Older model intertherm split unit. Compressor runs, but blower will not come on auto. I have to press the switch inside the unit.
  • gussie doucet Oct 03, 2009
    Thank you I will print this solution. My problem is at my fishing camp 112 miles away. When I go back I will give what you suggest a try. Thanks, Olan
  • 3,741 Answers
The same circuit from the thermostat to the indoor unit and the fan relays, etc. in the indoor unit is used to operate the indoor fan in both ON and AUTO mode. The exception is an internal connection in the thermostat/subbase itself from cool to fan which comes into play when auto fan is used. [the subbase is the part that is mounted on the wall and contains the switches] Try taking the ring off the thermostat and look for 3 itty ***** screws that hold the thermostat to the subbase. Make sure they are tight. Next, put the thermostat in cool/auto and see if you have 24 volts from G terminal to C terminal in the indoor unit. The terminals will be where the cable comes into the indoor unit from the thermostat. also likely the problem is in the fan switch sensor internally. check,keep us updated.please do rate and accept the solution.thanks
Posted on Oct 03, 2009
Thermostat not working
My guess is it has a low pressure cut off switch on it. When it runs with a low refrigerant charge it causes pressure in the refrigerant lines to go low, then the compressor shuts off (thats what the low press switch does to protect the compressor). When the gas warms up it expands and increases the pressure and the low side switch closes and starts the cycle again. Get it charged...problem solved!!
Feb 13, 2014 | Intertherm Heating & Cooling
I have a intertherm model e2eb-017ha the blower wont shut off i have to turn the braker off
One The blower relay is stuck in the on position. Two at the thermostat, fan switch should be set to auto. Set it on the blower wont quit.
Jan 29, 2014 | Intertherm Heating & Cooling
INTERTHERM HEAT PUMP/AC. BLOWER KEEPS RUNNING WITHOUT THE COMPRESSOR ON. SOMETIMES FOR HOURS. ALREADY REPLACED THE CONTROL AND LIMIT SWITCH.
Blower? Internal house air blower I assume. - Blower relay contacts pitted and stick in on position.
BAD Control BOARD, fault or adjustment program keeping relay energized. Bad emperature sensor not telling Board unit has use up cold air. loose wiring to sensors and board connections
Sep 11, 2013 | Intertherm Heating & Cooling
Intertherm Air Conditioner S3BA-042KA compressor and fan not working (has power)
It sounds like that unit is connected to a "power saving load controller" device from the power company. The power company can turn your unit on & off with a radio signal. If you manually activated contactor and unit ran. I would bet that the power company's device or the wiring connecting it is where the problem lies. Call the power company and have them check their device. If they tell you that the device has been tested remotely and is working fine. Explain to them that you can activate your unit manually and it works fine. They should not charge you to come out. Those "load controller devices" have a pretty good longevity record.
Jul 11, 2012 | Intertherm Heating & Cooling
Compressor will not stay on.
very good possibility that it is low on freon. If indoor unit is blowing ambient air, not cooling is happening. If this is the case and you are sure the compressor is running and then shutting off, the compressor could be overheating and the internal overload is taking out the compressor. If outdoor fan runs and compressor runs, probably cause. If capacitor is bad, unit would most likely not run that long. While unit is running, feel the large line at the condensing unit. If it is cold, and stays cold, could be something else going on. If stays warm, most likely low on freon.
Apr 19, 2010 | Intertherm P3RA-030K Air Conditioner
I have an intertherm electric furnace FEH-A020, with multispeed blower installed when A/C added. My problem is blower operation. at the end of the cooling season with fan set to auto operation the fan ran...
The model of T-stat you gave comes up as a discontinued model on Honeywell's web site, but it looks to be a manual stat that type of stat would have to be wired with a summer winter switch with electric heat, allowing it to turn on the fan with a call for heat. If yours is a programmable T-stat you would need to select electric heat or in the installers set up change the default setting for fan from unit controls fan in heat to thermostat controls fan.
Oct 17, 2009 | Intertherm P3RA-048K Air Conditioner
No AC from older Intertherm split system
It sounds like you are low on refridgerant. Double check to make sure both fans and the compressor are running. If so then you have a refridgerant problem.
Aug 29, 2009 | Heating & Cooling
Intertherm S3QA042K compressor won't restart
You probably need a hard-start kit. A hard-start kit connects to the run capacitor and provides a starting boost for your compressor. If you install a hard-start kit, monitor your a/c for a while because it is possible that the bearings in the compressor are going bad.
Jul 30, 2009 | Heating & Cooling
Heating & Cooling Logo
32 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen