Replaced ECM on my Carrier Heat Pump. Fan still does not run. it starts to move, but stops
    President:
  • 1,124 Answers
It could be the capacitor..
What you describe is very typical behaviour of a bad capacitor..
Should not cost to much..
Be SURE the power is off when you replace it..
Enjoy your day..
Posted on Sep 10, 2009
Condenser fan on heat pump does not turn off
If it is just the condenser fan that means you have a fan relay that has welded shut. Turn power off to your unit and trace the wires from your condenser fan back into the control panel at the unit. You'll have 3 wires going to it. 2 go to the run capacitor and one goes to the fan relay. The one that goes to the fan relay is the part that needs to be replaced. If you have no fan relay and it goes to the main contractor, half of your main contractor is welded shut and will need to be replaced.
Sep 18, 2014 | Carrier 52PQ-515---3 Premier Series Heat...
Furnace won't stop running
Jump out limit switch blower should stop and inducer should come on then the heating sequences should start from there
Nov 28, 2013 | Carrier 52CQ-312-4 Comfort Series Heat...
My Blower starts and stops early causing the lines to freeze up.
Your fan motor might be on the way out, and causing the motor's internal overload to trip.Try feeling the fan motor with the palm of your hand after it trips out.If it's hot (without using test instruments), then I'm willing to bet that fan motor is defective. If it has a variable speed ECM motor, it could just be the electronic module on the back end. some manufacturers will allow you to buy the module separately.If it's an ECM, contact me after you get an ohmmeter and I'll walk you through it. I have a simple inexpensive fix
Aug 03, 2013 | Carrier XHB123D X/Y Series Heat/Cool Air...
Carrier 48NMX042 IFM wont stop, condenser fan motor and compressor wont run
Ok first thing is it sounds like a wiring problem. So first step is to make sure the thermostat is properly connected. Which... the main thing here is there needs to be 24v dc power coming from your control board (transformer) going to the thermostat..generally that is the red wire. All the thermostat does is connect that "red" wire (power) to one of the other wires to complete a circuit. So make sure you have 24 volts... (generally about .5amps) . if you have power than switch thermostat to fan only should energize the green wire only. then switch to ac and move temp low enough that the ac should turn on and that should energize the yellow wire. for sure one of those wires is incorrect now or the fan wouldn't be on OR THE THERMOSTAT IS NOT CONNECTING THEM AND IT IS BAD. Now about the compressor and fan.... those same wires run out to the compressor unit... ok the yellow for ac.. greeen does not go to compressor unit that is for fan only (vent).. red carries the same 24 volts... one difference here is that most carrier units only have the one transformer....so you run the red wire is the +pos 24 volt..and then a "common " wire is needed which is the Ground or neg... that wire on a carrier is brown usually but could be different depending installer. The orange wire goes to the pump reversing valve it is always energized when on ac mode...when heater is on in the winter it is heat pump and is not energized so just connect the orange and yellow together... tell me more specifics if this doesn't help and i'm sure I can help you... thanks Chuck
Jun 22, 2012 | Carrier Heating & Cooling
Fan motor runs backwards
Make sure the capacitor is connected to the start lead, not the run lead(s). Also some fans come with some wires you can switch to reverse the direction. If your motor has them there will be 4 and the label on the motor will tell you how to connect them. Let me know if you need more assistance or if this helps.
Jun 02, 2010 | Carrier 38CKC042 Air Conditioner
When the unit is in heat mode is the fan on the outside supose to run? Capacitor on outside and inside have been replace fan was running when capacitor was first replaced.
Hi, and the outdoor condenser fan should not be on at all in the heat mode unless this is a heat-pump!! So, I can see that this is a 3-ton Carrier split system and I haven't pulled up any information on it, only if I need to. But if the indoor unit runs on natural gas/propane, this would not be a heat-pump and the outdoor fan would run only in the cooling cycle. So, if it is not gas fired it is a heat-pump, and yes the outdoor unit should be up and running all year around. On a heat-pump you will have what is called a reversing valve in the refrigerant system that directs the flow of freon in the right direction for the season you are in. Most all heat-pumps will have a heat strip package installed in unit for emergency and aux. heat if compressor lets say fails. You're thermostat will have on it a selector switch, you will see on it these labels, Aux., emergency heat, auto/on/off/heat/cool. You will know from what I have just went through with you what you have. Forgive me for such a long explanation as I like my customers to understand more about there units in question. I could have just said yes or no and thanks? Doesn't work like that for me. I hope this has helped you out. One thing, If you determine this is a heat-pump and the fan is not on when in heat, you may have lost this condenser fan motor? You say both run caps. were replaced, and normally when you loose a run cap for a motor they will open internally, leak, buldge ect. So if this is taking place, if you can yourself take a look at the run cap. Also, make sure you have 220 volts to condensing unit. If not, check breaker probably a 30 amp double pole to see if it has tripped. You will have a disconnect box at the unit and inside there will also be 2 fuses. If you see only a pull out square connect, the fuses are still there but in behind the cover. If you have power and can hear the compressor come on but fan does not, I am positive you will have A faulty run cap, or faulty motor. Kill power to unit and try and slide a metal coat hanger down to prop or blade to see if it spins freely. If it is hard to turn bearings are froze up. If the capacitor seems to look ok, and the motor does spin free, It still may have open windings. Do these checks I have asked of you on power to the outdoor unit. If all is good, Stand in front of the unit and have someone turn the stat on for what season you are in. Lower or raise temp a ways above or below room temp. You should her the contactor close and compressor will start along with the condenser motor.If compressor starts and motor does not, then I would say it has failed and or cap again. When a motor is replaced, the run cap must always be replaced to!! Please get back to me and keep me posted. I will wait to hear what has happened. Good Luck.
Sincerely,
Shastalaker7
Jan 13, 2010 | Carrier 38CKC036 Air Conditioner
Carrier AC fan not working right
it sounds like the capacitor is shot there is usually a duel capacitor one side is for the compressor and the other side is for the condensor fan motor if it is bad the motor will over heat and turn off on internal overload
Aug 25, 2009 | Heating & Cooling
UNIT RUN FOR APPROX 1HR. THEN OUTSIDE FAN STOPS RUNNING AND STARTS HUMMING
whats going on is your outdoor fan motor is over amping itself and causing it to go into heat overload shutting down the fan. It needs to be replaced
Jun 10, 2009 | Carrier Heating & Cooling
Heating & Cooling Logo
14 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen