I have a rheem condenser that the contactor does not pull in.I have changed the relay control board
  • ajh195252 Sep 13, 2009
    tried that now the compressor went out and got hot i think the unit was on time delay
    thanks but did that first
    President:
  • 1,922 Answers
Have you checked for 24volts A.C. from thermostat two small wires on the magnetic coil on contactor,w/o this voltage the contactor will not pull in to energize compressor with 240 volts A.C.it needs
Posted on Sep 12, 2009
Rheem RAKA-060JAZ trouble question
pls check for compressor shorting and relay issue in pcb
Oct 12, 2013 | Heating & Cooling
My a/c ruud/rheem wont come on by it self noisy relay
did you replace the contactor. if so, you need to verify the control coil voltage. should be a 24v coil. you need to also check to verify you are getting 24v at the contactor coil.
Apr 14, 2013 | Ruud UBHC Air Conditioner
The outside fan in my carrier unit will not stop running when temp inside has been reached?
There can be multiple problems with your situation, one being a stuck condenser fan motor contactor/relay, a shorted motor, bad control board, etc. If you could at least check the contactor that controls the CFM and see if it is pulled in that could help narrow down the search for the answer.
Sep 23, 2011 | Carrier 50TJ028 Rooftop Electric Cool Air...
Rheem RPGB-37JAS. I purchased Defrost Control Kit 47-102684-83 to replace old defective one. Old board had wires on terminals labeled 18-30 VAC, COM, DEF RELAY, and HOLD. New board has terminals labeled...
C- is common/ground of the board FM transformer
R-is 24 volts to the board FM transformer
B- is to energize reversing valve for heat from thermostat.
D- energizes the electric heat in defrost mode.
Y-comes from the thermostat and energizes the compressor and condenser fan motor by pulling in the contactor.
Feb 11, 2011 | Ruud UAKA042 Air Conditioner
4 ton rheem 3yrs old thermostat
It is possible that the relay in the thermostat for "cooling" has gone bad. The relay that runs the blower is different than the condenser relay. Check that you have 24v AC coming from the t-stat to the "y" terminal at the air handler. That same "y" wire should go out to the condenser, make sure then that you have 24v out there. If you have 24v at the condenser then see if the contactor is pulling in. If not then you may have a loss of charge switch that is stopping the current to the contactor. See if you have 24v to the coil of the contactor. If the contactor is pulling in and power is going to the compressor then the compressor has failed. If this is the case the condenser fan will be running but the compressor is not. If neither the condenser fan or the compressor is running then you have a problem in the 24v circuit, which could be a bad wire or a safety switch.
As you can see there are a number of possibilities for your problem. You will need to methodically go through everything to eliminate the possiblities till you isolate the problem,
I hope that this will help you to solve your problem and get you cooling again!
Thanks for using Fixya!
Heatman101
Nov 23, 2009 | Air Purifiers
I was looking at a 4 ton split system,goodman indoor and outdoor fans come on but no compressor think it's the relay but didn't see 1 in the furnace control board,is the relay inside the contactor on the...
Try to put a booster cap in parallel with the compressor capacitor ,but if still the compressor won't start it has a problem and because it's hermetic it has to be replaced.
Sep 14, 2009 | Heating & Cooling
Rheem RGPH 07EAMGR keeps blowing 2A 250V fuse from transformer to circuit board. I can't find a short and the fan will come on for a 20 seconds then the fuse will blow again. i have done this 4 times(i had...
99% of the time proves to be a short- in the thermostat, furnace, condenser, or the 24V wires between them. Time to get out an ohm meter and check continuity between the wires and between each wire and ground - detective work - can be fun!?
Much less likely: condenser contactor, furnace control board, other condenser controls any of which could be drawing too much current. I bet on a short curcuit but if not I'd try changing the contactor first I think.
May 05, 2009 | Heating & Cooling
Replace Contactor Relay on Rheem Air Condenser
I have a Rheem heat pump/airconditioner, Mod # RPFA-036JAS, that I have had problems with for at least 5 years and have paid over $1,000 in parts and service calls. I can vever recreate the problem when a tech is here. It usually happens in the middle of the night. I hear a Click, ckick, click sound, through the unit and it sounds like it is comming out of my air handler, but the outside unit also clicks at the contactor and the condensor cooling fan moter will start and stop about every half secongd or second. Both contactors have been replaced, the small one twice, one capaciter
has been replaced. I allow the unit too cool down and its alright for a few hours. That is difficult when the outside temp is below zero. HELP PLEASE!
Feb 16, 2009 | Heating & Cooling
Heating & Cooling Logo
57 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen