Question about Carrier XHB123D X/Y Series Heat/Cool Air Conditioner
Furance not staying on
I'M TRYING TO RUN THE HEAT FOR THE FIRST TIME AND THE FURNACE COMES ON THE COILS LIGHTS UP, BACK FLASH OR FLAMES STARTS AND SHUT DOWNS. WHAT CAN BE THE PROBLEM?
  • 334 Answers
The flame sensor is not sensing flame.
You can try cleaning it, but will probably have to replace it.
When the sensor does not detect flame after ignition, it will shut down the gas flow.
Posted on Oct 02, 2009
Have a gmp125-4 furance blower runs all the time checked themostat wires error code 1 blink then 2 then 3 then 5 furance works if you turn power off turn back on when heat kickes off blower comes on gives...
Sounds like limit switch issue. Furnace heats up, high temp limit switch opens, fan will stay on. GMP model is older and do not have the codes.
May be over fired, have airflow problem, to cause the limit to open.
Next time before shutting off power, try to find the limit, it has two wires that connect to a 1.5 x 2 inch card mount to the furnace fire wall. tap on it and see if the blower stops. If so replace the limit.
Sep 06, 2011 | Goodman Heating & Cooling
My girlfriend has a forced air Goodman furnace in her house. Her furnace has been not running well. Whenever the filter gets dirty the furnace does not run right which it to be expected. The problem is...
where is the thermostat located? i should be on a inside wall in a comon room and not around lights, computer or heat vent or air return. a thermostat is just a switch and will operate in its enviroment. does the fan cycle off before the heat starts blowing again? the fan on these are on a timer that the t stat will have to "brake" open on reaching temp to shut off. not knowing where your at look this over and i hope it helps. i dont think i would let someone sell me a control board for this problem.
Feb 08, 2011 | Goodman GMS90703BXA Heater
Unless we set the thermostat very high, like 80 degrees, the heater will blow cold air. When the heat does blow, it will eventually stop blowing heat and the fan will continue to blow cold air.
Check and make sure the filter is clean. This sounds like a restriction in the system. If the unit has central cooling make sure ther indoor evaporator coil is clean at the furance.The unit may be cycling the burners on and off at the high heat limit , fan/limit control. You can also eliminate the thermostst from the furance. Turn power off at the furnace and disconnect the wiring from the thermostat. Jumper the red and white wire together. Turn the furnace back on. The furance should run in the heating mode. Try this and see if the problem is still there.
Jan 25, 2011 | Heating & Cooling
Rheem 3204-80D furance. Turns on and fan starts. Then in about a minute the fan shuts off.
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Heating & Cooling
Having a problem with a goodman gas furnace, pilot starts and burners fire up, blower starts and burner goes out after like 5-10 seconds. Blower continues to run but only circulates cold air. burner does...
Sounds like the rollout is being tripped from the blower moving the falmes. i would have your heat exchanger checked for cracks or holes as this is usually the reason the blower moves the burner flames to tripp a rollout.
Feb 22, 2010 | Heating & Cooling
Had Team Comfort Installed a new furnace last year. House was not warm in the winter. Furnace starts and shutdown very frequently and not heat up the house. Sometime there are poping sound. The first...
if you live in the arctic i guess a 120k furnace would be ok. that is a huge furnace, depending on what part of the country your in you could heat 3 times that w/ 120K
dirty yes dusty no but as long as you have a good filter in the system it will be ok.
gas valves rarely go bad and a chimney liner is required often times,or a chimney friendly kit.
Call your county inspection office and see if they pulled a permit, its required by law. and if they didnt, make them, Then have an inspector come out and evaulate
Oct 31, 2009 | Heating & Cooling
Goodman Furnace Lights But Won't Continue to Run
The flame sensor is dirty. You can not see the build up on the sensor but enough build up will change the resistance and the furnace thinks there is no flame.
To clean the sensor, first you need to locate it. it will be a sensor located in the path of one of the flames. Once you locate the sensor, open the bottom panel to turn"off" the furnce. After the panel is removed, unscrew the sensor from the frame above the jets. Use a clean rag and gently wipe the sensor several times. Place back in the cut out and close the lower panel.
The furnace should cycle on and the flame stay on for the normal cycle.
Jan 18, 2009 | Goodman GMS90703BXA Heater
Amana alg643rb gas won't stay on
repl/ coils when bad does the same thing that it going on w/ your dryer
Feb 10, 2008 | Amana ALG643RB Gas Dryer
Carrier XHB123D X/Y Series Heat/Cool Air Conditioner Logo
132 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others