turn the isolator switch on the outdoor unit to off wait 30 sec then turn it back on you should hear a ticking sound coming from the outdoor unit when u turn the unit on. if u can hear the ticking sound that is the EEV working then it is possibly a board fault. You can check the motor by doing a diode test. If you are unsure get a new EEV and replace it they are about $90 and to change it they just pop off.
May 01, 2014 | Heating & Cooling
Even I turn of the indoor unit via the controller , the outdoor unit is still running. I turn off the breaker and turn on still the the outdoor unit still running. What do you think the problem is?
Usually when this occurs it is a contactor burnt shut. If left to run, it will freeze the outdoor condensing unit into a block of ice. The contactor activates the compressor and
fan and the contactor is controlled by the low voltage from the thermostat. If the contact points are burnt shut the thermostat becomes of no use in controlling the outdoor condensing unit. The solution is to replace the contactor. Make sure all power to unit from all sources is shut off before attempting to replace. Hope this is helpful.
Jun 01, 2011 | Frigidaire Heating & Cooling
Is it normal for the outdoor unit on my coleman h/p to make a surging humming noise? the fan does not run during this period, approx. temp. is 28 degrees F. the fan runs 30 seconds befor the unit...
Sounds like your unit is going into defrost mode. When this happens the fan in the outdoor unit shuts off so you get more heat in the outdoor unit to defrost the coils. The heatpump is basically in A/C mode during defrost and the electric heat strips will kick in so you don't feel a cold blast of air in the house.
Jan 03, 2011 | Heating & Cooling
AC Condenser motor will stop at 1pm but inside unit is still running but no AC. If I turn the AC unit breaker unit off and then an hour later turn it back on. The unit runs fine all day until 1pm. Had a...
Hi, the tech should have been able to figure the stat out with out a manual to see why the condenser is shutting off at 1:00 P.M. This is unusual for this to happen, unless it was winter and this is a heat-pump going into defrost, but just the fan would shut down. Does this unit have a box on it that was installed by your electric company that shuts the unit off during high peak conditions in the summer? This would cause it to shut down at the same time everyday. If not, it would have to be something in the thermostat that is set for it to shut off at that time. It still does not make since, as it would shut both the indoor and outdoor unit off, not just the condenser. Are you saying that just the condenser fan motor is shutting off, but the compressor continues to run until it shuts off on high head pressure when the fan stops, or does the complete outdoor unit shut down fan, compressor and all at that time??. It sounds to me like this outdoor unit has a time delay relay that has a fault in it may be shutting it off at this time daily? Please let me know if its just the condenser fan motor that shuts off, or if the complete unit is shutting off all together, this will help .
Sincerely,
Shastalaker7
A/C, Heating,
Sep 08, 2010 | Carrier 38CKC060 Air Conditioner
On my window unit the compresser only runs for 15 sec. and shuts off for 4 min. the fan stays running.. its not cooling the room
possably a problem with the outside condensor fan motor. Pls check
1.) when unit is running is the outside fan motor also runnng. My guess is the outside fan is locked bad motor ect. Unit would only run maybe 30 seconds before cycling on its overload
May 04, 2010 | Whirlpool ACE244XS Air Conditioner
WE have Amcoraire Mini split unit heat pumps. One is
P 4 code means problem with the outdoor unit, Most likely low on refrigerant. Check all copper pipe connections for leaks first, then add refrigerant after checking pressures.
Jan 17, 2010 | AmcorAire UCHW-H12AF2 Split System Air...
Open Questions:
Heating & Cooling Logo
48 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen