Intertherm gas furnace inducer centrifugal switch does not close in time. Blower works but furnace does not ignite
  • 334 Answers
Chances are the draft inducer motor is not pulling enough CFM through the heat exchanger.
That is usually due to either blocked/clogged flue pipe/vent.
damaged, missing or dirty fan blades.
or a motor going bad.
Check those three things first, as they are the usually problem. Other than that, it would be a sticking or bad switch.
If you s-uck on the end of the hose like a straw, while it is attached to the switch and it does not pull in then you are looking at a bad switch/cracked hose issue. If it does, then you are back to the draft inducer motor or it's squirrel cage fan being bad.
These are notorious for rusting and the blades breaking off.
Posted on Oct 03, 2009
Intertherm furnace ignitor will not kick on
furnace operation= call for heat- inducer blower motor energizes- pressure switch makes- after a few seconds ignitor activates.
If this series of processes is not whats happening the furnace may be going into a code safety. Call to discuss further=913-557-9111
Feb 25, 2014 | Intertherm 56000 Btu Gas Furnace
Furnace wont work
Have to know the model and serial of the furnace.
locate code list usually inside or on the back of a door.
Operation sequence= call for heat--inducer blower motor--makes pressure switch--signals board to bring on hsi--after a set time gas valve opens and you have ignition--main blower motor comes on after a set time
Feb 14, 2014 | Coleman 7990-319p Evcon Gas Furnace...
Goodman 95 %furnace keeps saying low pressure is stuck. changed out low pressure switch and high pressure switch and still have same problem.
That thang might be sensing a lazy flame. In other words the flames took too long in the board's opinion to quit sensing the flame. Yall probably need to do pressure tap on the gas valve.
Here is a realistic look at goodman fault codes and what to check fer and I am assuming you are not a tech and don't know this already and am hoping it helps:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Now here is how it should all go down:
Bottom dollar: it all goes back to type of gas, the initial setup, the pressure tap. and how it is wired up to begin with.
This will give you an idea where to start I hope.
Dec 10, 2010 | Goodman GMS80903BNA Heater
I have a newer tappan heater and get 4 blinks on led for error code the unit starts up fine and has flame but flame goes off when blower kicks on
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Heating & Cooling
Goodman unit. when i turn it on the blower fan and the exhaust fan comes on butit does not lite no flames at all. i don't even hear the gas click in.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Feb 15, 2010 | Intertherm P3RA-048K Air Conditioner
I have an intertherm gas furnace and it will turn on but it takse almost an hour from the time i turn the heat up until it kicks on. I can hear the click and it sounds like the motor is humming. I have...
Jan 23, 2010 | Heating & Cooling
York furnace model p2mpd12h06401f flashes 4 times for trouble code does'nt have code list inductor motor comes on but ignitor does'nt come on
Check pressure switch for inducer motor. If switch closes, check for crack in ignitor. If gas valve opens and you can hear/smell gas, the ignitor is bad probably. If pressure switch isn't closed you need to check for blocked vent/chimney/heatexchangers.
Dec 18, 2009 | York Furnace Draft Inducer Blower Fasco #...
Ruud furnace Model URKA A030jK08 Code opt 589
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
Nov 23, 2009 | Heating & Cooling
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
Nov 23, 2008 | Goodman GMS90703BXA Heater