Furnace Ignitor have a Goodman furnace and it kicks on however the ignitor blows out. What could my problem be? The model number is GMS804703ANA. I did not see this in the model numbers
  • 1 more comment
  • lmissdanger Dec 03, 2007
    Yes I still have not figured out the problem.
    a couple of seconds after it lights. then the furnace shuts off and then tries to start all over again. It does this like three times. Sometimes it will light and sometimes it won't.
  • Anonymous Mar 17, 2014
    what is an open rollout on a goodman furnace model number gms80703anbd
  • 1,420 Answers
At what point does the pilot blow out? Within 5 seconds after it lights or when the room air blower turns on?
Posted on Dec 03, 2007
  • Chandler Ede
    Chandler Ede Dec 04, 2007
    OK, I suspect that the flame sensor is either dirty or bad or that it is not getting flame to it within a second or two after your burners ignite. I suggest first cleaning the flame tray that allows the flame to travel from the pilot area over to the flame sensor. Secondly, inspect and with a small wire brush, scrub the flame sensor. Check all wiring down from the sensor to the control board. Check all ground wires coming from the control board going to the cabinet.
    Make sure the pilot when it starts is good and blue.
    While you are in the unit, just for kicks, check your filter.
    If this does not help, call a good technician and tell them what you have done so far to rectify the issue. It will save him time and you money.
Goodman gas furnace model number gms80904bna won't light. Changed the flame sensor and the ignitor is bright orange please help
Obvious that the unit isn't getting gas to the ignitor.
To receive gas to the ignitor, there is a gas valve located upstream of the burners.
Have a friend turn on the heat while you are up close to the furnace.
Once the ignitor gets hot, there will be an audible "click" at the gas valve when the low voltage controls call for the gas valve to open to supply gas to the burners.
Listen for it.
If you hear a click, and the furnace still isn't firing, you need to check to see if someone has closed the gas shut off supply valves located on the gas line.
If all the shut off valves are open, you need to verify you have gas pressure in front of the gas regulator.
If you verify have pressure on the upstream side of the regulator, you will need to verify there is also pressure downstream of the regulator.
If there is gas pressure upstream but none downstream, replace the regulator.
If you have pressure downstream of the regulator, and the gas valve clicks, but furnace doesn't light, replace the gas valve.
LP has higher pressure than natural gas, and is dangerous.
LP is heavier than air and will sink to the floor or lowest area.
One static electricity spark is all it takes and an explosion can occur.
Nov 01, 2017 | Goodman Heating & Cooling
How to install a spark ignitor in a gas furnace?
How to install a spark ignitor in a gas furnace? - Fixya
www.fixya.com/support/t15727344-install_spark_ignitor_in_gas_furnace
Jan 8, 2013 - How do I connect the high voltage wire to the Model 990-516 spark - Air ... SOURCE: Goodman furnace wont light, ignitor suspected. Notice.
carrier igniter
Jan 08, 2013 | Heating & Cooling
LOCATION OF 62-24164-01 IGNITOR ON WEATHER KING FURNACE
Who knows? You gotta post a video of your furnace so we can see what you got. Here is the sequence of operation of a late model furnace. they all basically work the same way. They have a draft inducer fan that causes a vacuum in a small hose leading to the pressure switch. If the board reads negative pressure it know the draft motor is working and pulling a draft it then cause the ignitor to kick in and after a minute opens the gas valve. It wait a sec to verify flame with the flame sensor and then if that flame is there it keeps burning and after 30 more seconds the fan kicks in.
Most of the time if the ignitor ain't workin it is either bad or a limit has tripped due to some sort of overheat problem like birdnest or cobwebs and such.
https://www.youtube.com/watch?feature=player_embedded&v=NjOsXv4Z-lg
If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61
Oct 05, 2012 | FACTORY AC PARTS Furnace Spark Ignitor...
I have a goodman gpmn furnace. The ignitor lights, and then the flames turn on, then the blower kicks on, and about 30 seconds later the flames turn off, and the blower continues to blow air. We have tried...
Hello, looks like you limit switch keeps opening because your furnace is overheating, Check your air filter and blower wheel to make sure it is not dirty and make sure you blower motor is moving at the proper speeed. Usually when air flow is cutoff the limit switch will open.
Feb 15, 2011 | Goodman GMS90703BXA Heater
The Goodman Heater was installed in 2004. Thermostat set at 75F, the fan that blows CO2 out was on for about 1 minute, then I could hear the sound of the gas blowing into the furnace, but the ignitor...
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 30, 2010 | Goodman GMS80903BNA Heater
I have a Lenox furnace. Before this igniter kicks off, there is a loud noise comes from furnace. Where is that noise from? Thanks.
This is what we call a "delayed ignition",(gas is not being ignited right away), gas builds up in the chamber and then lights causing a boom. The cause of this problem could be from having dirty burners or ignitor not position to ignite the gas right away or your ignitor may not being glowing enough to ignite the gas being released, check all, Good luck.
Jan 08, 2010 | Goodman GMS90703BXA Heater
I have a goodman gmpn 100-4 REVB furnace that will not stay lit
If the igniter lights the burners the ignitor..... is not bad. Its like a light bulb.... it works or ot doesn't.
You are describing a dirty flame sensor. Dishonest contractors will sell you a new ignitor but clean the flame sensor when the are installing the ignitor. It is located at the opposite end of the burners than the ignitor. It has one wire going to it. Remove it and clean the rod with a piece of fine grit sandpaper. this should be done every year before heating season.
Good luck
Mar 28, 2009 | Goodman GMS90703BXA Heater
Ignitor last a day then goes bad again going on 4th try help .
You are getting improper voltage to the ignitor. Check all grounds both in the furnace as well as at every connection heading back to the circuit breaker panel. If you find none, you will need to replace the circuit board.
Dec 08, 2008 | Goodman GMS90703BXA Heater
I need to remove a goodman ignitor B1401015.
The gas pipe should have a union and shut-off on it. Turn gas off and spn out the gas line. Re-install using pipe dope and check for leaks.