Question about Smith A.O. SMITH Cyclone XHE Natural Gas Commercial Water Heater BTH-120
Fault blower prover switch open.
Does the fan need to be replaced if tubes look good and the electrical connections are good.
I have a Jandy LXi 400N that will not start. I push the button and it wants to go, but the blower does not come on. Sometimes the blower comes on and it works and other times it tries to come on, but...
The blower must be operating during the test procedure
for the blower pressure switch. Start by checking the
voltage between test point 1 and the common and
normally open contacts of the air flow switch.
Leaving the black lead of the meter on test point 1, check
the voltage at test point 11. If there is not 20-28 Volts
AC at this point, the eight-pin wire harness is faulty and
must be replaced. If 20-28 Volts AC is detected at this
point, then move the red lead of the meter to the Air Flow
Switch NO contact.
If 20-28 Volts AC is detected at this point, the device in
this circuit is closed and the circuit is working properly.
If there is not 20-28 Volts AC at the Air Flow Switch
NO contact, the pressure switch contacts are open. This
is usually due to a blower speed problem or a problem
with the air pressure tube connection between the blower
housing and the switch.
Be sure that the blower is on and that it is working
properly. Check that the gray flexible tube between
the blower pressure switch and the blower housing
is connected at both ends and has no holes or splits.
Replace the tube if necessary. If there is no problem with
the blower or the tube, check for blockages in the vent,
flue or heat exchanger that would prevent air flow. If no
blockages are found, replace the pressure switch.
If the Air Flow Switch NO contact shows 20-28 Volts AC
and the ignition control shows an air flow fault, then there
is a bad connection between the blower pressure switch
and the ignition control, or the ignition control is faulty.
Jan 03, 2015 | Jandy LXI 400 NATURAL GAS POOL HEATER -
AO error code on 250k btu hayward pool heater
Dear ,
Please try the below solutions,
Solution 1:
If the blower prover switch does not close after the blower starts the control will stop the ignition trial go into lockout. The blower will continue to run. Automatic reset is immediate after the switch closes
Solution 2:
If the blower prover switch opens unexpectedly during operation the control will shut down and attempt to re-light. If the switch does not close after the blower starts the control will go into lockout with the blower running. Automatic reset is immediate after error is corrected
Solution 3:
If the blower prover switch opens during the postpurge cycle (heater is not fir- ing) the control will display the error code. The post-purge cycle will be com- pleted once the blower prover switch close
Regards,
Samy
Aug 10, 2014 | Hayward Pool & Spa
Want to change fan on blower heater
Removal
  1. Remove wiper arms.
  2. Remove cowl panel.
  3. Disconnect blower motor electrical connector and vent tube.
  4. Remove blower motor retaining screws.
  1. Remove fan retaining nut from blower shaft through plenum opening while holding the fan from the engine compartment.
  2. Remove fan from blower motor while removing blower motor from vehicle.
Installation
  1. Hold fan through plenum opening.
  2. Install blower motor to vehicle while installing fan to blower motor.
  3. Install fan retaining nut to blower motor shaft through plenum opening.
  4. Install blower motor retaining screws.
  5. Connect electrical connector and vent tube.
  6. Install cowl panel.
  7. Install wiper arms.
Aug 13, 2013 | 1991 Oldsmobile Cutlass Ciera
Fan blower switch not working
Keep in mind you have an electrical problem and the first place to look is the fuse box. Then the relays. Check if power gets to them. - If not, the switch and/or connections to them may be at fault. - If yes, check the motor. At this point you may know if the problem is there.
Dec 20, 2011 | 1999 Dodge Durango
I have a commercial water heater and on the screen it says "Blower Prover Open" and i have no hot water at any sinks.
The fan is not operating -- when this conditon exists, the unit will not fire up. Here's a link to the manual. The unit needs servicing.
http://www.hotwater.com/lit/im/com_gas/318556-000.pdf
Here are some excerpts from the manual relative to the blower prover and error msgs.
If the Blower Prover switch contacts do not close after the
Combustion Blower is energized the Control System will lock out and display Blower Prover Open
Blower Prover Open
Fault occurred 2 mins ago
The blower prover switch remains
open after the blower has been
energized.
Call a service professional:
Your Company Name Here
(press [DOWN] for more....)
These plastic sensing tubes must be routed to the correct sensing ports on the water heater. Sensing tube
routing should always be checked whenever Blower Prover Open, Blower Prover Failure, Blocked Air
Intake or Blocked Exhaust is displayed on the Control System LCD, see Figure 31 on page 29. These "Fault
Conditions" can be caused by incorrect sensing tube routing.
Charlie
Mar 20, 2011 | Smith A.O. SMITH Cyclone XHE Natural Gas...
Ao appears after ignigtion
Either the fan is not working, or the fan prover (pressure switch) switch is stuck. If you can hear the fan going strong, it is most likely the switch. You may try to just clean it out, but you may need a replacement.
This error is produced when the blower prover switch does not close after the blower starts, the control will stop the ignition and go into lockout. Automatic reset is immediate after the blower prover switch closes.
If you keep having this problem, contact a reputable service company, especially if it's under warranty.
The link to the owners manual is below, it references fault codes, etc..
Hope this helps.
http://74.125.95.132/search?q=cache:4mAdY7bLfoQJ:www.haywardnet.com/products/Manuals/pdfs/Manual227.pdf+hayward+AO+error
Dec 30, 2010 | Hayward H Series Pool & Spa Heater 400k...
How do I convert from blower to vac
First, remove the blower tube. Then connect the collection bag on the blower tube outelt. Then open the bottom fan cover. Keep it open and connect the vacuum tube into the opening.
Dec 05, 2010 | Craftsman 225 Mph Electric Blower Vac
Automatic gas shutdown light comes on. replaced ignitor that was not glowing. worked friday. today troubleshooted new ignitor is fine. replaced ignition control box. still no power (voltage) going to...
This sounds like your fan prover (air switch)
check switch continuity, and air switch tubing.
Replace if neccessary.
Sometimes these vinyl air tubes just melt
Nov 01, 2010 | Jandy Laars Lt 250,000 Btu Heater
Error AO ON MY HAYWORD H SERIES POOL HEATER
The AO mindicates an open prover switch ,, here from Hawward site .
immediate after error is corrected.
reset is immediate after the switch closes.
May 08, 2010 | Hayward H Series Pool & Spa Heater 400k...
AO error
Hope this helps.
http://74.125.95.132/search?q=cache:4mAdY7bLfoQJ:www.haywardnet.com/products/Manuals/pdfs/Manual227.pdf+hayward+AO+error&cd=7&hl=en&ct=clnk&gl=us
Sep 16, 2009 | Hayward H Series Pool & Spa Heater 400k...
Smith A.O. SMITH Cyclone XHE Natural Gas Commercial Water Heater BTH-120 Logo
575 people viewed this question
Top Smith Pool & Spa Experts
Mike Squire
Jay Finke
Jay Finke
Bill Jordan
Are you a Smith Pool and Spa Expert? Answer questions, earn points and help others