Question about Goodman CKL24AR24 Air Conditioner
My unit keeps blowning fuses checks fan motor, compressor,and switch and no vail
Line fuse keeps blowing
Posted on Jul 25, 2009
Why is one 30 AMP fuse pair blowing on Carrier Tech 2000 SS AC Unit?
Pull off one of the wires to the fan. If it still blows a fuse the compressor is shorted. If not replace the fan motor.
Jul 03, 2014 | Carrier Heating & Cooling
Fuse keeps blowing on a/c on 2001 dodge truck
Let's break this down.
1 Does the fuse blow when the heater is on, or just the AC?
Yes- Fan motor problem likely need new blower motor.
No- 2
2 Disconnect the AC compressor clutch wire. Remove the blown AC fuse, connect a multimeter across the sockets for the fuse, measure DC voltage across the two sockets with the AC switch, and Ignition switch ON. Is Battery voltage present?
Yes- The wiring harness has a short between the output of the AC switch and ground, likely a pinched harness.
No- The AC compressor clutch is shorted. Replace either the whole compressor or the clutch.
Apr 01, 2014 | Dodge Ram 1500 Cars & Trucks
Hi,I have a travel trailer 37ft. Problem with my ac, the fan starts good but my compressor does not kick on. My next door neighbour says it's the compressor that is done. Could you help me?
see this causes and fix it. God bless you
Motor Trouble Cause Diagnostic Procedure Repair Procedure Electrical Power is Off Check that all service switches for the equipment are in the "on" position.
Check for voltage at the pump motor or pump controls. If no voltage is found, check for voltage at the electric panel.
If power is on to the building, check fuse or circuit breaker serving the electric motor that won't run.
Check for local reset button on the motor (popped out = off )
Check for other power reset or power off buttons such as an access door compartment safety switch that turns off power to the equipment (found on A/C blower compartment doors)
Turn on "off" switches.
Replace bad fuse. Reset circuit breaker; if necessary replace bad circuit breaker.
Let hot electric motor cool down, then push in its reset button.
Be sure all safety interlock switches such as on compartment doors are depressed and that the doors are securely shut. Replace a bad safety switch.
See
ELECTRICAL POWER SWITCH FOR HEAT
FAN AUTO ON Thermostat Switch
WATER PUMP ELECTRICAL SWITCHES
CIRCUIT BREAKER FAILURE
ELECTRIC PANEL INSPECTION
Blown fuse, tripped breaker Replace fuse or breaker - does the pump run and keep running normally? Be sure proper breaker or fuse size in ampacity is installed - ELECTRIC PANEL INSPECTION Low voltage to the motor Check with VOM at the pressure control switch or at the motor wiring Be sure the proper size of wire is used for the ampacity and length of circuit; Test for low voltage to the building. Loose, improper, or broken motor wire Check wiring against the motor installation manual diagram, check all connections for tightness, shorts, burns, damage Rewire or repair or replace wWhen a sealed compressor motor has "burned out" this means that the internal wiring of the motor has become irreparably damaged: the compressor motor windings may be burned and shorted together or shorted to the steel shell of the motor, or the windings may have burned and simply become "open" or disconnected. If the motor has burned out in either of these ways it needs to be replaced.
Oct 08, 2012 | Dometic Rooftop RV Air Conditioner
My 2000 Maxima GLE blower has stopped working. The a/c compressor comes on & runs but no air. I have run the temp switch above 80 to see if heater comes on but nothing. I do not find a fuse...
Check fuses 52 15A and 51 15A in the underhood fuse box. Check the Blower motor relay behind the right side of dash. Check the fan control amplifier (controls fan speed) behind right side of dash. Sound more like a blown fuse or bad blower motor relay
Jan 12, 2018 | 2000 Nissan Maxima
I have a whirlpool central air conditioning and the condenser stoped working. what could I expect it to be?
When you say the 'condenser' stopped running - I'm 'assuming' you are talking about the outside unit, and I'm also 'assuming' that when you say it stopped running you mean 'nothing' runs on the outside unit - fan motor OR compressor. The fan motor will drown out the compressor running noise which is a 'low rumbling' sound - often not heard by the layman because of the noise the fan motor puts out.
Assuming you are talking about the outside unit and 'nothing' is running either fan motor or compressor then you might be 'in luck.' Because the most likely reason for the outside unit to be totally off will be a 'blown fuse' or a 'tripped breaker.' The good news is that in 'hot weather,' especially the kind of hot weather that has been present this summer (especially in the south) - blowing a fuse or tripping a breaker is not necessarily an expensive repair.
Indeed, it's not uncommon for a AC unit to blow a fuse (or trip a breaker) on occasion, although it must be noted that doing so is also is sign on something seriously wrong with your AC, i.e. a fan motor breaking down electrically or even a Compressor, both being expensive items to replace.
But, as I said, it's not uncommon for a fuse to blow once in awhile.
I would check my fuses (and breaker) and see if this is what has happened.
If you have fuses (usually located outside close to the condenser) and have no way to check them (you check them with a ohm meter looking for continuity) - then just 'replace' them with new ones. Note: always put 'time delay/dual element' fuses back in - even if the ones that are in there now are 'one time' fuses. 'Time delay' fuses do just what they say they will do - (they hold for just a second or two during that initial start up (of the compressor) without blowing).
If a blown fuse/tripped breaker is your problem then "most" of the time the AC will run ok and you will not have any more problems.
However, if after replacing the fuses and turning the AC back on - the fuse(s) blows instantly, or a short period thereafter (say a few minutes or an hour) then you probably have a problem that is causing it - i.e. the fan motor or compressor is going bad.
Note: one thing that you can fix that might be causing the fuse to blow is a dirty condenser. So, check the condenser coil (think of it like a car's radiator). It 'must' be clean to run properly and when it gets 'really dirty and clogged with dirt it will cause high head pressure and can cause the unit to blow fuses and trip breakers.
Good Luck!
Aug 10, 2011 | Whirlpool Heating & Cooling
Goodman cpl-j42-1a outside unit fan will not run i do get some cool (not cold) air out of vents inside house
The fan motor on the condenser not working can be a easy fix or the motor itself could be bad. One important thing is, if your condenser fan isn't coming on, but the compressor inside is running, you could cause a lot more damage and may have to replace the compressor also, which could get expensive! I will try to go through a few things to see if any fit your problem.
(WARNING) Before working on any part of the electrical system, or even opening the compartment, please disconnect all power to the unit!
1. Fan motor not running, but compressor IS coming on-
Bad Capacitor- Its a small round or oval part that is inside the electrical compartment on the outside condensing unit. You will have to have a multimeter that reads MFDs to check it. If you do have a meter, take off the connections that or on the Herm terminal, (if you have a capacitor with just two terminals, make sure you disconnect one side), set your meter to Mfds and touch your leads to both terminals. Remember the reading it gives you and compare it to the Mfd rating on the side of the capacitor. It should read something like 15mfds/5% 370v, they vary in sizes, but make sure that your capacitor is running close to what it's rated at, if not, then it needs to be replaced. This is a common reason the fan motor stops working when everything else is still working.
Bad Motor- This can be a little more complicated sometimes since a motor can go bad and not show normal indications. The first way you want to check is to try and turn the blades on the fan motor. It should turn freely with no problem, if it doesn't, it needs to be replaced. You can also check for continuity in the motor with a multimeter, but as I said before, sometimes it can show that its okay, but still have a problem. Sometimes when your fan motor burns up, it makes a loud humming sound when it tries to kick on.
2. Fan motor not coming on, compressor also NOT coming on-
Fuses on disconnect switch- There will be two fuses on most disconnect switches that are inside the disconnect on the outside of the house, usually right by the unit. (Some condensers do not have a disconnect at all, see BREAKER BOX) To check the fuses, you will need a multimeter that has a ohm setting, they should have continuity through them. Some fuses have a small window that you can see if they are blown or not. If so, replace fuses with the same size that was pulled out.
Breaker Box- Simply enough, sometimes your condenser will trip the breaker in the breaker box. Make sure all your breakers are switch to the on position. Sometimes this is all it takes and other times it can mean that there is a more serious problem. (If you reset the breaker and it automatically trips again, there is a short and needs to be left off)
Compressors internal overload switch- If the compressor is running when the fan motor is not, it will eventually over heat which will trip the internal overload switch and shut the compressor off until it cools back down. The best way to check this is to feel the compressor itself and see if its extremely hot. ( An over-heated compressor can cause burns!) The other way to check it would be with a multimeter with a ohm setting to check for continuity within the compressor. You must follow the wires from the compressor to find the terminals where they are connected. Take the connections off and place your leads on the wires, you should have continuity through all three wires.
Of course there are a few more technical things you can use to trouble-shoot, but these are some of the more common problems and answers. Things like the capacitor and fan motor can be pick up by yourself from a local supply store that carries A/C supplies. The compressor has to be bought from a licensed contractor. The capacitor is basic, but the fan motor will need a fan blade puller in order to replace. Hope this helps or at least points you in the right direction. Good Luck!
Jun 18, 2010 | Goodman CKL42AR42 Air Conditioner
When i turn the a/c on the inside furnace motor runs but the outside compressor units does not. the compressor is a janitrol, about 20 years old
Does the outdoor fan run? If not then start by checking for tripped circuit breakers or blown fuses. If you have power then check the capacitor. If that is good then check your contactor for the fan and compressor. If that is good then check the compressor motor windings. Let me know if you have any questions.
Jun 14, 2010 | Weather King 10AJA3001AH Air Conditioner
THE MONITOR OF INDOOR UNIT DISPLY ALL THE
This could be caused by a blown circuit breaker or fuse inside the unit, a damaged compressor or fan motor, faulty wires connecting the compressor or fans to the control board unit, a faulty or hung relay on the control board (this can sometimes be solved by tapping the relay with a screwdriver), or the starter capacitor for the compressor or fan motor.
Sep 17, 2009 | Samsung AQ24 Air Conditioner
Coleman rooftop a/c hums in all modes, does not start
Replace the start capacitor for the fan and compressor. Check all the wires to the capacitor.
Aug 29, 2009 | Dometic Rooftop RV Air Conditioner
I have an older Goodman CKB 18-1
FOR QUESTION 1: They do run independantly. What will happen when your compressor is running but your outdoor fan does not, the pressures in the system will go really high and compressor will overload. That outdoor fan is used to disipate all the heat that is transferred from the inside to the outdoor unit.
FOR QUESTION 2: If you hear humming it can be 2 things. FIrst one is that that capacitor went bad. Dependiing if its a dual run capacitor(which helps both compressor and fan motor) or they both have individual capacitors. The second would be a bad fan motor. OPen your service panel outside to the AC. Find your capacitor for you fan motor. if there are 2 , locate the one that goes to your fan motor. Check it out(if its blown physically youll will notice it like really bubbled, like swollen) then change itout. Or you will have a dual run capacitor that runs both compressor and fan motor. It will have the terminals marked (Fan, Common, Herm) Bsically check your capacitor mfd(micro fared rating, it will say on the capacitor what its rated) Get a multi meter and put in the "MFD' selection. Before you check any capacitor you have to discharge the the voltage charge it has. Use an insulated handle screwdriver and just place the metel part across the capacitor leads. Basicall short them out. Then proceed with checks...hope this helps( remember to always pull the disconnect out from the box outside to cut power)
Jul 30, 2009 | Goodman CLJ30AR32 Air Conditioner
Goodman CKL24AR24 Air Conditioner Logo
130 people viewed this question
Top Goodman Heating & Cooling Experts
Paul Carew
Tim Whalen
christian nielsen