15-ton Allied commercial a/c
I am working on a 15-ton Allied commercial a/c unit. This unit has a Wagner three-phase line voltage monitor. When the emergency generator comes on, the split-second amp spike between clean power and generator power trips the monitor. Is there a setting on this monitor that I can adjust to correct this problem?
P.S. There are three other Allied units with the same monitor that are connected to separate emergency generators, and the amp spike does not trip those monitors.
  • knobloch-air Aug 05, 2009
    It does not have an auto reset option, I have to manually reset the unit each time the generator comes on and goes off. I'm not sure how to get to the line differential settings. Your answer did help me a lot and I sure do thank you!
  • 68 Answers
It may not be the start of the generator but the voltage drop. most monitors have a low voltage cut out and a line differential setting have you compared the settings with this monitor, does it have an auto reset option to turn on
Posted on Aug 04, 2009
How do I balance the voltage of the 3 phases L1-N, L2-N and L3-N?
If you are measuring unbalanced voltage when the unit is running but unloaded, the problem most likely is in the generator windings. One of the windings could possibly be shorted or failing.
Nov 13, 2014 | Electrical Supplies
Load resister is not working it is very hard to peddle
Procedure 6.4 - Troubleshooting the Generator
The generator performs three functions in the EFX. First, by controlling the amount of electrical
load applied to the generator, the user's pedalling resistance is controlled. Second, the generator
is used to charge the EFX's internal battery. Lastly, one of the generators six phase output
windings is monitored to determine when the unit is in use and when it is idle. This system also
determines the stride rate by determining the operating speed (output frequency) of the
monitored generator winding.
Warning
Because this is a self powered unit, it will either be necessary to either equip the unit with the
optional external power supply or have an assistant pedal on the unit while voltage
measurements are being taken. Because of the danger of working on the unit while it is in motion
using the optional external power supply is strongly recommended.
1. Perform the generator resistance test per Procedure 5.1. If any of the resistance
measurements are significantly high or significantly low, replace the generator.
2. The following voltage reading must be taken while the unit is in motion. Extreme care must
be taken to keep meter leads, hands, etc. clear of all moving parts. Using an AC voltmeter,
measure the voltage between 1 & 3, 2 & 3, 5 & 7 and 6 & 7 on J1 of the lower PCA. All AC
voltage readings will vary depending on the unit's stride rate at the time the measurement is
taken. At a stride rate of 100 strides per minute, all three voltage readings will be
approximately 100 VAC -110 VAC.
3. If any of the six readings in step 2 are significantly low, replace the generator.
Repair Parts for Precor EFX 546i Ellipticals SPORTSMITH net
Oct 25, 2013 | Precor EFX 546i Elliptical Version 4
How to wire a photo eye to a Ramset
Ok, so you only want the Ramset to receive power at night?
Or you want to reverse photo-eye operation and only have Ramset receive power in day?
Are you working with household single-phase, or commercial three phase?
If this is at your home, what voltage are you working with 120V or 240?
What size circuit breaker controls power to this unit. Is it a single breaker for 120Volt, or double breaker for 240Volt. Look for power line coming from circuit breaker box.
For household wiring (non 3-phase), the power line from breaker box will have 2 wires, plus a ground.
The additional wires you have are probably for reversing motor, but I can't see the wires.
Copy following link to get started. And then add a comment, or re-post with more details, for example if you have link to the product manual with wiring diagram.
http://waterheatertimer.org/How-to-install-and-troubleshoot-photo-eye.html
Aug 12, 2012 | RAMSET Ram 100 Slide Gate Operator 1/2HP...
Precor efx 546 shuts off when I need to reverse direction during a workout also, the sliding is not smooth (very difficult to push the pedals on an easy level)
Warning
Precor Equipment Repair Parts Treadmill Belts Ramp Sleeves SPORTSMITH...
Sep 05, 2011 | Precor EFX 546i Elliptical Version 4
My Kipor KDE19STA3 shows lower voltage on one of three phases in control pannel and keep shutting down. Voltage is actually OK on all 3 phases, if I measure it with my voltmeter. I need to adjust measuring...
There is no way to adjust voltage on just one phase. I would check voltage sensing leads and check to see if there is a way to calibrate. Otherwise it sounds like a logic problem.
Jul 08, 2011 | Electrical Supplies
Hi I purchase a 3 ton -3 phase condensing unit. Dayton model 1nxd4 for a friend house,after the instalation was finish the unit will not turn on. after installing the unit i found out that the unit was...
Three Phrase is usually only avail at a commercial
business
You would need a complete additional service to the house just for the AC
They would have to install a new transformer on the pole
I would suggest replacing the motor if that is the only issue,
to single phase 240 volt
May 23, 2011 | Heating & Cooling
How can i get single phase power from my 3 phase generator
I have not wire this myself
Wiki says under heading of single-phase:
http://en.wikipedia.org/wiki/Three-phase_electric_power
Single-phase loads may be connected to a three-phase system in two ways. A load may be connected across two of the three phase conductors or a load can be connected from a live phase conductor to the system neutral. Single-phase loads should be distributed evenly between the phases of the three-phase system for efficient use of the supply transformer and supply conductors. Where the line-to-neutral voltage is a standard utilization voltage (for example in a 230 V/400 V system), individual single-phase utility customers or loads may each be connected to a different phase of the supply. Where the line-to-neutral voltage is not a common utilization voltage, for example in a 347/600 V system, single-phase loads must be supplied by individual step-down transformers.
So it sounds like you take 2 legs of the 3-phase.
or
Take one leg of the 3-phase and connect to neutral ... neutral could be a ground rod.
I would put a meter on that circuit before hooking up my power saw.
Nov 17, 2010 | Electrical Supplies
I have 3phase in my shop. I have a new machine that is rated for 208v 3ph. how can I tell what my incoming voltage is?
You will need to take the cover off of the breaker panel. Find the three lugs that the incoming hot wires are hooked to. With three phase you will have three hot lines. Check the voltage between the phases. L1 - L2- L2- L3- and L1 - L3 Also check the voltage from each line to ground. If you havw 120/208 three phase current you will have 208 +or- a few voltage between the phases and 120 or so from each line to ground. If you have 120/240 three phase you will have 240v across the phases and 120 to ground on two legs and 208 to ground on one leg, this is called a "wild" or high leg. You may also have 480v into the shop and you will know that very quickily if you get 480v between phases. No matter if you have another voltage, you can buy a trandformer that can convert whatever you have to 208/120 3 phase for your unit.
Nov 15, 2009 | Jackson 25 in. TempStar HH Free-standing...
Voltage 1phase or 3 phase 240 volts BTUs M# 585epo36o75
Looking at the model number, it appears to be a 3 ton. (36,000 btu) Most all residential units are single phase and most all commercial are 3 phase. One way to tell, look to see if the compressor has a capacitor. 3 phase never use capacitors on the compressors as they are not needed. Some residential units have a "Dual" capacitor. That is, it has 3 terminals, 1 common, 1 for condenser fan motor, and 1 for the compressor. Also, this info should be printed on the unit's lable.
Good Luck and hope this helps.
May 09, 2009 | Amana Comfort Zone 12M32PBEH Air...
Prblem with ASCO ATS
This could be part of the normal behavior of the ATS. Many ATS are set up to allow the switch mechanism to sit in the "neutral" position for a time delay (as much as a minute) so that things like large motors, pumps, etc to wind down so that they don't get powered up at full speed. Here is how I would troubleshoot your ATS:
1) With the Commercial power on and the ATS in Normal, start the generator and make sure that the power at the Emergency terminals of the ATS is the correct voltage and frequency, if this is a 3 phase system also make sure that the phasing matches the commercial power side.
2) Turn the generator off, make sure it's in off not auto. Turn the commercial power off. Then manually operate the ATS transfer mechanism (there is usually a little handle for this), check continuity of the poles of the transfer mechanism to make sure that it's really making and breaking contacts where it's supposed to. While you're doing this you need to check the limit switches at both sides of the transfer mechanism, These switches are how the ATS controller "knows" what state the mechanism is in, they sometimes get out of mechanical adjustment and on rare occasions break and have to be replaced.
3) Once you've satisfied yourself that the transfer mechanism is operating correctly, set it to the Normal position and turn the commercial power on. Switch the generator into Auto so that the system is in it's Automatic mode. Find the manual for the ATS if possible and locate and record all of the adjustable time delays, I often write down the time values we want inside the door of the ATS.
4) With your stopwatch or sweep second hand wristwatch at the ready, start the Test function of the ATS and time out the various operating states as the system goes thru them. In general your ATS should do something like this:
a) You hit the test function, the system simulates a Commercial outage and begins a transfer sequence. On many systems there is an adjustable time that the Commercial power has to remain off for anything to happen, this is Time Delay Start.
b) The ATS closes the contact that tells the generator to start. Then it waits until it sees correct power at the Emergency terminals of the transfer mechanism. When correct Emergency power is available, the ATS controller fires the transfer mechanism to put it into its neutral position. After an adjustable time delay (Time Delay Neutral), the controller fires the mechanism again to put it into Emergency position. Some mechanisms aren't designed to do this "stopping in the middle" feature and so there is only the one action by the controller to get from Commercial to Emergency position, it's also worth noting that on mechanisms that can stay in the neutral position the delay could be 0 so the switch will transition as fast as it can.
c) The system is now suppling the load from the generator. Some ATS require you to interact with the test at this point to get back to the Automatic mode, read the fine manual. In any case there will be a delay from the time the ATS detects correct power at the Normal terminals until it starts the sequence to get back to Auto, this delay is called Time Delay Emergency to Normal. You want this time to be just long enough to keep from making false transfers, but not so long that you waste fuel, most places are something like 15 - 30 minutes.
d) If there was a delay in the neutral position going to Emergency, there ought to be one coming back to Normal. Keep in mind that this delay isn't about the source of power, it's about the load.
e) Once the switch is in the Normal position, the ATS should keep the generator running for a time (Time Delay Cooldown), to allow the prime mover (engine) to return to a safe to shut down condition. On small air cooled engines this can be 0, on very large diesel engines it can be as much as 30 minutes.
f) The system is back in Automatic mode waiting for a power fail.
5) If the ATS can perform a transfer test as above correctly, it should be able to operate just the same way during a real outage. One can and should be able to demonstrate this by operating a disconnect (switch, breaker, etc) at the Commercial power side of the ATS.
If your ATS doesn't pass the transfer test as above, look for (in order of probability)
Incorrect power from the generator.
Broken or missadjusted limit switches in the transfer mechanism.
A mechanically broken transfer mechanism.
A bad controller in the ATS.
Regards,
Carl
Apr 07, 2009 | Winco 200-Amp Automatic Transfer Switch -...
Heating & Cooling Logo
94 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen