Question about Carrier 38CKC042 Air Conditioner
Carrier AC condenser unit stopped working. Power supply OK. Fan motor is not turning, and compressor just makes a click. This happened overnight. Any thoughts as to what the culprit may be??
  • 252 Answers
If all is as you say you probably have a bad "dual motor run capacitor"
Posted on Sep 07, 2009
Replace compacitor on Carrier 5 ton 3 phase AC
Your 3 phase unit should not have a capacitor. I'm guessing it's single phase. If it's a single capacitor than the compressor should not be going to it also. To test the motor, common to start plus common to run should equal the ohms you get between start and run. For instance, 1.2 ohms+ 2.2 ohms= 3.4 ohms. Follow the wiring diagram on the inside of the door, send model number!!
Aug 29, 2017 | Carrier Heating & Cooling
I have a Carries AC unit (model FK4CNF002). Heat pump in the outside works but blower doesn't (tried both heat and cool). Power load (240V) on the blower is there and I also measured the voltage on control...
If you have determined that the line voltage is getting to the blower motor then the unit is defective and needs to be replaced. Check for the presence of the voltage at the wires going directly into the motor to make sure. It is not the compactor relay because it supplies power to both the compressor and condenser fan. If your air handler is inside the house, the housing also has circuit breakers for the fan motor - check that also.
Nov 23, 2013 | Carrier Heating & Cooling
Carrier 48NMX042 IFM wont stop, condenser fan motor and compressor wont run
Ok first thing is it sounds like a wiring problem. So first step is to make sure the thermostat is properly connected. Which... the main thing here is there needs to be 24v dc power coming from your control board (transformer) going to the thermostat..generally that is the red wire. All the thermostat does is connect that "red" wire (power) to one of the other wires to complete a circuit. So make sure you have 24 volts... (generally about .5amps) . if you have power than switch thermostat to fan only should energize the green wire only. then switch to ac and move temp low enough that the ac should turn on and that should energize the yellow wire. for sure one of those wires is incorrect now or the fan wouldn't be on OR THE THERMOSTAT IS NOT CONNECTING THEM AND IT IS BAD. Now about the compressor and fan.... those same wires run out to the compressor unit... ok the yellow for ac.. greeen does not go to compressor unit that is for fan only (vent).. red carries the same 24 volts... one difference here is that most carrier units only have the one transformer....so you run the red wire is the +pos 24 volt..and then a "common " wire is needed which is the Ground or neg... that wire on a carrier is brown usually but could be different depending installer. The orange wire goes to the pump reversing valve it is always energized when on ac mode...when heater is on in the winter it is heat pump and is not energized so just connect the orange and yellow together... tell me more specifics if this doesn't help and i'm sure I can help you... thanks Chuck
Jun 22, 2012 | Carrier Heating & Cooling
AC Condenser motor will stop at 1pm but inside unit is still running but no AC. If I turn the AC unit breaker unit off and then an hour later turn it back on. The unit runs fine all day until 1pm. Had a...
Hi, the tech should have been able to figure the stat out with out a manual to see why the condenser is shutting off at 1:00 P.M. This is unusual for this to happen, unless it was winter and this is a heat-pump going into defrost, but just the fan would shut down. Does this unit have a box on it that was installed by your electric company that shuts the unit off during high peak conditions in the summer? This would cause it to shut down at the same time everyday. If not, it would have to be something in the thermostat that is set for it to shut off at that time. It still does not make since, as it would shut both the indoor and outdoor unit off, not just the condenser. Are you saying that just the condenser fan motor is shutting off, but the compressor continues to run until it shuts off on high head pressure when the fan stops, or does the complete outdoor unit shut down fan, compressor and all at that time??. It sounds to me like this outdoor unit has a time delay relay that has a fault in it may be shutting it off at this time daily? Please let me know if its just the condenser fan motor that shuts off, or if the complete unit is shutting off all together, this will help .
Sincerely,
Shastalaker7
A/C, Heating,
Sep 08, 2010 | Carrier 38CKC060 Air Conditioner
Ac unit clicks outside but nothing engages fan or compressor on unit furnace still runs for heat setting and fan still blows but ac will not engage just hear a clicking was running for three days this...
Have you check the outside breaker? If its ok then you got a problem in your electrical system inside the unit probably the contactor is not engaging this is where the 24 volts from the thermostat calls for the 240 volts to run the condenser fan and compressor. Be careful checking this out because of the high voltage.
Jul 09, 2010 | Carrier 38CKC048 Air Conditioner
Condenser Fan and Compressor not turning on.
Are you sure you have high voltage going to the unit? One wire from fan lands on top left of contactor, the other two go to C and Fan on capacitor. Manually push in contactor, if no fan than no high voltage.
Jun 05, 2017 | Carrier 38CKC060 Air Conditioner
Carrier AC fan not working right
it sounds like the capacitor is shot there is usually a duel capacitor one side is for the compressor and the other side is for the condensor fan motor if it is bad the motor will over heat and turn off on internal overload
Aug 25, 2009 | Heating & Cooling
I live in south texas overnight the ac stopped GOODMAN MODEL
Is the condenser fan (outside) turning? You mention that it's hot but don't say if it's turning or not.
These fan motors normally run pretty hot, but not so much that they shut down due to internal thermal overload protectors.
Both the compressor and the fan have termperature overload protectors to keep them from burning out the motor in the event of an overheated condition. The condenser fan must be running or high freon pressure will put an excessive load on the compressor and it will 'kick out' the high-temp overload protector.
Turn off the unit by pulling the outside disconnect (in a small box near the outside compressor unit) or flip the AC breakers in the breaker box. Wait about 30 minutes for the unit to cool off and turn it back on. If the compressor and fan both run for awhile then kick back off, or the fan motor seems to be working under excessive strain, you've probably got a bad motor start condenser (inside the unit) that little round can that is connected through the fan motor wiring. If it's swollen or leaking, it's almost surely defective and even if it's not, excessive load on the motor is a classic sign of a bad start condenser.
You can usually find these at electrical supply stores, well-stocked hardware stores, or most certainly at an HVAC parts house. Be sure to replace the old one with one of the EXACT same value (in voltage and Microfarads (mF) capacity. The shape may be a little different, but as long as the electrical characteristics are the same and is rated at the same or higher voltage than the original, it will work.
Connect the new condenser, mount it to the frame, and restart the unit. This should take care of the problem.
Hope this helps.
Jun 28, 2009 | Heating & Cooling
AC blower runs but compressor will not.
It could be the CONTACTOR. It could be dirty and when the system calls to run, the contactor won't make contact and complete the circuit. Worse case scenario, compressor is siezed up. If you hear a clicking noise at the condensing unit where the compressor is located, that could be the overload protector clicking and breaking the circuit if the compressor is seized up. Good luck. I hope it is a contactor or a capacitor.
May 31, 2009 | Heating & Cooling
Carrier home ac system
sounds like your contactor is stuck closed.This is the part that high voltage connects to and lets power through to the compressor and condenser fan motor when you get a call for cooling.If you go to pull it out,kill the power outside AND at the furnace.
Aug 12, 2008 | Carrier Heating & Cooling
Carrier 38CKC042 Air Conditioner Logo
374 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others