Goodman ac/gas furnace unit mdl. # gmp075-4
Problem:gas furnace will not lite. When i start unit in heat mode , induction blower begins, then igniter at 3.9amps lites. After that unit turns off! Checked gas valve for 24volts and only getting 13volts. Checked voltage from secondary transformer and 27volts is coming out. Could the pc board be a problem, but the red light on the pc board is on continuasly and not blinking , schematic says that is normal operation. I say board is malfunctioning, HELP!
  • Anonymous Feb 19, 2009
    I have a 13-yr old Goodman Gas Furnace, GMP Series. Where is the Flame Sensor?. I took the front panel off furnace and I'm told I need to use a 1/4" driver, remove screws, and clean sensor.
No 24v. going to gas vale to open whentry to lite.
Posted on Nov 04, 2010
I HAD THE SAME PROBLEM, TURNS OUT IT WAS THE FLAME SENSOR, CLEANED IT, AND ALL WAS GOOD
Posted on Dec 13, 2007
Carrier troubleshooting furnace
If the thermostat isn't selected for "FAN" then the relay is stuck. In heat mode the thermostat opens the gas valve and starts the igniter and the induction motor. If the induction fan isn't running, the flame will stop.
Jan 28, 2014 | Office Equipment & Supplies
I have a Goodman GMS9 furnace. When the furnace starts the induction fan runs for about 15 seconds, the ignitor turns on but thats as far as it goes. The burners do not light and I don't think the gas...
The igniter heats a thermocouple to turn on the gas valve. From your description, the thermocouple may have failed. The noisy stack blower probably needs to be replaced but its controller may be in need of replacement as well.
Nov 01, 2013 | Goodman GMS90703BXA Heater
My heil n9mp2 isnt working just hums
is the flame igniting and then cutting off? on a gas furnace, the induction fan motor(draft motor) should start first (if the furnace is so equipped), then the flame, then the blower. if you have an induction motor (flue gas exhaust mmotor) this may be your problem (the induction motor isn't starting), if your unit doesn't have one, have you checked to see that you have gas? finally, the capacitor on the blower motor may be causing the motor not to start.
Jan 06, 2013 | Heating & Cooling
Hi Proper way on wiring furnace.
I can give you a start, For heat only, R terminal on furnace to Red wire to R or RH terminal on thermostat. W terminal to White wire to W terminal on thermostat. G terminal to Green wire to G terminal on thermostat. This will get you heat but not air conditioning.
Jan 06, 2010 | Goodman Heating & Cooling
Hello I have a goodman gas furnace
On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Oct 18, 2009 | Goodman Heating & Cooling
Goodman GMP075-3 ignition problem
bad board,i have had several board failures on goodman
Dec 18, 2008 | Goodman GDS80904BNA Open Flame Heater
Furnace start buts shuts off
It sounds like you have an obstruction in the exhaust vent. Thats why when you bybass the pressure switch it runs ok. Steve
Dec 15, 2008 | Goodman GMS90703BXA Heater
Flame going out!
Take the flame sensor out and clean with fine sand paper or emory cloth
Dec 09, 2008 | Cozy (W352E) Heater
Cozy (W352E) Heater Logo
928 people viewed this question
Top Cozy Heating & Cooling Experts
Paul Carew
vance jones
Tim Whalen