Question about Electrical Supplies
I need help to wire or connect switch boxes and 3 way
    President:
  • 1,723 Answers
Go here to my 'knol' on google. I have a knol there and scroll down to '3-way switches.
http://knol.google.com/k/craig-butler/electrical-troubleshooting-for-dummies/vhee7eorx8pj/1#
Posted on Sep 24, 2009
I have a box that has four 110(black, white and copper) wires coming in. (1) is power, (2) is light (3) is outlet & (4) is light across the room. I need power to (2), (3) & (4) but need a switch to (2)...
Firstly (1) will be Black=hot, White=neutral and Copper=Ground. Don't work on these wires with them live.
All copper wires will be connected together and if possible, the metal box earth lug.
You will need a SPST or SPDT switch (image of SPDT switch is shown below) to mount in your junction box. If your switch has a ground lug, you need to also connect the copper wire there.
(1) Black will connect to Switch Common, (3) Black and (4) Black. Note: all can connect to the Switch Common connection as the switch will generally allow 3 wires to be connected per terminal; one push terminal and two screw pressed terminals.
(1) White will be connected to (2) White, (3) White and (4) White. For this connection, you can use a twist cap of the correct size to parallel these neutral wires.
(2) Black will connect to other free connection on the switch. There may be two free connections, so the one you use will basically determine which direction the switch will be on/off.
Once connected and checked, you can power up. If correctly wired, you should now have switched power to (2) and continuous power to (3) and (4).
I hope this helps with your inquiry.
Feb 27, 2015 | Electrical Supplies
How to you install a Leviton Slide Dimmer with Preset No. IPI06 to a double switch box where one switch controls the ligth fixture over the table(the one I want to connect the dimmer to) and the secon
Hi Velie,
I am an electrician and can help you wire this switch. If I understand correctly, you have a two-gang switch box in the wall. In it, you have two switches installed. One switch is a 3-way type, and is one of two (or more) switches used to control preparation area lighting. The other switch is a single pole type and controls a light over your kitchen table. Right?
If this is correct, remove the double switch wall plate. Let's set aside concerns with the 3-way switch. We have nothing to do to this switch so we will not need to remove it from the box, nor will we need to disconnect it. It works independently of the switch that controls the light over the table.
Remove the switch that operates the light over the table. If it is indeed a single pole switch, it will have just two terminals for wires to connect. It will probably also have indications for ON and OFF on the handle. If installed correctly, flipping the toggle up or pressing the top of the switch will turn the light on. If is a 3-way switch, it will have terminals for 3 wires to connect. One of the terminals will be a dark color from the other two. Additionally, no ON and OFF markings are on the switch handle and the light may turn on in either handle position (depending on the position of other switches controlling the light). With this information, I assume that you have now verified that it is in fact, a single pole switch. Right?
If all is going as expected, then we can continue. Shut off the power. Since a single pole switch has only two wires to connect, this should be fairly easy to do. One terminal should have a single wire that goes to the light over the table. The other terminal should have a wire that is powered all the time. It is very possible that the wire that connects to this terminal is ALSO is connected to the the 3-way switch either directly, or by a short length of wire that has a wirenut to connect several wires together. If you need to verify a connection to the 3-way switch, remove the switch from the box if needed (do NOT disconnect any wires). The wire should be connected to the dark colored terminal screw of the 3-way switch. This would indicate that this wire - and those connected by wire nut to it - is the source of constant power. Carefully fold the wires into the box and re-secure the 3-way switch if you pulled it from the box.
You new switch has a single RED wire and TWO black wires. Twist a wirenut cap on ONE of the black wires (it does not matter which). Remove the wire that was determined to be powered all the time (was also connected to the 3-way's dark colored terminal) from the old switch, and twist it around the dimmer switch's remaining BLACK wire with a wirenut. Disconnect the remaining wire from the old switch and twist it around the dimmer switch's RED wire with a wirenut. Add the dimmer switch's GREEN wire in to the bundle of uninsulated ground wires in the wirenut inside the box. Fold all the wires gently into the box and secure the dimmer to the box. Install the wall plate and turn on the power.
I hope this helped & good luck!
Feb 10, 2012 | Leviton MFG L00-IPI06-1LM DIMMER SLIDE...
The Casablanca 88U33M Scandia Ceiling Fan only has three wires, a black, a white, and a green wire (ground). How do you wire the fan and light on seperate switches?
If you want to control both the light and the fan using 3-ways, then just wire 2 sets of the 3-way circuits. For this you need two sets of 3-wire between the switches, and one 3-wire cable from the switch location to the fan/light box.
At box #1 (a 2 gang box), you will run a power cable (marked cable #1) into it. From there you run 2 sets of 3-wire cables (identified as cable #2 & cable #3) to the other switch location, which will also be a 2-gang box (box #2).
Also from box #1, you will run a 3-wire cable (cable #4) to the fan/light box (box #3).
Hook up is as follows:
Box #3: connect black of cable #4 to black (fan), connect red of cable #4 to blue (light), connect white of cable #4 to white (fan/light), and connect the bare to the green.
Box #2: Connect white of cable #2 to identified terminal on 1st 3-way switch (#3). Connect red & black of cable #2 to the remaining screws of 3-way switch #3. Next connect white of cable #3 to identified terminal of 2nd 3-way switch (#4), and connect black and red to remaining screws. Tie all grounds together and terminate to both switches.
At box #1, connect black from cable #1 to whites in cables #2 & #3, using a wirenut. Connect white in cable #1 to white in cable #4. Connect black and red in cable #2 to 3rd 3-way switch (#1) and connect black and red in cable #3 to 4th 3-way switch (#2). Connect black in cable #4 to identified terminal of 3-way switch #1, and connect red in cable #4 to identified terminal on 3-way switch #2. Tie all grounds together and to the switches
Jul 04, 2011 | Casablanca Fan (88U33M) Ceiling
I have a single pole switch that currently controls a bedroom outlet. i am installing a fan and light in the bedroom. i have a new triple switch that i want to control the existing outlet, the fan and the...
Wiring is not fully described: Location of hot wire and neutral wire from breaker box are unknown.
If Hot wire arrives in ceiling box first, the switch box will not have white neutral wires that are twisted together and covered with wire nut. Neutrals will be in ceiling box.
What is known: You are replacing single pole switch attached to one 14-2 wire going to light.
You are replacing light with a fan-light and replacing switch with a 3-pole TM8111 switch.
You have replaced 14-2 wire with 12-3 wire.
TM8111 wiring shows following link:
http://waterheatertimer.org/images/TM8111-switch-wiring-500.jpg
Fan pull-chain wiring shows following link:
http://waterheatertimer.org/images/Fan-motor-1-344.jpg
Assume neutrals in ceiling box.
Assume Hot wire in ceiling box: Connect 12-3 black wire to black Hot wire. Connect 12-3 white wire to black wire on light. Connect 12-3 red to red wire on fan.
White neutral from fan and white neutral form light connect to other white neutral wires and covered with wire nut.
Wiring at switch:
Black Hot wire from ceiling box connects to A COM terminal.
White wire to ceiling light connects to A SP2
Red wire to fan connects to A SP1
Jun 21, 2011 | Pass & Seymour Legrand TM8111 Three Single...
Wiring heater, vent, light with 12/2 and 12/3 from switch to unit. email: lfranklin5@charter.net
I wish we had more information to go on here.
1) You have 2 cables to to the Heat-Vent-Light
One cable is 12-3 and 1 cable is 12-3
2) That's where it's gets fuzzy.
What color wires are on HentVentLight?
Is power at the ceiling box or at the wall box?
What other wires are inside the wall box?
What kind of switch are you installing?
3) With that number of wires, it sounds like power is at ceiling box.
Power would arrive at ceiling box on one cable that has a Hot-black and Neutral-white wire.
4) Start at wall box:
Let's suppose you are installing a wall device that has 3 individual switches, with one switch for each HentVentLight.
The Hot wire from ceiling box would drop down into wall box on a black wire, and this wire connects to brass screw on switch.
Wire going to heater connects to one of the silver screws.
Wire to fan to another silver screw
Wire to light to another silver screw.
5) Work at ceiling box:
Let's suppose your HentVentLight has 4 wires: Black for light, Red for fan, Blue for heater, and White Neutral.
The white neutral connects to Neutral wire as described in #3.
Black, Red and Blue connect to each of the wires that come up from switch.
Add a comment for more free help, and fill in the missing information.
Also take advantage of fixya phone service.
For a price, expert speaks with you over phone while you work on timer or any do-it-yourself project.
Fixya is always less expensive than a service call.
Feb 01, 2011 | Broan-NuTone FAN CONTROL SWITCH
I have a Leviton 5634 two rocker switch that I'm using to replace an old double switch that controls two lights. There are 1 black, 1 red, and 1 white wire in the light switch box. The white wire is...
Review old switches:
Two old switches > each has 2 wires
Old switch 1 > Red and White
Old switch 2 > Black and White
The same white wire connects to both switches, so effectively they count as 1 wire
This means you have 3 wires ... 1 White, 1 Red, 1 Black
Each switch controls a separate load (light, fan, motor)
New Leviton double-rocker switch:
-Leviton has 2 Brass-colored screws on one side, and these screws are connected together by a brass plate >> your Hot wire will connect to brass screw
-Leviton has 2 Silver-colored screws on other side, and neither of these screws are connected in any way >> the wires going to each load will connect on a different screw on this side of switch.
Hot wire: Each box in your house has exactly 1 hot wire that is connected back to breaker box. This is true for all boxes (excluding boxes that have a 3-way & 4-way switches).
We need to identify Hot wire.
-By code the Hot wire is black for identification purposes ... but your box sounds like maybe the Hot wire is White.
-If your Hot wire is white, that is NOT an immediate safety issue ... it will not cause a fire or malfunction ... it is a code violation ... because code requires things be uniform so next electrician knows what previous guy did. So some day, electrician working outside grabs wrong color wire, and wow. I say this so you know.
Moving on.
Identify Hot wire:
-Pull 3 wires up so they can be tested
-Turn on power
-Use ordinary tester, or old lamp with plug cut off and wires stripped back
-Tape tester lead to sticks so hands are away from voltage
-Power is on. Don't stand in water or touch metal pipes, and you're fine.
-You have 3 wires in box + ground wire
-Test all 3 wires to bare ground wire >> when tester lights up, that is Hot wire ... testing is complete
Connect wires to Leviton double-rocker:
-Power is OFF.
-You have 3 wires - 1 White, 1 Black, 1 Red >> one is Hot wire, the other two wires go to load
-Hot wire connects to Brass-colored screws on new Leviton.
-Brass colored screws are connected together by a brass plate so the Hot does not need to connect to both brass screws.
-The other two wires connect to Silver screws on other side of new Leviton switch
-One wire goes to each silver screw
-Connect bare ground wire to green screw.
-Push wires back into box. Use eraser end of pencil if needed.
-Make sure ground wire is back and away from screws on switch
-That's it.
Sep 30, 2010 | Leviton Electrical Supplies
I have an ST01 timer that I want to place in a three way circuit that appears to be different than that shown in the directions. My circuit has power (black/white/ground) coming into switch 1 with a three...
One caveat of most In-Wall electronic switches/timers is that the device _must_ be installed at the switch box that has the power, in your case switch #1. In order to install it at switch #2, in your case, you need an extra wire between the switches (to carry the HOT wire), and unfortunately, the bare ground(ing) wire is not permitted to be used to carry current per National Electric Code (NEC).
In your case the wiring for the ST01 is as follows:
Switch box #1: Connect the incoming White wire to the White wire in the 3-wire cable that goes to switch box #2. Connect the incoming (Black) HOT wire to the Black wire on the switch/timer. Connect the Red wire in the 3-wire cable to the Red wire on the switch/timer. Connect the Black wire in the 3-wire cable to the blue wire on the switch/timer. Connect the green wire on the switch/timer to the 2 bare ground(ing) wires. If you have a metal box this connection should also have a pigtail that connects to the box with a green ground screw.
Switch box #2: Remove all of the existing wires from the 3-way switch. The three-way switch will have 2 screws the same color (usually black) and 1 screw (usually brass). For this scenario, one of the black screws will _not_ be used.
Connect the Black wire in the 3-wire cable coming from switch #1, the Black wire going to the lights, and a short Black pigtail together under one wirenut. The pigtail is then connected to the brass screw on the 3-way switch. The Red wire in the 3-wire cable coming from switch #1 is connected to one of the 2 black screws on the 3-way switch (pick one).
In effect you are installing a single switch at switch box #2. In fact, you can use a regular single pole switch if you want too.
To finish, connect the White wire in the 3-wire cable coming from switch #1 to the White wire going to the lights.
Grounding is the same as switch #1 except you'll need a pigtail to connect to the green screw on the 3-way switch.
That's it. You may want to check the battery compartment in the switch/timer, as sometimes they put in a pullout plastic tab to keep it from being energized until needed.
Now, the E1210 is a different animal, and can only be used to replace a single pole switch. You could use it by basically passing the power through to switch box #2 from switch box #1 and then cover switch box #1 with a blank plate. The ST01 could be used that way too, in which case the black on the device connects to the hot, the blue to the lights, and the red on the device is not used, nor will the Red wire in the 3-wire cable between the switch boxes be used.
Sep 11, 2010 | Intermatic EI210 Electronic Auto Shutoff...
I want to install a light in my garage i have a live source but how do i connect it to the light and wall switch
My first response would be to seek help from an electrician or someone qualified to perform this work.
If you are going to attempt it, you will need the following items:
- electrical box
- light switch
- light fixture
- wire ( ask you local hardware store clerk what is recommended or needed to meet code in your area.
Disconnect power at breaker to your source.
From your source,
- connect wires to electrical box. then to;
- connect wires to switch then to;
- connect wires to another box at the fixture
- connect fixture to the box.
box=====switch=====box=fixture.
Apr 27, 2010 | Westinghouse Electric Ceiling Fan 3-way...
I need to wire a 3 gang switches in a 3 gang box
before u start make sure power is off before working with electrical lines ---start with the 12/2 coming into box black [power] white [ground-neutral] and u will have 3 separate lines for the lights so u will have 4 lines total coming in the box== with the 3 light lines take the white and strip back the plastic and connect [wire nut] all 3 to the 12/2 white line --now take the 12/2 black line and connect it to the first switch gold color screw- bottom screw -now take some wire about 2-3 inch strip both ends and connect from the 12/2 black wire connection on the switch and connect to the gold /bottom of switch 2 than do the same for switch 3 connecting the wire from switch 2 so u will have power feeding all 3 switches-- now connect the black lines for the lights to the other side of each switch and ur done
Feb 14, 2010 | Cooper Industries Cooper Wiring 2158V 3...
How to wire 3 switches in a 3 gang box
WARNING: Do not attempt to do this work unless you completely understand the information provided below. If in doubt call an electrician.
Always make sure the power is disconnected from all possible sources before making any connections. Your description of the problem indicates that there may be multiple power wires coming into the same box. In that case local codes may require that the box be partitioned to prevent exposure to voltages up to 220 volts.
You need to determine where each wire goes to know how to connect them together. You cannot rely on color alone. If the power supply runs through the box to the loads then most (but probably not all) of the white wires will be connected together. If the power runs to the load boxes first then none of the white wires in the switch box should be connected together. They are used to run the switched/dimmed power back to the loads (and should be taped to cover the white in the box). In that case each switch has its own power input and they should not be tied together. A wire (could be black or white with black tape) brings power from the load box, gets connected to the input terminal of the switch and the corresponding black wire carries the switched power back to the load. The fan/light switch will have one power in and a switched power out for the fan and another for the light. The 3-way will have one "power" in (or it could be the final power out to the light) and two "carrier wires that connect to the other 3-way switch. If the power supply goes through the switch box then there will be at least 10 wires in that box. In that case see the attached diagram: a5fa64a.gif
Sep 23, 2009 | Cooper Industries Cooper Wiring 2158V 3...