Question about Ruud UAMB Air Conditioner
Heat side of heatpump is blowing a transformer when switched to heating mode.
  • Johnny
    Johnny May 11, 2010
    any recent work done to the system?
  • 3,361 Answers
It is either a shorted wire or a shorted component in the heat cycle wiring. The most likely is a bad reversing valve solenoid. You can use a re-settable transformer to help lower cost while troubleshooting. Remove the RV solenoid wires and set the unit for heat. If nothing blows,you will have found the problem. If it is not the RV,plug it back in and remove another low voltage wire and restart the unit. Keep doing this until the unit runs. When it runs OK,the last wire removed will go to the defective part.
Posted on Oct 04, 2009
What would make the indoor fan stay on when thermostat is satisfied by heatpump it does not do it when ran in auxillary heat mode it cycles off like it should
One of the safeties has the unit locked to keep the fan running. Probably a high temperature limit switch.
Usually a unit that has been runnung for longer then normal in the heating mode causes the heat exchanger to get really hot and causes the safety to trip.
The safety will lick out the heat mode and cause the fan to continually run. Other then that it could be the fan limit switch or a bad board.
Jan 19, 2016 | GE Hybrid Heatpump Geospring Water Heater...
Had 16 xi Trane heat pump installed 3 years ago. It ran well for the first couple of years. It began to stop heating and would blow cold air only. Have tried both aux heat and reg. heat to run and neither...
That's a complicated system that needs a qualified technician to service it. Lots of people can install them and they run fine, for a few years. Your indoor unit, operating on 2 heat elements, will feel like its blowing cold air even though its heating, just not so well. And not like you are accustomed to. Each element (5kw)=22.7amps, on average. So 3 elements operating should trip a breaker. Its probably been operating on 2 heat element plus the heat pump. And now you have trouble with the heat pump. If you can't TRUST the guys working on your equipment, try someone else. A second opinion. Normally a 3 or 4 ton unit will have 15kw heat installed, heatpump or not. 5 ton, 20kw. If yours is a 3-4ton, cooling, the 100amp(or normally two 60 amp) breaker should have been installed upon equipment change out. If yours is blowing cold all the time, something is wrong with your heatpump. The electric heat inside operates only when the heatpump can't keep up(real cold outside), the heatpump is in defrost(then it's actually in cooling mode), or if you have the tstat in aux/em. heat. Try a local trane dealer? Of a technician with 15-20 yrs under their belt. A trane dealer should have trane tech support also. BIG HELP!!!
Mar 01, 2017 | Haier Energy Star ESA3183 Air Conditioner
2005 s type jag a/c quit blowing cold air suddenly .just blows hot at any setting or on auto
hi,is this a heatpump or a ac unit only...if a heatpump ,there is a valve that switchs from heat tocool mode...go outside with unit running..put hand on big copper line,if it is hot your in heat mode..if cold your in cool mode....possible stuck change over valve if a heatpump...hope this helps...good luck...michael doctor airr appl.repair..843-384-8474...if need more assitance..call..its free...good luck
Mar 26, 2010 | Heating & Cooling
I Have a honeywell RTH2410 Thermostat I wired it without the blue wire which used to go to X on my old thermostat. Now it comes on with aux heat all the time and I have a Heat Pump. How can I fix this?
What was the old thermostat labels and the wire colors that went to them?
The typical heatpump wiring Terminals are:
R = Red = Hot side of Transformer
C-B-X = Common side of transformer Depending on brand of heatpump
Y = Yellow = Cooling Contactor
G = Green = Furnace Blower
O = Orange Reversing Valve Energize to Cool
B = Blue Reversing Energise to Heat Depending on brand of heatpump.
W2 = White = Auxiliary Heat
You need to be sure where each wire comes from when you connect them to the new thermostat.
The best way to do that is to go to the furnace and see where they are connected. R-Y-G are probably correct, you need to see where the Blue wire comes from and determine what the X terminal was on the old thermostat.
Dec 29, 2009 | Honeywell Electronic Programmable...
Thermostat Wiring Problems!!!
. your blue is probably common and if you hooked it to Y you shorted the transformer or blew the low voltage fuse. Green is fan, yellow is AC, Red is 24volt. Is it a heatpump or just ac? I think its probably a heat pump and your brown is your Reversing valve it needs to be hooked to O on the new stat. If its a heatpump your tstat must be a 2heat 1 cool stat w/ aux heat. Without knowing what terminals the wire were hooked to on the old stat you may have to look at whats hooked up at airhandler( furnace) and on A/C (heatpump) tobe able to determine what goes where on the new one.
Sep 20, 2009 | Heating & Cooling
Heatpump A/C not working
First,Turn on the heat cycle (Not Emergency)and see if the outside unit come on,If not,and you don't have low voltage outside,Go to the inside unit and test the transformer,If you have low voltage from the transformer but not outside,It is the low voltage wires,If you don't have low voltage from the transformer,It's the transformer.If you have low voltage outside when in heat mode,but the unit won't come on,It's the contactor.Let me know if you need more help.
Please take time to rate this fixya
May 13, 2009 | Goodman CLQ36AR49 Air Conditioner
Goodman heatpump. Crazy pressure in heat mode
Check the TXV valve on the outdoor unit, it could be stuck closed. We have been experiencing the same problems with the 410 systems and the TXV was the culprit. Good Luck
Dec 19, 2008 | Goodman CLQ36AR49 Air Conditioner
I'm having a problem with my heating and air system, my heat only works on emergency heat ( and run 24/7) if i turn it to regular heat it only blows cold air. i dont think my outside unit fan is turning( i...
If your Heatpump's fan isn't running but your compressor is, your fan motor is out. If nothings happening at all ensure your getting power to heatpump (ex: breaker tripped, fuses blown on outside power switch, or fuses blown in breaker box?)
Dec 04, 2008 | Heating & Cooling
Heat pump is not kicking in, no heat at 42 degree outdoor temp
HI,
Most likely has a freon leak , or a control problem causing heat to turn on, or if you have a heatpump the reversing valve has a problem.
Oct 10, 2008 | Amana PTH123B35AE Air Conditioner
Electric heat
pull cover off unit to expose the coil fins. on right side there may be a switch that turns with a screw driver that switches between heat pump and elec. heat. we use this to stop the heater from dripping water in the winter, for some people
Feb 04, 2008 | Amana PTH123B35AJ Air Conditioner
Ruud UAMB Air Conditioner Logo
76 people viewed this question
Top Ruud Heating & Cooling Experts
Bill Long
Tim Whalen
Dennis Boxerman
Are you a Ruud Heating and Cooling Expert? Answer questions, earn points and help others