NEED INSTRUCTIONS ON CHARGING LIQUID INTO 410A SYSTEM. HOW MUCH SHOULD BE PUT IN BEFORE TURNING ON COMRESSER. SHOULD I CHARGE FOM THE LIQUID LINE OR THE SUCTINON LINE. IF POSSIBLE GIVE STEP BY STEP PROCEDURE.
  • wm_kidd Aug 03, 2009
    do i charge the liquid from the high side or the low side 410a
    President:
  • 2,185 Answers
Hello Wm_kidd,
Here are the steps:
1. You must take the 410 out of the cylinder in liquid form to ensure that the blend of the refrigerants that make up the 410 are kept in their original mixture.
2. You must throttle your gauges to ensure that the blend vaporizes before it enters the compressor.
3. As you have taken the 410 out of the cylinder in liquid form, when it vaporizes in the hoses going to the compressor the blend will maintain its correct mix .
Please let me know if you still have any questions.
Posted on Aug 01, 2009
  • virtualhost
    virtualhost Aug 03, 2009
    From the low side, my friend. :)
What happens if you would add a charge to a running system that has a low charge on a 404a system and you charge thru the suction as a vapor. I had a memory lapse and have charged 410 systems as a liquid...
as long as you recovered the charge, pulled a vacuum, changed the filter/dryer, and added the correct amount of refrigerant as a liquid, you should be good to go.
Jun 28, 2017 | Hoshizaki Freezer Commercial Ice Machines...
Tip
Charging an air conditioner by superheat or subcooling
Charging AC by superheat and subcool
First charging a unit by superheat, this is only for Acs with an orifice or capillary tube.
Optimum superheat is 12° to 15° at the compressor or suction line outside the unit.
Hook up your gages and put a thermometer on suction line (large line), start the AC. Measure the temperature of the suction line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant, (you can also use a temperature pressure chart), now read the thermometer, let’s say the suction temperature( the thermometer) is 67° and the saturation temperature (the gages or temp. press. Chart), is 55°, subtract the saturation temperature from the suction temperature, 67°- 55° = 12° superheat.
Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, indoor room is at approximate set point of the thermostat). If there is no sight glass then the Optimum sub cooling is 12° to 15° at the outdoor unit.
Hook up your gages and put a thermometer on liquid line (small line), start the AC. Measure the temperature of the liquid line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant,(you can also use a temperature pressure chart), now read the thermometer, let’s say the liquid temperature( the thermometer) is 100° and the saturation temperature (the gages or temp. press. Chart), is 114°, subtract the liquid temperature from the saturation temperature, 114°- 100° = 14° subcool.
This is also the only way to know if your a/c has the proper charge.
on Dec 28, 2009 | Heating & Cooling
How do you put in 410a into Ac unit
You turn system on to cool setting and run temp down until outside unit comes on. Then you connect your suction side of your gauges to the suction side of your outdoor unit. Next you connect the liquid(high)side of your gauges to the liquid line on your outside unit(the little copper line). Connect the middle hose of your gauges to the 410a drum of refrigerant. Before opening the suction or low pressure side of the gauges you need to turn the drum upside down and turn drum of 410a on. Then you need a temp reading meter and clamp to read the temp of your liquid line(small line). While charging you want to make sure to release refrigerant slowly. The unit should call for a specified subcooling on unit plate. 7 to 10 degrees. You take the liquid line temp and subtract it from saturation temp on the high side of your gauges.(it'll be the pink numbers on the right side of your gauge.
Jun 05, 2013 | Heating & Cooling
How do I recharge the freon in my unit? model is 38CKB060300
Hello, freon should be charged by a hvac technician with a epa card. But the way you charge it in is hook up the manifold gauges to the unit tjen take the yellow and hook it up to your refrigerant bottle. If this is a R-22 unit then you add vapor refrigerant to the low side of the system untill your superheat is correct if it is a fixed orifice system, however if it is a txv system then you chek the subooling. If it is a 410a system then the same principle applies however you flip the cylinder upside down and add liquid refrigerant through the low side a little at a time here is a link that shows you proper charging methods http://www.air-conditioning-and-refrigeration-guide.com/charging-air-conditioning-systems.html.
May 27, 2011 | Carrier 38CKC036 Air Conditioner
I have a 4 ton outside and a 5 ton coil inside square footage of the house is 2495 living.my preasures are 75 low side and 225 hi side i'm not getting any flood back is this ok are do i need to add more...
Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, indoor room is at approximate set point of the thermostat). Optimum sub cooling is 12° to 15° at the outdoor unit.
Aug 09, 2010 | Amana Heating & Cooling
Do you have to charge a 3 ton 410a unit split as a liquid? on a 85 d day
It is always best to charge 410a as a liquid to ensure that you get the proper mixing of the refrigerant...just turn the can upside down and take your time adding the liquid slowly...with the unit running.
heatman101
Aug 09, 2010 | Whirlwind FH-778 Air Conditioner
How to refill gas in home spli a/c, advise presure details as wel
Mar 19, 2010 | Panasonic CW-1006FU Air Conditioner
Gas pressure
It depends on the indoor and outdoor temperature and humidity. The low side pressure can be in the area of 135# to 145# with an indoor temperature of 80° and 50% relative humidity, and the outdoor pressure can be in the area of 300# to 330# on a 95° day depending on effeciency rating.
If your asking this to charge your a/c this is not how to charge your a/c.
Dec 25, 2009 | Heating & Cooling
When i was fixed a problem in central ac trane i found decreased in freon r22 and the suctione line was freezed, i charged the ac with froen gas r 22 then i found that the suctione line changed and begin...
You are still low on freon. Charging AC by superheat and subcool
Oct 05, 2009 | Heating & Cooling