Air handler does not respond to thermostat - Heating & Cooling
  • 1 more comment
  • klcarsey Sep 13, 2009
    freon....it is a residential airconditioning unit
    it is either the thermostat or the ignition control unit. the outside unit seems to operate properly
  • Ian White
    Ian White May 11, 2010
    Supply more detail... Is it a self contained unit (DX) or a full Air Handling Unit, is the thermostat supplied with the unit? Is it just a simple thermostat i.e simply a thermostatically operated switch? What is the electrical rating of the stat?
  • please the AHU IS COOLED BY CHILLED WATER OR FREON
  • 55 Answers
If you have high voltage power to the air handler you need to make sure there is a low voltage call to the air handler from the thermostat. sounds like the low voltage wiring is miswired.
Posted on Sep 13, 2009
Need wire diagram from T-stat to Air-Handler then cond unit
green goes to g on air-handler,white goes to w on air-handler yellow goes to outside condensor, red from air-handler goes to rh-rc on thermostat, whire off c on air-handler goes to outside condensor.
May 13, 2014 | Ruud Heating & Cooling
WIRING THE THERMOSTAT TO AC UNIT THEN FROM THE UNIT TO HANDLER
Generally, you would go from the thermostat to the air handler, and then, from the air handler to the outdoor unit. I don't know if you have a heat pump or not, so I will give you a simple diagram and you can contact me if you need more.
Thermostat : Y G R W and sometimes C
Air handler: Y G R W and C
Outdoor unit: two wires connecting to the contactor ( not heat pump)
Thermostat; Y--------------Y(air handler cooling)------------------one side of contactor, outdoor unit
G-------------G (air handler, fan)
R--------------R (air handler ,hot)
W-------------W (air handler, heat)
C--------------C (air handler, common)------------other side of contactor, outdoor unit
This is a typical wiring diagram. Just contact me if you have something different. Hope this helps. Stay cool. mark
Jul 10, 2011 | Heating & Cooling
How to wire condenser and air handler to the t-stat
Assuming this is a standard unit the thermostat connections you will use: Y, R, G, W and possibly C.
Run two conductor thermostat wire to the condenser. The condenser will have two wires to connect. Connect the two conductors to the condenser wires and run them in to the air handler.
At the air handler, connect the two condenser wires to: Y (yellow) and C
Run 4 or 5 conductor thermostat wire from the air handler to the thermostat. At the thermostat, connect the yellow wire to Y, the white wire to W, the green wire to g, and the red wire to r.
At the air handler, connect the thermostat wires: White to w1, yellow to Y, green to G, and red to R
*Y will now be connected to the thermostat and the condenser
*If you have 5 conductor wire to the thermostat, connect the last wire (which is probably blue) to C
At the air handler, connect the last wire (blue) to C. This will enable you to have 24 volts at the thermostat in case the thermostat actually requires 24 volts to operate it.
R=hot
G=fan
Y=cool
W=heat
May 19, 2011 | Heating & Cooling
I have a T3BA-036KA the outside unit will not
You need 24 volts going to the coil of the contactor. If you do not have 24 volts, you will need to trace the wiring back to see where you are losing it from. Try placing your voltmeter at C & Y coming from your air handler. If not, go to your air handler and test for 24 volts ac at C & Y coming from your thermostat. If you do not have 24 volts coming from your thermostat, there is either a problem with the thermostat or there is a problem with the wiring between the thermostat and the air handler. If you have 24 volts at the air handler coming from the thermostat but you do not have 24 volts at the outdoor unit coming from the air handler, then you have a problem with the wires between the air handler and the outdoor unit.
I hope you find this information to be very helpful to you moving forward. Please leave a rating. :-)
May 10, 2010 | Intertherm P3RA-036K Air Conditioner
I have air handler nordyne the blower dont stop
check thermostat make sure fan is not set on on, if thermostat is right the fan relay may be stuck closed or thermostat wire can be touching
Oct 27, 2009 | Heating & Cooling
Fuse blowing on tappan air handler
most of the time its out by the ac unit . you have a shorting thermostat wire .. the outside unit has a large wire thats 240v and a small one that 24v thats the one you want to look at . look for bare wires , look where it goes into the wall , thats the common place . "critters" love to chew thermostat wire . so take a look . .....please rate this answer , i need votes . thanks
Jan 24, 2009 | Heating & Cooling
My Blower Turns itself on when it is not supposed to.
If your indoor unit is located in the attic, you may be experiencing the result of a high temperature safety device (possibly too sensitive) that is responding to warm air drifting up the return air duct. The function of this device is to turn on the fan at a given set point and cool the unit back down. Have someone identify your limit rating and change the limit device with one rated the same or see if the maker of the unit has an upgrade/service bulletin on this fault.
May 03, 2008 | Ruud Handler Air Conditioner
Wiring Diagram
here is a basic wiring diagram for all air cond systems your thermostat consist of treminal r w y and c run a four conductor wire fromm thermostat to ai handler the air handler should allso have eather have red blue white wires or a teminal block marked r w c r stands for red w for white c for comon allso blue run color for color from the thermostat to ai handler with exeption of yellow yellow runs straigth to condenserand retuns in white wire to air handler wich gets conected to comon hope this help[s you
Sep 02, 2007 | Ruud UBHC Air Conditioner
Heating & Cooling Logo
93 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen