Question about Electrical Supplies
I'm installing a 40A 2-pole CH GFCI breaker in a Square-D panel that is supplying a hot tub. The 8-3 cable runs to a sub-panel beneath in the crawl space beneath the tub. The new GFCI trips immediately upon closing. I opened the breaker in the crawl space and it tripped upon closing. I removed the breaker in the crawl space and it did the same. I disconnected the two hot leads at the GFCI and it tripped upon closing. The only lead left was the neutral so I disconnected that at the GFCI and it remained closed. I find it hard to believe induced voltage could somehow do this. The neutral line and ground line are connected to the same bar in the sub-panel. Can you help?
  • 1 more comment
  • gsawtelle Sep 08, 2009
    Are you there?
    I'm assuming you are there. The two hot line conductors are connected to the two hot terminals on the GFCI. The neutral conductor is connected to the neutral terminal on the GFCI breaker. I understand how a GFCI works and have installed single pole versions before. The pig-tail lead is connected to the neutral bar in the panel. The ground lead is also connected to that point. There are two bridges of screw connectors on the neutral bar of the panel. The ground wire and neutral pig-tail may be on different bridges. I'm not at the location at this moment.
  • jeepfxr May 11, 2010
    where on the gfci are you connecting the neutral ? the ground and neutral do go on the same bar in the panel.
  • 313 Answers
Try this...
You mentioned a 8-3 cable suppling power to the sub-panel. I am assuming you have a 8-3 WITH ground or 4 conductors, black, red, white AND ground.
In the sub-panel do not bond the neutral bar to the box or ground bar. If there is a green bonding screw on the neutral bar...remove it. If you have only one (1) neutral bar add another bar for your grounds and bond this bar to the box. Keep the neutrals isolated from the grounds.
I hope this has helped. If you need additional information please send me a follow-question.
Posted on Sep 10, 2009
5000 watt inverter schematics circuit
If you have (90) 50w lamps = 4500 watts total. Assuming a 120/240 panel, if you put 1/2 on one "side" of the panel and the other 1/2 on the other "side" of the panel, that would be 2250 watts on each half. The generator should be rated *at least* 125% of the load; 4500w x 1.25 = 5625W. Using a 4500W generator on this load will cause it to overheat and shorten its life as it is running at 100% of capacity all the time..
One half of the panel is 120V to neutral, and the other is 120V to neutral - or 240V between both circuit breaker terminals. Ohms law for DC circuits and purely resistive AC circuits says Volts x Amps = Watts; or Watts / Volts = Amps. So, 2250W / 120V = 18.75A on each pole of a 2 pole circuit breaker that feeds the sub panel. A #12 copper wire is rated for 20 amps; but as per National Electrical Code - must be de-rated to 80% of rating which means it is good up to 16 amps maximum. A #10 copper wire is rated for 30 amps, but it too must be derated to 80%, making it good for 24 amps maximum. So, if you are going to feed a sub panel supplying (90) 50watt lamps, you will need to run a #10/3 copper cable from a two pole 30 amp circuit breaker at the generator to a 120/240 volt "main lug only" sub panel rated for at least 30 amps.
Divide your load evenly across the sub panel - (4) 15 amps circuits via (2) two pole 15 amp circuit breakers on each "side" of the panel if you run (2) 14/3 cables out to the lights - or (4) single pole 15 amp circuit breakers if you run (4) 14/2 cables out to the lights. No circuit breaker terminal should have more than 23 lamps that means you have (2) w/ 22 lamps and (2) with 23 lamps. The circuit w/ 23 lamps will draw 23 lamps x 50w = 1150W. 1150W / 120V = 9.6A. The 22 lamp load will be 22 x 50w = 1100W. 110W / 120V = 9.2A. Which is well within the 12A maximum allowed (after derating as required by code) by a #14 copper wire rated for 15A.
Mar 10, 2014 | Electrical Supplies
Qo260gfi not tripping
Question is not fully clear.
2-pole 240Volt gfci circuit breaker requires the white wire be connected to neutral busbar.
Easy solution for 240Volt spa that comes with gfci:
Replace spa gfci with regular non-gfci breaker.
Install 2-pole GFCI breaker in main panel, and connect wire to spa breaker.
http://waterheatertimer.org/How-to-wire-GFCI.html#2-pole-gfci
Having 2 breakers is not a problem.
Having 2 GFCI on same circuit is a problem.
Apr 18, 2013 | Pool & Spa
My hot tub has been running perfectly until a few nights ago when the GFCI breaker tripped and now it wont reset
Either you have a ground fault or the GFCI is toasted. Turn off the power to the GFCI, open the box the GFCI is in and disconnect the output wires, close up the box, re-energize, and try to reset it again. This will tell you which problem you have.
Jun 04, 2012 | Cutler Hammer CH250 2 pole 50 amp
Need to install a 2pole 20 amp gfci breaker in an ite bq panel. what are my options as I don't think they make this breaker in type bq?
Hi Pauline, I'm an electrician and can help you with this problem.
The only breakers that are permitted to be installed in any circuit breaker panel are listed inside the door on the label. Introducing any other type or brand is a fire hazard and a code violation. The national electrical code is very clear on this.
If you need to provide a GFCI protected circuit from this panel, you'll probably need to install a smaller panel from this panel - called "sub-panel" of a brand and type that will accept a GFCI circuit breaker. This is done by purchasing a 2P20A GFCI breaker and a smaller circuit capacity / ampacity panel rated for the same voltage as the main panel. You'll also need a ground terminal strip for this panel, too. A 60A main lug panel with 8 or more circuits type panel might be a good place to start. Purchase a 2P circuit breaker with an ampacity no greater than the sub panel is rated at - in my example - a 2P60A would be right. You may use a smaller breaker (2P40A or 2P50A) if you wish - but none greater. Mount the sub panel in a location near the main panel. Remove and discard the bonding screw or lug (if provided and installed already) that may connect the neutral bar and threaded into the panel enclosure. Install the ground terminal strip you purchased separately into the threaded holes provided for it inside the panel enclosure. Install the Ground symbol sticker next to this bar. Run a 4 conductor cable, pipe & wire, etc. feeder sized for 60A based on the location, temperature, etc. between the main panel and the main lug panel. Terminate the cable the sub panel end as follows: black & red or "hot" wires into the the lugs that are connected to the bus bars, white or "neutral" to the neutral bar and the bare or green "ground" wire into the ground terminal strip you installed previously.
Next terminate the other end of the cable. Power off the main panel completely. Terminate the white neutral and the bare or green cable in the neutral bar in separate terminals. Install only one wire per terminal - do not "double up" wires under a single screw. If there is a separate strip for neutral and separate strip for ground - maintain neutral wires to neutral strip and ground wires to ground strip. Also, do not intermix ground and neutral wires in the others terminal strips! Install the 2P60A breaker in an unused space in the main panel. Connect the two hot wires to the breaker terminals. If using aluminum wires, be sure to clean and apply oxide inhibitor to stripped ends of the wires.
Now, you should have a smaller panel with 8 or more empty spaces for circuit breakers that will become live when the 2P60A breaker is in the main panel is turned on. With it still off, install the 2P20A GFCI breaker in the new sub panel. Run your circuit(s) to this panel. Connect them as usual - but any neutral and ground wires installed must be terminated in their respective terminal strips. As mentioned above, never install them in the others strip.
If installing in a 3 phase environment - you may wish to install a 3 phase sub panel so that 3 phase loads can be connected to it. This will require a 3P60A breaker and 5 wires instead of 4 wires to be run between the two panels. The additional wire would be a hot and blue in color for a 240/208/120 panel.
I hope this helps & good luck!
Apr 26, 2012 | Siemens /ite Bq Circuit Breaker Bq3b090 3p...
My breaker is conected to a hot tub. tub was working fine in auto mode. Turned on jets and breaker tripped. will not reset can you help me
I am assuming this is a GFCI circuit breaker? If it is it will have a "test" button on the breaker. When you say "jets" i'm assuming you mean when you turn on the blower to make the air bubbles? It could be you have a problem with the blower motor. When you start the blower, it trips the breaker. Be sure the blower is in off position when you reset the breaker. The most common fault though on a spa/hot tub is with the heater. If the element goes bad, and current flows to ground, it will trip the GFCI breaker. Again try and turn all functions off. Reset breaker, and then turn on one at a time till the breaker trips. First the pump, then the heat, then the blower.
Oct 06, 2010 | Square D Trilliant 40 Amp Circuit Breaker...
Running a 220 volt 40amp service for my hot tub.
By code, this would require underground cable to a breaker panel with a double pole GFI (maybe that's what you were planning). Then from the breaker panel to outlets, pumps, etc.
40 amp breaker will require 8 AWG cable.
More info, let me know...
Charlie
Aug 23, 2009 | Qca Spas GT 396 Hot Tub
Hooking up a Hot tub
Everything above tells me this is 120V unit...if thats the case a single pole breaker is sufficient. Also by what you have written, a 15 amp breaker should suffice.
Jun 22, 2009 | Spa Parts Plus GFCI, Circuit Breaker, 30...
30 amp 2 pole GE GFCI breaker pops on hot tub after hrs of use
I have seen circuit breakers trip at a lower amperage. It seems that they are weak. Generally circuit breakers run with 80% load with no problem, in your case 24 amps. I would replace the circuit breaker.
Jan 11, 2009 | Spa Parts Plus GFCI, Circuit Breaker, 30...
I need to install a GFI breaker on a Baptistry.
You could install a standard GFCI in line at each component ( heater, pump & timer) or you could install AFCI breakers similar to what are required in many residential codes (provide the same protection at the panel not at the location... http://www.cpsc.gov/CPSCPUB/PUBS/afcifac8.PDF
The AFCI breakers will need to match your panel type (siemens, GE or Square-D) and the amperage/configuration.
I would install them at the lowest level (closest to the components) in the system to reduce possibility of fire in the wiring between the components and the afci breaker.
Jan 04, 2009 | Electrical Supplies
Electrical Supplies Logo
188 people viewed this question
Top Electrical Supplies Experts
Craig Butler
Craig Butler
Steve
Gene Haynes
Are you an Electrical Supply Expert? Answer questions, earn points and help others