Vulcan central heating unit ilec 5010023 - comms diag o/t pressure flame - green light flashing 11 times
3 Suggested Answers
  • 53 Answers
SOURCE: Vulcan Ilec central heater main burners turn off after few second
Flame rollout sensors, overheat thermistor, air proving switch, bad earthing, blocked flue. Any of these things can cause your problem. If its a permanent pilot, is it clean burning?? If electronic ignition, is the flame rod clean i.e. no carbon or rust etc.. Safest bet is a qualified gasfitter take a look at it.
Posted on Jul 19, 2009
shastalaker7
  • 1515 Answers
SOURCE: I had a vulcan central heating unit that was made
Hi Rob, The number you have listed AUW230A may be the model number. You say its a central heat so, If it is a package unit, the model, serial, and all of the ratings would be on the unit near the elect box on a package unit.I do know by the # you gave me it is a Vulcan 3000 watt thermostatically controlled Immersion heater. Here is a link I can give you, they deal with this heater for parts Ect. that maybe of help to you, it is www.grainger.com. There are many model # and I believe this is it, AUW230A. I hope this helps Rob, Sincerely,
Shastalaker7
Posted on Nov 17, 2009
The pilot light takes a long time to light, once lit it barely has but a small blue flame, what is the problem?
Ensure that the unit receives the standard gas pressure as rated on its nameplate.
Pilot orifice may be partially plugged or has some dirt on it, You have to dismantle the whole pilot assembly to gain access in cleaning the pilot orifice. Be careful not to enlarge the orifice bore in cleaning for that will only result to poor pilot flame quality.
The thermopile must be free of soot or soot form of dirt in order to detect the right amount of heat from the pilot flame so that it could also, in turn generate the right amount of voltage needed by the gas valve for pilot and burner operation.
Regards.
Jun 23, 2011 | Vulcan EF3 Deep Fryer
Hi, the lights on my circiut board are flashing the one on the left is on all the time and the one to the right of it flashes two times and then waits and then flashes two times again
Error Codes
A green LED indicates system faults
Steady On: System OK
Steady OFF: Board control fault or no power applied
1 Flash: Ignition failure (control in one-hour lockout)
2 Flashes: Pressure switch fault, fails open (switch is
stuck open)
3 Flashes: Limit switch open (main or auxiliary)
4 Flashes: Pressure switch fault, fails closed (switch is
stuck closed)
A yellow LED indicates flame status
Steady on: Normal flame is sensed
Flashes: As flame weakens, frequency of LED flashes
increases
hope this is helpful.
Dec 21, 2010 | Ruud Central System Air Conditioner
Armstrong upflow,unit works intermittent problem,call for heat nothing happens,error code of 5 blinks then 6 blinks. i have no manuel, and the panels dont have the codes on them. anyone have access to the...
Armstrong
FAILURE CODES
LED Status Fault Description
Off
No Power to the System Control
Steady Flash (11 or more flashes with no pause)
Normal Operation (Standby or call for heat)
2 Flashes
Pressure Switch Closed When It Should Be Open
3 Flashes
Pressure Switch Stuck Open 30 Seconds or Longer After Call for Heat (System in 5-minute delay mode before next call for heat). On/off switch in "off" position during a call for heat will generate this code.
4 Flashes
Open Limit Switch or Limit Switch Circuit
5 Flashes
Flame Sense Signal Sensed Out of Proper Sequence
6 Flashes - pause - 1 Flash (see Note 1)*
Soft Lockout Type 1 (Failure to light within 4 trials for ignition)
6 Flashes - pause - 2 Flashes (see Notes 1 & 2)*
Soft Lockout Type 2 (Flame sense lost during run)
6 Flashes - pause - 3 Flashes (see Notes 1 & 2)*
Soft Lockout Type 3 (Pressure switch opened during run)
6 Flashes - pause - 4 Flashes (see Notes 1 & 2)*
Soft Lockout Type 4 (Limit or limit circuit opened during run)
6 Flashes - pause - 5 Flashes (see Note 1)*
Soft Lockout Type 5 (Flame has gone away after Error Code 5)
6 Flashes - pause - 7 Flashes (see Note 1)*
Soft Lockout Type 7 (Self-check failure)
10 Flashes* - SV9520H8034 only
Line Input Voltage Polarity Reversed
Dec 12, 2009 | Coleman Heating & Cooling
I had a vulcan central heating unit that was made in 1990. Could you please tell me what the model number is on a 1990 vulcan central heating unit. Thanks, Rob
Shastalaker7
Nov 17, 2009 | Vulcan AUW230A Heater
We have a Vulcan Ultra high efficiency gas ducted heating
Gas ducted central heater won't switch on all of a sudden
Nov 04, 2009 | Vulcan AUW230A Heater
I am renting a unit and just moved into a brand
try changing batteries in thermostat for starts.not uncommon for batteries to be faulty in new thermostats especially if it was made in red china
Jul 23, 2009 | Heating & Cooling
Jul 02, 2009 | Heating & Cooling
10yr Vulcan Central Heating unit. Had tech come out and said main fan unit was faulty. I replaced myself and still not working. I discovered the O/Temp manual switch had cut off power. When I reset the...
I have the same problem, heating unit will not ignite, it trips out, i go into the roof cavity and remove the top of the unit (4 screws) and there is a motherboard, it has a Green light flashing what tells you the type of fault it has, mine has 3 Flashes telling me it a combustion air pressure system failure, ithen push the reset switch and it starts to initiate, a red light comes on and then it ignites and it will work for about 30 minutes to an hour and a half.
Hope this helps
Shane
Sep 08, 2008 | Heating & Cooling
I have a Vulcan/ILEC ducted central heating system. The controller is hard wired. After about 1-2 hours the system switches itself off and the controller is indicating "Reset" which we do and...
there is probably a sensor in the duct somewhere that is either fault or maybe quite dusty. be careful though it may have mains voltage at the terminals
Jul 10, 2008 | Heating & Cooling
Heating & Cooling Logo
172 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen