Ruud system and heat is not working
Installed a new thermastat and heat will not turn on. A/C is working fine. Orange wire is not connected to anything and Blue in connected to O/B
    Sergeant:
  • 288 Answers
This is a heat pump right? You have the blue connected to o/b, I assume you have a yellow wire connected to y or cool. The thermostat may need a jumper wire from RC to RH on the thermostat. This gives 24v to the heat system to work. If you have this already, then the orange wire is most commonly connected to the reversing valve. On the wiring directions that came with the thermostat what does it have common assigned to (if any)? And you need to know that the reversing valve is energized in cool or heat mode. the wiring diagram will tell you this.
Posted on Dec 18, 2007
How to hookup Auxiliary heat (and/or use an extra wire at the thermostat)
They don't always use the correct wire colors,if it is labeled w it is for your strip heat,shouldn't hurt to hook it up,most likely they used it for the strip heat,most heat pumps are wired to turn on your strip heat when the heatpump is in defrost mode and it is controlled by the heat pump,you can hook this to the emerg. heat or w2 :)
Mar 08, 2013 | Ruud Heating & Cooling
New heat pump system freezing, questioning wiring.
W1 and E on stat need tied together. When W1 comes on wire where all heat elements come on. On the outside unit defrost board set the 45-60-90 to 45 and see if that takes care of the frost problem.
Jan 03, 2010 | Heating & Cooling
I recently replaced my thermostat to digital and the air conditioner works great but the heat doesnt seem to get hot enough like it is blowing out room temperature air. when i replaced the thermostat there...
Sounds like you got the wrong thermostat.
The orange wire is for the reversing valve, which reverses the flow of refridgerant and changes the system from cooling mode, to heat mode.
If your thermostat has no terminal for the orange wire, (usually labled "O") then you have a thermostat that is not compatible with heat pumps.
Oct 15, 2009 | Ruud Central System Air Conditioner
Reversing valve installed backwards on goodman heat pump have a simple comfort 2000 thermastat the defrost cycle doesn't work . can the reversing valved be wired on the terminal board to accomadate this...
You should be able to move the reversing valve wire from O terminal, (the changeover relay), on the thermostat to B terminal. I deal mostly with York
which O on the t'stat is normally open and B is normally closed.
Oct 01, 2009 | Goodman PHKJ048-1 Air Conditioner
Ruud achiever heat pump
the reversing valve needs power to switch to heat. more then likly the o wire is connected when it shouldnt be
Jun 15, 2008 | Ruud UBHC Air Conditioner
If back-up heat comes on when a/c is turned on and then the back up heat turns off shortly after the a/c turns off, then the low voltage wiring is NOT correct. Your "R" terminal is basically your "hot" and your "C" terminal is basically your "neutral" to simplify explanation. The Furnace supplies the "R" power to the thermostat and then depending on what wire the thermostat sends the power back on determines what the system does. The thermostat terminals are as follows "G" is fan, "W" or "aux" is elect heat, "Y" tells the outdoor unit to run, "O" or "B" tells the outdoor unit whether it is heating or cooling, and "E" is emergency heat. "G" should connect from the t-stat directly to the furnace and go no further. "W" or "aux" AND "E" should both connect to your "W" or "W1" terminal in the furnace, there should also be a "W" connection to the heat pump ( this allows the H/P to turn on the elect heat when the unit defrosts) "Y" and "O" or "B" may or may not connect to a terminal in the furnace, usually they just pass through the furnace from the t-stat to the H/P and get wire nutted in the furnace. Now, here is the key. As I mentioned previously "O" or "B", a system will only use one or the other. The entire industry (except for Rheem and Ruud) uses the "O" terminial which has 24v on it when you are cooling and no power when you are heating. Rheem and Ruud use the "B" terminal which is just backwards, 24v in heating and no power in cooling. this could also be your problem if the t-stat thinks it is telling the H/P to cool but the H/P is actuall interpreting the signal to heat. Check your amp draw on the furnace, if you have anything drawing 15 amps+ then it is most likely the actual elect heat running, if not then check the "B" terminal. Most universal t-stats come set from the factory to use the "O" terminal which is more common. Usually this can be changed in the installer setup menu on the stat or sometimes the stat will have separate "O" and "B" terminals
Wiring connection for a Ruud air handler & seeking its wiring diagram.
we are trying to install a goodman heat pump with a rheem air handler, the orange wire is hook up and the unit is still staying in the heat mood. does anyone have a wiring diagram for the air handler, their is some white wires in the air handler one with a purple strip and one with a black strip we need help
Jan 05, 2008 | Heating & Cooling
Wiring Diagram for Ruud Heat Pump
Unfortunately, the wiring diagrams for heat pumps are not so easy to come up with. The outdoor unit will have its own diagram, but may not include the indoor air handler and will probably not include the thermostat. That said, the orange wire is commonly run from the thermostat to the reversing valve in the outdoor unit. This wire is usually not connected to the indoor airhandler. The orange wire is usually used in a unit that has the reversing valve energized in cool. Ruud, however has its reversing valve energized in heat. Probably not useful but maybe helpful
Mike
Jan 04, 2008 | Heating & Cooling
Heating & Cooling Logo
198 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Mack Baxter
Marvin
Marvin