Traulsen URS36DT: Freezer Coil freeze's Question is what needs replaced ? Defrost Timer or Defrost Thermostat ? How does one check ? I have Multimeter & would check it out if I had a clue where to start ? Thanks Rob Aespey@cox.net
  • 410 Answers
Checking a def system is kind of easy. if you have located the defrost timer just turn the little knob on the timer until the unit shuts off, shortly you should hear "hissing and pooping" from water dropping on the heater. this lets you know that the defrost thermostat is good. if you dont hear this noise check your def thermostat and heater for continuity. if you put it into def and the heater comes on then you have a bad timer..
Posted on Dec 12, 2007
Traulsen freezer with intella true continuously frosting the evaporator coil and blocking the air flow?
Your defrost circuit ... should (about twice each day) gently warm up.. and remove the frost to an evaporation tray at the bottom of your FREEZER (refrigerator?)...
Regardless of the design...
THERE are only two reasons for excessive FROST.
- massive air intrusion (check seals & gaskets)
- defective defrost circuit (check defrost timer/controller)...
EZ trouble to fix...
Post comment reply: 7/3/2016...
In general... there are only three elements to the defrost circuit:
- 1st failure is usually the "timer" (in your case (other cases it is being replaced by the power control board (do remove power: line voltages present).
- 2nd failure (inside ... usually atop the evaporator) is the "DEFROST THERMOSTAT" (designed the keep the heating element from getting much hotter than 55 degrees Fahrenheit, ("failing" = open.. prevents the heater element from being energized at all).
- 3rd the heating element... itself goes open (usually below the evaporator (caution: line voltages on 2nd & 3rd)).
Anytime you don't feel you've got this surrounded just comment me back... I'll be around.
Go to Bing homepage
http://www.bing.com/search?q=traulsen+freezer+wiring+diagrams&qs=AS&pq=traulsen+freezer&sk=LS1AS5&sc=8-16&sp=7&cvid=47349AEC29CA4E1D8902F3954D86C0BF&FORM=QBRE&ghc=1
Jul 02, 2016 | Traulsen Freezers
Freezer side not freezing
Check for ice / frosting inside the freezer .... If present you probably have a defrost problem.... This causes the freezer coil to ice up and block the air flow ... the causes could be a bad defrost heater , defrost timer, defrost sensors, or control board. Also make sure that the condenser coil is clean. remove ALL dust with a vacuum and a coil brush .the coil is located either on the bottom or on the back side of the unit... You didn't give the Make and model #
Apr 04, 2014 | Freezers
Evaporator ice up and unit has a temp at 31F not going down in singles digits
Melt the iced up evaporator with a hairdryer for a temp. fix. The auto defrost system isn't working. I can't find diagrams of yours but here is basically how it works.
The evaporator coil behind the cover on the back wall inside the freezer will ice up under normal conditions. Every 8 to 10 hours for around 20 minutes the defrost timer (or in most newer models the electronic adaptive defrost control) will turn the defrost heater on to melt the built up ice. There is a defrost thermostat which prevents the heater from overheating the freezer by breaking the heater circuit when the temp reaches close to 32 degrees F. The entire cooling system shuts off during the defrost cycle and starts back when the timer advances through the cycle.
If this ice is not melted it will continue to build up until the air can't flow over the coil to circulate the cold air through the freezer and into the fridge. The temperature change in the fridge is usually noticed first followed by the freezer.
If the defrost thermostat is bad, it can prevent the heater from coming on OR it won't turn the heater off when it gets too warm. It is clamped to the evaporator coil at the top to sense the temp. If it appears to be misshapen it is bad.
With an ohm meter it should show continuity when cold and none when warm.
You can also bypass(disconnect the two wires plugged into it and twist them together) the thermostat to see if the heater comes on then. If it does then you know the thermostat is bad and needs replaced.
The defrost heater is located on the evaporator. It is in a tube which is at the bottom and can also go up the sides of the evaporator. On some types you can see a burnt spot if it's bad. With an ohm meter it should show continuity from end to end when disconnected from the wiring in the freezer. You can also test the wiring for voltage when it's in the defrost mode.
If you have a defrost timer you can test it. It can be located under the fridge behind the kick panel on the front. Some are in the fridge with the controls at the top. You can turn the defrost timer till it clicks and everything shuts down. The heater should now come on. If it does, replace the timer because that means the timer is not running. If it doesn't, check the heater and defrost thermostat. Turn the timer again till everything starts back up to end the defrost cycle.
If you have an adaptive defrost control instead of a timer, replace it if the heater and thermostat test good. It is located in the fridge with the controls in some models and on the back in others.
Jan 09, 2011 | Traulsen RLT232NUTHHS Commercial Freezer
Ice up on the coil
DEFROST PROBLEM The evaporator coil behind the cover on the back wall inside the freezer will ice up under normal conditions. Every 8 to 10 hours for around 20 minutes the defrost timer (or in most newer models the electronic adaptive defrost control) will turn the defrost heater on to melt the built up ice. There is a defrost thermostat which prevents the heater from overheating the freezer by breaking the heater circuit when the temp reaches close to 32 degrees F. The entire cooling system shuts off during the defrost cycle and starts back when the timer advances through the cycle.
If this ice is not melted it will continue to build up until the air can’t flow over the coil to circulate the cold air through the freezer and into the fridge. The temperature change in the fridge is usually noticed first followed by the freezer.
If the defrost thermostat is bad, it can prevent the heater from coming on OR it won’t turn the heater off when it gets too warm. It is clamped to the evaporator coil at the top to sense the temp. If it appears to be misshapen it is bad. With an ohm meter it should show continuity when cold and none when warm. You can also bypass(disconnect the two wires plugged into it and twist them together) the thermostat to see if the heater comes on then. If it does then you know the thermostat is bad and needs replaced.
The defrost heater is located on the evaporator. It is in a tube which is at the bottom and can also go up the sides of the evaporator. On some types you can see a burnt spot if it’s bad. With an ohm meter it should show continuity from end to end when disconnected from the wiring in the freezer. You can also test the wiring for voltage when it’s in the defrost mode.
Jul 20, 2010 | Hoshizaki 48.5 cu. ft. / 1373 liter...
Fridge freezer problem
Sounds like the defrost system of your freezer is not working. It could be either the defrost timer, defrost thermostat or the heater has a problem. The defrost timer turns off the compressor periodically to sent power to the defrost heater via the thermostat. The defrost heater then powers up and heats the evaporator coil to melt the accumulated ice buildup on the cold coils. Most likely issues are that the timer motor is not advancing the timer or the heater itself has burned out.
Jul 14, 2010 | Freezers
Not freezing
Either the defrost circuit has failed or the refrigerant is low - my money is on the defrost circuit.
Most defrost circuits have three main parts:
1) defrost electric heating coil
2) defrost terminator
3) defrost timer.
The heating coil and terminator are in the freezer compartment - behind a protective panel. The heater is usually piggy-backed on the freezer coil and the terminator is in contact with the freezer coil to detect its temperature. The defrost timer is a simple assembly of a clock motor with switch contacts that can be located anywhere the manufacturer desires. The timer turns on or enables the defrost circuit every 8 or so hours for up to 30 minutes give or take.
When the timer has enabled the defrost cycle, the cooling mode ceases; the compressor shuts off and power is sent through the terminator to the heater. The heater warms and melts any ice build up on the freezer coil. The water drips to a pan and flows down the tube to a pan under the fridge - where it is evaporated off. The heater warms the freezer coil until either a) the timer returns to cooling mode or b) the terminator senses a preset rising temperature on the freezer coil. Once either condition is present, power is interupted and heating stops. The compressor is energized through the adjustable thermostat in your fridge. Since it is warm, the compressor turns on and cooling begins.
If any of the components listed above (1,2 or 3) have failed, the defrost cycle never warms the freezer coil and the ice never melts to clear the freezer coil as intended. Air can not be circulated through the freezer coil since it is choked with ice, so even though the compressor runs, the fridge and freezer spaces never get colder. The adjustable thermostat never sees the temperature you've set so the compressor never shuts off.
Water dripping in the fridge is melting ice from the freezer space - as the freezer is not getting colder - only the protected space around the freezer coil is.
To fix this, you'll have to get the service manual or schematics for the fridge to determine where the parts are located and do some troubleshooting with a multimeter after disassembling the freezer compartment and wherever else to access the timer if needed. This is not a good first appliance repair job for a DIYer due to the danger of refrigerant and testing live electrical parts in closed in spaces.
I hope this helps.
May 20, 2010 | Kenmore 20.3 cu. ft. / 575 liter Upright...
My service man replaced the defrost cycle timer and the relay (timer was definitely broken, relay was highly suspect) but the freezer fan still has no power so freezer will not chill adequately despite...
Most all commercial freezers have a fan delay/ defrost terminator. It is usually mounted on the end of the evap coil. It's purpose is to sense the temp of the coil during the defrost cycle. When it hits a preset temp., usually around 55 degrees or more (depends on Mfg.) It terminates the defrost cycle. It also doubles as a fan delay. It allows the evap coil to cool off from the defrost cycle before allowing the fan to come on. Usually, the coil has to get around 20 degrees before fan will energize. I would look for this as a possible problem. It could be one device with 3 wires or 2 separate devices with 2 wires each. I've seen it both ways.
Hope this helps.
Nov 19, 2009 | Traulsen 46 cu. ft. Commercial Freezer...
Freezer won't freeze
If the evaporator coils behind the back panel of the freezer are icing up because of auto defrost failure that will stop the circulation of cold air and eventually affect the freezer too.
If the defrost thermostat is bad it can prevent the heater from coming on OR it won’t turn the heater off when it gets too warm. It is clamped to the evaporator coil at the top to sense the temp. If it appears to be misshapen it is bad.
You can also bypass the thermostat to see if the heater comes on then. If it does then you know the thermostat is bad and needs replaced.
Nov 08, 2009 | Frigidaire Freezers
Freezer is cold, but not freezing stuff...
Oct 11, 2009 | Freezers
It just stop freezing, how to I check if it is the compressor problem?
. Cut everything off for a few minutes then turn it back on and listen for a click from the compressor relay as the compressor tries to start.
Is the compressor motor running.If no check starter/overload relay.
Check to see if the condenser fan at the back underneath near the compressor is running. If no check fan.
Are the condenser coils near there warm or room temp. should be warm
If you need help finding your model number see here> http://www.appliancepartspros.com/modelnumber_locator.aspx
To locate your timer, motherboard, control or adaptive defrost control , enter your model number and search for the part or post back on Fixya.
http://www.searspartsdirect.com/partsdirect/index.action?psid=26129238&sid=PSx20071217x00001a
Oct 04, 2009 | Frigidaire 14.1 cu. ft. Upright Freezer...
Traulsen 7 cu. ft. / 198 liter Commercial Freezer ULT27 Logo
512 people viewed this question
Top Traulsen Freezers Experts
Dennis Boxerman
Craig Butler
Craig Butler
Charles T Nevin
Charles T Nevin
Are you a Traulsen Freezer Expert? Answer questions, earn points and help others