Question about Goodman GMS90703BXA Heater
The igniter glows and the burner starts but shuts down after abou
The fan starts up and the igniter glows and the burner starts but shuts off after about 5 seconds, then the ignitor glows, the burner starts and stops, all about five times before the fan stops and everything is idle
    President:
  • 1,922 Answers
One of two things it could be the flame sensor or the control board for the entire unit
Posted on Oct 02, 2009
My good man furnace model gmh80903bnca will not get to temp fan shuts off and burners keep burning then kicks off on high limit then starts process over but never gets to temp set at 655
If you have a switch that can manually turn on the fan, try it to verify the fan works. This is what I think is happening. The normal operation should be thermostat calls for heat, inducer fan comes on, pressure switch closes, igniter glows, main burner ignites and then in 30 or so seconds the fan comes on and stays on until the thermostat is satisfied. Once the thermostat is satisfied the burner shuts off and the fan runs for approx 120 seconds then shuts off. I think the control board that automatically turns your fan on is faulty. On most modern furnaces if the auto fan control fails and the furnace gets to hot and limits, when the limit opens and shuts off the burner it also energizes the fan motor to cool the heat exchanger.
Jan 13, 2018 | Heating & Cooling
Bernz omatic patio heater starts runs and shuts down
Look for a check the regulator for gum & build-up...it willp cause the burner to go out soon after lighting.
Feb 24, 2015 | Heating & Cooling
Goodman furnace Model GDS80703AXBB -fan comes on then igniter light comes on, then burners turn on but shut off right away and wont stay lit. Now igniter light wont come on so burners not coming on at...
Sounds like either the flame sensor is not working.
The sequence for starting the furnace is:
1. extraction fan on
2. pressure sensor (for fan)
3. ignitor (spark or glow plug) comes on
4. gas valve opens up
5. ignition of flame
6. flame sensor (or temperature sensor)
7. plenum temp. sensor
8. main fan starts
It is most likely that the flame sensor is dirty or gone,
or (and I hope not), the module is gone and needs to
be replaced.
Sep 10, 2017 | Heating & Cooling
Furnace starts up blower starts..nothing ignites...then shuts down. repeats and doesnt stop...sanded igniter stick and nothing happend. flashes red once.
Do you see the actual ignitor glow? You must be saying that you sanded the sensor. The ignitor, after the little inducer fan comes on will begin to glow a bright orange until the burner lights. If the ignitor is broken, you will NOT see a glow, and you may smell a faint smell of gas.
Apr 14, 2011 | Goodman GMS90703BXA Heater
Air pro gas furnace model #g8c07512mub11a The combustion fan comes on the igniter glows red the gas fires in the burners for 5 seconds the it shuts down. Any suggestions would be helpful.
I would suggest you change the flame sensor. It will be a small diameter probe extending into burner compartment,usually over or inbetween burners. If your furnace is lighting the burners but they won't stay lit That Is what I would do first.. I also would turn thermostat to fan on to make sure you don't have a problem with the fan. Hope this helps you. Thanks
Nov 17, 2010 | Heating & Cooling
The thermostat is set to heat at a temp of 68 degrees. However,the thermometers temp read 71 and the blower was running and passing cool air. I tried setting the thermometers temp to 72. The furnace...
The burners are not igniting and the timer turned on the blower thinking the burners were already lit by then. You have a burner/ignition problem. Either the ignighter or themocouple is bad
Dec 31, 2017 | Goodman GMS90703BXA Heater
The exhaust blower starts for about 15 seconds then shuts off. several minutes later, the same thing happens - over and over
goodman furnance the exhaust fan starts, igniter glows hot, all burners lite up & will burn for about a minute and shuts down . I think it senses the room blower does not start so it shuts down.
Oct 20, 2009 | Ruud UBHC Air Conditioner
No ignition and E04 Code
The HSI (ignitor) has 2 wires, its like a cigeratte lighter, power is applied and it heats then glows red, the single wire you mention is the flame sensor, used by the control board (igntion module) to ensure the burner has lit or it shuts the power to the gas valve off but keeps the fan operating for a period of 1 hour till it resets.
It sounds like your ignitor is defective, it happens often, depending on your location, you may be able to purchase one, but I would advise having a service tech do it.
The manual for troubleshooting and repair can be found at this link:
http://www.staritepool.com/pdfs/MiniMaxNTServiceManual.pdf
Aug 14, 2009 | Pentair MINIMAX NT TSI IGNITER
Heater starts and then stops.
I will keep you posted. I have aquired all the service manuals and I am in the process of taking the heater apart. It is not the motherboard.
Mar 09, 2009 | Pentair MINIMAX NT TSI IGNITER
After a few heating cycles the burner does not ignite
The problem you are describing is usually associated with a bad gas valve coil. The dryer runs normally until it gets hot, then starts making a strange clicking noise. After it cools down, the dryer runs normally again. The gas valve coils (there are two of them) usually run about $20 a piece. I recommend replacing both of them at the same time just to be sure. I hope this helps.
Apr 15, 2007 | Maytag MDG3600BW Gas Dryer