Burner fires when calls for heat, runs for 5 seconds kicks off changed flame sensor still same problem
    Scholar:
  • 91 Answers
Make sure the flame sensor is connected good. If the terminals are dirty or corroded the board will not get the proper millivolt reading from the sensor. Also, remove the flame sensor and take emery cloth and clean the point where the flame sensor attaches to ensure a good contact point there.
Posted on Nov 04, 2009
Having problem with lennox furnace Model ML193DF090P48C-02.Furnace has been working but now and getting worse furnace will kick on 20 seconds or so but nothing.Igniter does not come on.When it finally
Usually when your flame sensor gets dirty, the igniter and burner come on for approx.15 seconds, then shuts down. After 3 tries it will lock the furnace out. You have to shut the power off to the furnace then turn it back on to reset it. You need to turn all the power off to the furnace and remove the flame sensor, clean it with some very fine steel wool and put it back in. Be careful not to handle the Sensor (metal) part with your fingers. Turn the power on and set your thermostat so that it will call for Heat. That should fix, it if not you may need a new flame sensor.
Mar 16, 2014 | Heating & Cooling
Burners kick on for 10 seconds then kicks off will keep repeating this
Hello, sounds like the flame sensor needs to be cleaned with steel wool. The flame sensor is a metal rod located on the opposite side of the igniter that senses the burner flame and will keep the Furnace running, what happens is the rod builds up oxidation and then cannot sense the burner flame and will shut the burners down and keep repeating. Just remove the sensor and clean with steel wool and reinstall.
Dec 08, 2011 | Weather King 10AJA3001AH Air Conditioner
Thermostat calls for heat, purge motor turns on, 15 seconds later hot igniter turns on, then gas turns on and burners are lit. Problem is, they only stay lit for 5 seconds then shut off and cycle repeats...
,Hello, Make sure the flame sensor is clean near the burners, The flame sensor is a metal rod that is on the opposite side of the ignitor. To clean the flame sensor you will need some steel wool, turn off power to the furnace and remove the flame sensor and clean it with the steel wool. After cleaning reinstall it and turn power back on to furnace.
Mar 02, 2011 | Goodman Heating & Cooling
Just replaced idnitor and flame sensor on a bryant model 376c and its still not kicking on. blower kicks on fans kick on and then cycles off. no heat need help
Make sure all wires are connected and the gas is on. Follow the sequence of operation for this model and a few tips on what could be the issue.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 27, 2010 | Heating & Cooling
Furnace not kicking on when thermostat calls for heat
Jan 10, 2010 | Heating & Cooling
My york diamond 80 fans come on and I can see the glow then it fires before cutting off after 5 seconds, is this a bad ignitor
Bad or dirty flame rod or burners.
Jan 09, 2010 | Heating & Cooling
Goodman Model C16-28 1FF is not able to heat my basement. The burners igniting but only fire for approximately 5 seconds. This cycle continues about every 60 seconds. At times the burners only stay on for...
Sounds as though your issue lies within the flame sensor.
The flame sensor senses that there is flame present once there is a call for heat. It sends its signal back the board or ICM and the furnace operates as normal. If no signal is sent, then the furnace automatically shuts down as a safety procedure. The furnace will attempt to light several times before shutting down on a fault code or lockout.
The number 1 reason for flame sensors to fail is they are dirty. Check the sensor for dirt build-up. Clean the sensor with a damp rag or a scratch pad. Inspect the grommets for crackings. Also check and clean all grounds. If this doesn't work, you will need to replace the sensor or call for a service technician to ensure the sensor is the only issue at hand.
Jan 08, 2010 | Goodman Heating & Cooling
Flame goes out when fan kicks on
If the flame lights all the burners within 2 seconds but does not stay on, you may need to clean the flame rod found at the farthest end of the burner box. It will be located at the end of the box that lights last. It will be a probe that is in the flame of the last burner. If it has carbon on it or scale, take an old tooth brush and scrub it. Check the wire connected to it and follow that wire back to the circuit board and check that connection.
Dec 11, 2009 | Goodman Heating & Cooling
I have a problem with my heating system. It is about 10 years old and has had the ignitor, combustion blower motor, and programable thermostat replace in it's lifetime. The system worked great last year....
sounds like its not proofing flame. it has a sensor usually like a needle sticks out into the flame that tells the gas valve the flame lit and is burning so its ok to keep sending gas, if its fails to proof flame then burner shuts down, then it tries to relight 3 times then locks out on fail safe. the blower will sometimes run continually once that occurs to highlight a failed condition. every time you reset it will try again 3 times then shut down. lp gas is very dangerous, even i do not work on it as the gas acts like gasoline and lays around. not like natural gas that disperses well. if you see the flame sensor try gently cleaning it with a little emory cloth. also a loose ground can cause this. check tio be sure any green wires are snug , they actually flow volts to ground through the flame on some to proof, thats why no ground no flame. if that fails then the board is most likely problem. change wire for wire , or get generic replacemant and follow directions exactly. good luck.some ignitors act as a flamre proofer as soon as they are done igniting! rarely do they fail to perform both funtions.
Nov 20, 2008 | Heating & Cooling
Heating & Cooling Logo
46 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen