I am finishing the wiring in my basement a I have 1 receptacle with 2 14/3 wires in it and another with 1 14/3 wire into it. I need to figure out the 2nd circuit and how to finish off the plugs
    President:
  • 704 Answers
With most receptacles, you can connect up to two (2) sets of wires to the one recptacle/outlet. Be sure the power is off to the circuits you're going to be working on, by turning off the breakers in the main panel that go to these circuits.
Strip back the outer jacket at 8 inches on the Romex wires and be careful not to nick the conductors inside the outer jacket.
With the black, white and bare ground wires now exposed and separated from the jacket, you can stirp off 1/2 inch of the insulation off both the black and white wires. You can also tear off the paper wrapper that covers the bare copper ground wires too.
Now take the ground wires and twist them together for at least 3 inches, making sure that you start the twist near the back of the outlet box, where the wires come into the box. Use a pair of lineman's pliers to twist the bare wires together. Once you've done that, you can clip off one (1) of the bare ground wires that is left sticking out, as you only need one to connect to the Green grounding screw on the receptacle/outlet.
Now connect the two (2) black wires to the brass colored screws, which is the HOT or common side of the outlet. On the other side, connec the two (2) white wires to the silver colored screws, as this is the Neutral side of the outlet. Now you can carefully bend the wires to let you push them into the outlet box and screw the outlet into the wall box. Put on the plate cover and you're all set. Turn the breaker back on and you've completed the wiring.
On the box with the single #14/3 wire (w/ground) just follow the instructions above, except you only have one wire to connect to each side of the outlet, matching them Black to brass screw and White to silver screw and the bare copper wire to the Green grounding screw.
Hope you find this Very Helpful and best regards.
Posted on Sep 20, 2009
I have a screwball electrical wiring issue. I have 2 wires coming into a box with 3 conductors each, the box has 1 receptacle and one switch in it. The wiring is as such wire 1 comes from the pane and goes...
This is what I think is going on.
Pull the bathroom light and verify that there is only one wire going to it. I'm betting that it only has one 3cond and that it's the second one in your j-box.
Connect the 3cond from the circuit breaker to the GFI.
Pull a single black wire from the GFI over to the switch. The black in the 3cond to the light goes on the other side of the switch. White from the light goes to white on the GFI.
What the electrician did is power the light from the receptacle box.
I'd like to know if this corrects the problem and everything works.
Dec 08, 2017 | Electrical Supplies
I am trying to wire a new Emerson 230v pool pump to a timer. The pump has 2 red wires and 1 green wire coming from it. The timer has 3 wire terminals. The receptacle has 1 black wire, 1 white wire and 1...
You really need a 2-pole timer -- 2 wires in and 2 out. In that case the Black/White from the receptacle goes to the 2 "in" terminals and the 2 red wires from the pump go to the 2 "out" terminals. The WHITE wire from the receptacle goes nowhere - tape it off. The Bare wire from the receptacle goes to the GREEN (ground) wire on the pump.
A single-pole timer can be used, but in that case, you ALWAYS have 110 v on one side of the pump. Not safe, and not code compliant.
May 27, 2017 | Emerson THREADED SHAFT UP RATED - 1.00 HP...
Can't get my switch to operate the outlet just bought a 5625 switch i have two wires coming out of the wall i want to plug a light in the outlet and have the switch control the power to the outlet.
  • Turn off the power to the receptacle that will be replaced by switching off the circuit breaker in the fuse box. Check that the battery is good in a circuit tester. If not, replace the battery. Place the tester's two ends in one set of the receptacle's slots, then the other set. The light on the tester should not come on. If it does, the correct circuit breaker has not been switched off.
  • 2
    Take off the receptacle's face plate by first removing its screw. Detach the two screw securing the receptacle to the box and pull out the receptacle. Loosen the receptacle's terminal screws and pull away all wires from the back of the receptacle. Take out the receptacle (if working properly, it can be reused). If the ends of the wires are chewed up after removing them from the existing receptacle, cut them off with wire cutters. Strip off 1/2 an inch of insulation from the ends, using wire strippers. Bend them into loops with the pliers.
  • 3
    Bend the copper ends of all wires into a loop, using a pliers. Connect the white wires to the silver terminal and tighten the screw to the wires. Connect the black wires to the gold terminal and tighten the screw to the wires. Connect the bare ground wires to the ground terminal and tighten the screw to the wires.
  • 4
    Push all cables into the back of the box, followed by the receptacle. Attach the receptacle to the box with the two screws. Hold the new faceplate in position and install the screw. Turn on the power at the circuit breaker.
  • HOPE THIS HELPS YOU...Jim...Please leave a comment
    Feb 13, 2011 | Leviton Electrical Supplies
    I would like a wiring diagram for an outdoor receptacle controlled by a photocell. Photo cell has 1 each black wire, red wire and white wire.
    If I understand correctly, you want to add a photocell to existing receptacle.
    Start by looking at receptacle:
    Receptacle has 3 different colored screws.
    Green screw for bare ground wire
    Brass screws with black Hot wire connected.
    Silver screws with white Neutral wire.
    How to wire photocell to receptacle.
    Remove black Hot wire off of brass screw and connect black wire to photocell-black wire. This will power the photocell switch.
    Connect photocell-red wire to brass screw on receptacle. This will turn receptacle on-off whenever photocell switch turns on-off.
    Connect photocell-white wire to silver screw, and this will complete circuit to photocell switch so the switch is able to operate.
    All white Neutral wires are connected to silver screws.
    Add a comment for more free help.
    Also take advantage of fixya phone service.
    For a price, expert speaks with you over phone while you work on circuit or any do-it-yourself project.
    Fixya is always less expensive than a service call.
    Feb 07, 2011 | Intermatic K4221C Photo Cell Control 120 V...
    Which color gets hooked up to what on a ceiling fan
    For residential wiring, some basic rules given in the NEC are:
    • Phase wire in a circuit may be black, red, orange (high leg delta) insulated wire, sometimes other colors, but never green, gray, or white (whether these are solid colors or stripes). Specific exceptions apply, such as a cable running to a switch and back (known as a traveler) where the white wire will be the hot wire feeding that switch. Another is for a cable used to feed an outlet for 250VAC 15 or 20 amp appliances that do not need a neutral, there the white is hot (but should be identified as being hot, usually with black tape inside junction boxes).
    • The neutral wire is identified by gray or white insulated wire, perhaps with stripes.
    • Grounding wire of circuit may be bare or identified insulated wire of green or having green stripes. Note that all metallic systems in a building are to be bonded to the building grounding system, such as water, natural gas, HVAC piping, and others.
    • Larger wires are furnished only in black; these may be properly identified with suitable paint or tape.
    • All wiring in a circuit except for the leads that are part of a device or fixture must be the same gauge. Note that different size wires may be used in the same raceway so long as they are all insulated for the maximum voltage of any of these circuits.
    • The Code gives rules for calculating circuit loading.
    • Ground-fault circuit interrupter (GFCI) protection is required on receptacles in wet locations. This includes all small appliance circuits in a kitchen, receptacles in a crawl space, basements, bathrooms and a receptacle for the laundry room, as well as outdoor circuits within easy reach of the ground. However, they are not required for refrigerators because unattended disconnection could cause spoilage of food, nor for garbage disposals. Instead, for refrigerators and other semi-permanent appliances in basements and wet areas, use a one-outlet non-GFCI dedicated receptacle. Two-wire outlets having no grounding conductor may be protected by an upstream gfci and must be labelled "no grounding". Most GFCI receptacles allow the connection and have GFCI protection for down-stream connected receptacles. Receptacles protected in this manner should be labeled "GFCI protected".
    • Most circuits have the metallic components interconnected with a grounding wire connected to the third, round prong of a plug, and to metal boxes and appliance chassis.
    • Furnaces, water heaters, heat pumps, central air conditioning units and stoves must be on dedicated circuits
    • The code provides rules for sizing electrical boxes for the number of wires and wiring devices in the box.
    The foregoing is just a brief overview and must not be used as a substitute for the actual National Electrical Code.
    Jan 29, 2011 | Hampton Bay 54 In. Flemish Pewter Ceiling...
    My home was built in 1906 and there is only 1 white wire and 1 black wire in the existing outlet box. I am installilng a Combo Switch and Receptacle device and I'm able to get the switch to control the...
    Receptacle needs 1 Hot wire and 1 Neutral wire to complete circuit.
    It sounds like you have 1 Hot wire and 1 Load wire but no Neutral wire.
    Neutrals are not always present in switch box.
    As a general rule, if a switch box has Neutral wires, they are twisted together and covered with wire nut, and then pushed to back of box.
    Every receptacle box has Hot and Neutral wire. Hot connects to brass screw, and Neutral connects to silver screw. The two wires together complete circuit when you plug in a lamp.
    So each receptacle box has Neutral wires, and you can get a Neutral wire from receptacle box and bring it over to the switch box. This work takes every tool and probably touch-up paint.
    Here is a link showing how to drop a wire down to your switch box:
    You have to tear out old switch box, and then install 'old work box.'
    Old switch box is nailed into 2x4s. Pry box out a bit, then reach in with hacksaw blade and cut nails.
    http://waterheatertimer.org/Install-owb.html
    Here are two more links that show basic 240V and 120V circuits:
    http://waterheatertimer.org/B220C.html
    http://waterheatertimer.org/See-inside-main-breaker-box.html
    Also take advantage of fixyas phone service.
    For a price, fixya expert speaks with you over phone while you work on electric.
    Jan 02, 2011 | Cooper Wiring Devices Combination Switch &...
    I need to know what screws are for what 2 black, 1 gold 1 silver
    You are install a switch-receptacle combo.
    As you have realized, screw color is the key.
    1) Black hot wire connects to dark colored screws.
    Both dark screws are connected together with brass plate, so hot wire only needs to connect to one of the dark screws.
    2) Wire going to Load (light,fan, motor) connects to brass colored screw.
    3) White neutral wire connects to silver colored screw.
    4) Lets look at problem as if new wiring device is replacing old on-off switch that has two wires.
    So old on-off switch has two wires >> one is black hot wire, and other is wire going to load.
    Separate wires, turn on power and test each wire to bare ground wire.
    Tester lights up on hot wire. This wire goes on dark screw.
    If old on-off switch had another wire connected with the hot wire, that wire also goes on the dark screw.
    The other wire from old switch is the Load wire, and it connects to brass colored screw.
    Now you need a neutral wire.
    In back of box are white wires twisted together and covered with wire nut.
    These are neutrals.
    To confirm that these wires are neutrals >> turn on power and test hot wire to other wires in box. Tester lights up on neutral.
    Neutral wire connects to silver screw, and this will complete the circuit for any electric device plugged into receptacle.
    If box does not have neutral wires as described above, you can violate code and connect bare ground to silver screw >>> but do NOT do this if your new plug is going to be used regularly.
    You can use bare ground temporarily until additional wiring is made available.
    Dec 14, 2010 | Leviton 10 Brown Switch Outlet...
    I can't figure out how to wire my cooper wiring combo switch/receptacle. I have a white, black and copper wire coming in. One terminal on the receptacle side is clearly marked white/blanco, the two...
    Take the black going to the light off the center and hook where the white going to the light is now....then hook the white to the light with the other white and you will be good to go...You almost had it right...
    just a couple of adjustments....:-)
    heatman101
    Oct 11, 2010 | Cooper Industries Cooper Wiring 274W...
    Need four prong wiring diaagram for the power cord to a fridgedaire dryer Model FDEB55R
    Due to a change in the National Electrical code in 2005 all dryer recepticals are required to have a 4 wire receptacle. This is to insure an isolated ground. You will need the following tools,
    • 1 – phillips screwdriver
    • 1 – standard screwdriver
    • 1 – 3/8′ nutdriver
    • 1 – 5/16′ nutdriver
    • 1 – 1/4′ nutdriver
    First disconnect any power cords from thier outlets. Then on the back of the dryer,/uploads/images/ae228a3.jpg You will need to remove this access panel. Once removed you will see a connection block that looks like,
    You will now need to loosen the connections using the nut drivers, once the connections are removed the loosen the screws on the strain relief. ( the clamp holding the wires)
    Once this is loose you can remove the old cord and install a new 4 wire cord. When making the new connections you will need to neutral or white wire in the center of the block, and the green wire is connected to where the bonding strap use to be or connect it to the frame of the dryer using the access panel screw holes.
    The black and red wires are your hot or L1 and L2 connections. It should look like this when finished.
    /uploads/images/527d09d.jpg
    Then reattach you access panel door and plug your dryer in and you ready for laundry.
    Thanks, Dorrian
    Aug 07, 2010 | Frigidaire Dryers
    How to ground receptacles in home basement
    you need a 2 wire with ground. Some older homes were wire with just a 2 wire. you can take a wire from the nuetral and connect it to the ground screw to trick testers into thinking it is grounded properly, but i would not.
    Dec 06, 2009 | Irons
    Heating & Cooling Logo
    132 people viewed this question
    Top Heating & Cooling Experts
    Paul Carew
    Dan Webster
    Dan Webster
    Tim Whalen