I have an older trane twe030c140b0air handler and it was workingq fine then today froze. Fan in unit will not run. Sparks from conteoller. Is that the correct name? Unit is 208 thanks
  • Heating & Co... Master
  • 1,803 Answers
Turn power off to air handler. Jump red and green inside the machine. Turn power on. If fan runs then the problem is likely outside of the machine, that being tstat or tstat wire.
Posted on May 18, 2017
How do I fix my Trane air handler to keep it from turning off about 20 seconds after being commanded to turn on?
Some units require both a start and a run capacitor. It's possible the wrong capacitor was replaced. It's also possible to add a run capacitor to a system to keep the fan running. There is an outside chance the bearings in the fan motor are worn to the point it's time to replace the motor.
Mar 29, 2015 | Heating & Cooling
Had 16 xi Trane heat pump installed 3 years ago. It ran well for the first couple of years. It began to stop heating and would blow cold air only. Have tried both aux heat and reg. heat to run and neither...
That's a complicated system that needs a qualified technician to service it. Lots of people can install them and they run fine, for a few years. Your indoor unit, operating on 2 heat elements, will feel like its blowing cold air even though its heating, just not so well. And not like you are accustomed to. Each element (5kw)=22.7amps, on average. So 3 elements operating should trip a breaker. Its probably been operating on 2 heat element plus the heat pump. And now you have trouble with the heat pump. If you can't TRUST the guys working on your equipment, try someone else. A second opinion. Normally a 3 or 4 ton unit will have 15kw heat installed, heatpump or not. 5 ton, 20kw. If yours is a 3-4ton, cooling, the 100amp(or normally two 60 amp) breaker should have been installed upon equipment change out. If yours is blowing cold all the time, something is wrong with your heatpump. The electric heat inside operates only when the heatpump can't keep up(real cold outside), the heatpump is in defrost(then it's actually in cooling mode), or if you have the tstat in aux/em. heat. Try a local trane dealer? Of a technician with 15-20 yrs under their belt. A trane dealer should have trane tech support also. BIG HELP!!!
Mar 01, 2017 | Haier Energy Star ESA3183 Air Conditioner
Trane Air Conditioner air handler drips water
are you still having issues with your twg030a140b1? the heatpump that you own should not be having this issue the question is the configuration of the coil in the AHU is it properly installed. I am a distributor for Trane equipment and am wondering if the install tech installed correctly
May 30, 2010 | DeLonghi Trane 5t Rooftop Air Conditioner...
Upgrade Baystat 239 to a Honeywell RTH7600D controller
For Trane sytems, B is your "Common" wire. O is your reversing valve relay, G is your fan, Y is your compressor contactor, R is Hot, Brown will not be used on your electronic tstat. X2 is your backup electric heaters. Without knowing what terminals are on your new tstat, I cannot offer more information than this. The installation manual may indicate what each terminal is controlling. I strongly suggest to write down ALL of the terminals and colors from your old t-stat and be sure to turn off the power to your air handler. Put the fan switch on your tstat to ON before turning off the power. Make sure the fan is running. Then turn the power off to your Air Handler. If your fan stops running, you have turned the power off to your tstat and are ready to start replacing it with your new tstat. I hope you find this helpful. Good Luck!!!
Feb 06, 2010 | Heating & Cooling
Why does my fan runs continus. and the condenser won't run out side.
The fan runs continously because your condensor is not kicking on and removing the heat. The thermostat needs to come under the set temp. to kick off the fan. If your compressor doesn't run and the fan on the outside unit does run, your compressor has an issue. If nothing runs outside, then your transformer on the inside unit(air handler) has an issue. This could also be a control relay on the condenser or the air handler.
Jan 15, 2010 | Omega Trane Furnace Draft Inducer Blower...
Trane AC Compressor fan cycling on and off.
it depends on the tempareture you have set that is why it was going on and off
Sep 09, 2009 | Heating & Cooling
Trane XT300 thermostat reads HOLD-AC. Unit will
by simply turning power off to furnace or air handler may not work but there might be a reset button in the t-stat. remove the faceplate off of the t-stat it might be in their.
Aug 16, 2009 | Heating & Cooling
Trane Air Handler and Trane Thermostat with no power. Please help
First of all put back the jumper wire you remved Rc to Rh and also put the red wire to either one then the white to W, the green to G and the yellow to Y .That is for the thermostat wiring for a not heat pump outdoor unit.Remember this electronic thermostat has a time delay so the unit will take a few minutes to start.All this if the problem is the thermostat.But also when nothing works it could be that the drain line is clogh and some air handlers have a flood switch who shut the unit off if drain is clogh(it could be located in the drain line out of the air handler or inside it on the drain pan.) newer TRANE units have it inside.
Aug 13, 2009 | Heating & Cooling
Trane air handler cycling rapidly
Depending on the age of your Trane unit. The fan relay has a time delay. This is a solid state board on the relay. Most of the time they stick on or off. Check for loose wires. But start with relay.
Jun 03, 2009 | Heating & Cooling
Trane air handler model #TWV036B140A Fan wont stop
Sounds like you have a bad fan relay, the fan should shut of within 30 to 120 seconds after t-stat is satsified.