Intertherm S3QA042K compressor won't restart
I have an Intertherm S3QA042K that has an intermittent problem. Once the compressor runs and cools house to set temp and cycles off the compressor won't restart when the thermostat calls for cooling again. I've checked the run cap and it checks fine, replaced contactor, thermostat, and wiring from outside unit to inside unit. I can switch off the breaker to the compressor wait for an hour or so and then switch it back on and it starts and cools again to set temp. Problem returns after next cycle or so where the compressor won't restart. The contactor clicks and I'm getting 24VAC . Shut off breaker, wait, and reset breaker and it runs again
    Master:
  • 414 Answers
Sounds like rotor lock. (intertherm sold a hard start kit under the name "soft start" kit for high temperature areas) If you hear your bus bar humming in the electrical panel when it attempts to start this is a good indication.
Posted on Jan 26, 2011
  • 30 Answers
You probably need a hard-start kit. A hard-start kit connects to the run capacitor and provides a starting boost for your compressor. If you install a hard-start kit, monitor your a/c for a while because it is possible that the bearings in the compressor are going bad.
Posted on Jul 30, 2009
Intertherm MGHA-070ABFC-05 will not run/cool
Multiple problems. Eliminate thermostat first. Remove face from wall and turn on breaker. If fan still runs you have a bad board or bad relay. If fan outside is running compressor should be too. These operate on same contactor. Verify you are getting 24 volts to coil side of contactor. If odf stops working and contactor remains pulled in you have a bad motor. If odf motor stops working the compressor will shut off due to overheating.
Jun 07, 2016 | Intertherm Heating & Cooling
INTERTHERM HEAT PUMP/AC. BLOWER KEEPS RUNNING WITHOUT THE COMPRESSOR ON. SOMETIMES FOR HOURS. ALREADY REPLACED THE CONTROL AND LIMIT SWITCH.
Blower? Internal house air blower I assume. - Blower relay contacts pitted and stick in on position.
BAD Control BOARD, fault or adjustment program keeping relay energized. Bad emperature sensor not telling Board unit has use up cold air. loose wiring to sensors and board connections
Sep 11, 2013 | Intertherm Heating & Cooling
Compressor dosen't restart
replace capacitors might be going off on safety.
Jul 21, 2013 | Dometic Rooftop RV Air Conditioner
I have a True GDM10 that won't cool. Motor runs normal, Evap fan is running, no ice build up, just won't cool. Is this a coolant problem and can a True GDM10 be recharged? See no hook ups in t
First let me ask, are you sure the compressor is running? If you verified that it was running by vibrations in the compressor area just know that the condenser fan can also cause those if your machine has one. The way to tell is if the compressor is generating heat. With that said, assuming that the compressor is running, and all applicable fans are running, you need to determine if the machine was losing cool over time or did it happen overnight? If the latter of the two you'll need to isolate where the leak is, be it the evaporator or the compressor area. To actually add freon to the system if no access ports are available you;ll need to get a piercing valve, I personally use pt# bpv-31 bullet piercing valves.
Jun 15, 2012 | True GDM-10 Refrigerator
Goodman Model CPLE24-1C - Unit will run and cool but after running for an hour in 100 degree plus heat - Compressor will not restart the next time the thermostat calls for restart
First off, the unit shouldn't be running continuously for an hour, that's a sign of the unit being undersized for the house. So, therefor the house is probably heating up so quickly that the compressor doesn't have time to equal out pressures to restart again, especially in the 100 degrees.
Jul 15, 2010 | Goodman CPLE24-1 Air Conditioner
Compressor will not stay on.
very good possibility that it is low on freon. If indoor unit is blowing ambient air, not cooling is happening. If this is the case and you are sure the compressor is running and then shutting off, the compressor could be overheating and the internal overload is taking out the compressor. If outdoor fan runs and compressor runs, probably cause. If capacitor is bad, unit would most likely not run that long. While unit is running, feel the large line at the condensing unit. If it is cold, and stays cold, could be something else going on. If stays warm, most likely low on freon.
Apr 19, 2010 | Intertherm P3RA-030K Air Conditioner
Will run and cool until the thermostat turns it off and will not start back up. Inside fan continues to run. Compressor is completely dead.
Dear jack289,
The thermostat is not working properly. When thermostat cutsoff the compressor Please turn the thermostat knob to higher setting if compressor starts working then please change the thermostat. The fan will run continuously since only the compressor is controlled by the themostat.
Regards,
ramesh22
Jun 25, 2008 | Intertherm Heating & Cooling
Intertherm gas furnace
Need more info. Are you saying that when tstat calls for heat then it short cycles. But if you turn it off then back on it runs ok?
Mar 21, 2008 | Heating & Cooling
Heating & Cooling Logo
406 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen