How to ogernal 2 ton split copper outdoor with highly compressor capillary size plz answer
  • 5,392 Answers
Maybe you should use spell check to get an answer for your question. it isnt clear.
Posted on May 10, 2017
chillmaster
  • 104 Answers
SOURCE: oil trap for 2 ton split unit
Pipe size is okay, not that I know any better than the manufacturer, but I would recommend at least two and possibly even three oil traps in the vapor line on the way back up.
Posted on Jun 15, 2008
Speed boy
  • 76 Answers
SOURCE: York Mini-Split Not Cooling? : (
This can only be a gas problem.
the split units goes on on and off if a shortage of gas is involved, the chances that you would here it wont be that big for the fans would make too much noise.
get a repair man for a re gas and all is well.
Good luck.
Wouter.
Posted on Oct 22, 2008
sodeep
  • 3267 Answers
SOURCE: LG DUCTABLE SPLIT TYPE A/C PROBLEM
what you have left out is the thermostat and they relays(electrical) which are activated by the thermostat. Another point is the door closing button near the bottom right side mounted on the body of the fridge. Check it out too.................................sodeep
Posted on Jul 26, 2009
  • 233 Answers
SOURCE: 13 degree Delta T
I assume r-22 refrigerant by the pressure... you have a saturate temperature of approximately 41 degree and 71 degrees at the service port this equates to a 30 degree superheat. a condenser saturation temperature of 105 degrees and since the liquid line temp at the service valve is not given only the enterin indoor coil on the liquid line a 96 degree temperature this would equate to a subcooling temperatureof about nine degrees. You have too high of a superheat reading. verify that the bulb for the txv is correctly positioned and insulated. if it is then you need to remove the bulb from the suction line, hold it in your hand to warm it up and see if the superheat changes. you could also have issues with your ductwork. If the supply temperture is around 50-55 degrees then the unit is doing all it can.. Check the txv and the ductwork as the subcooling indicates that the condenser side is doing it's job, but the superheat readings indicate that you are starving the evaporator..
Posted on Jul 28, 2009
greenspan
  • 1734 Answers
SOURCE: LG split (3 indoor) LMU360CE
The LED #2 is only flashing while in disconnection or short in Thermistor (3 sec off / 0.5 sec on). If you want to change it, note: this is not an easy job to do! You will need to remove the top panel, then remove the control paneland then the front panel to gain access to the thermistor. The part isnot available to the public and requires an authorized service techfrom LG to take care of this problem. You will need a special tool toremove the front door seal spring clamp.
But you can call customer service @ 800 243 000 and see if theycan transfer you over to parts. Just give them the model and serial #and see if they would be willing to sell you the thermistor part. Youwill also need the door seal spring clamp removal tool to make the jobeasier.
Posted on Aug 02, 2009
1.ton ac capillary pipe size and length I want to know. B coz suction line cooling level is very low gass psi 75
I'm guessing you should have 3/8 & 5/8 copper on that unit with a maximum of 50 feet. I doubt the line set size is affecting your pressures that significantly, you likely have a leak.
May 05, 2017 | Heating & Cooling
What is the size of the gas line piping on the out door unit of a elite elegance split unit
You need size of pipe , length of run , input of btu.s you need all this before you can size pipe
Jan 18, 2017 | Heating & Cooling
How do i fix AC Dolcool split type, Model KF61G, compressor not working. Breaker keep tripping.
It sounds like compressor is shorted,check ohms from compressor terminals to copper,clean area on copper.if it reads ohms,short,if not I would start by disconnecting outdoor MTR,indoor MTR,& see if still tripping
May 07, 2015 | Refrigerators
I have a split system air conditioner that quit blowing cold air
either the compressor is not running or you have a leak and are low on freon. the outside fan running does not tell you the compressor is running.
Jun 18, 2014 | Coleman Outdoor Split System Air...
I have a tempstar 2000 heat pump approx. 6yrs.We have the compressor go bad 3 different times and replaced by the original installer.Now Action Air of Florida says they don,t know why so many compressors...
no compressors don't just go bad first of all is unit a split system or a package unit.if its a split system need to make sure copper from evap.coil to outdoor unit sized properly.next need to make sure your ductwork is sized properly undersized ductwork makes comp. run much harder.sounds like non-condensibles in system
Mar 22, 2012 | Heating & Cooling
Compressor motors are constantly grounding each time the compressors are replaced. A new run capacitor is installed with compressor. A thorough cleanup and evacuation is performed with each compressor...
dear sir
please make sure your electrical connection to the compressor is correct and tighten. electricity supply is straight and not fluctuate i mean constant supply for unit and then change new run capacitor and make sure ground wire must connect to the air conditioner,s body and check copper filter and any other copper pipe is not block .
i think it cab be an electrical problem so check all electrical device and then re-install new compressor.
thank you
hope answer the question
please vote!
Oct 02, 2010 | LG LS180HE Split System Air Conditioner
Problem with compressor
Normaly on this units the problem is the PC boards if i'm not mistaken they have censors this censors give problems sending the unit to a Protection mode when the units works too hard sounds like thats your problem room 2 big and the High preasure presostat it's telling the unit to stop.
May 27, 2010 | LG LS-L1210CL Mini Split Air Conditioner
My 1.5 ton,LG split AC shuts off rather
Hello
First the foam insulation is not just for looks,you will have some loss of cooling on the unit,the larger cooper line needs to be insulated,the small one does not.The large line is the suction line,the small one the liquid line.
Voltage,168 is low,sounds like a 208 volt unit or 220 volt.running at 168 or 198 ac volts is going to raise the amperage causing the compressor to run hot and work harder and soon burn up,And cause it to trip the breaker or shut itsself down on high heat.Your going to need to get that voltage fixed.I dont know why it needs a stabilizer if the unit was sized correctly it shouldnt need one.
Hope this helps.
Apr 14, 2010 | LG LS-K2430HL Heat Cool Mini Split Air...
13 degree Delta T
Jul 28, 2009 | Heating & Cooling
2 ton sanyo suction pressure erratic
Your suction pressure is erratic, your max. pressure is to much high. You did not measure your unit current reading liquid line press. to complete the data. But the problem of your unit is not the compressor its the system. Try to reprocess the system flush the unit with nitrogen, isolate the capillary tube and flush it with nitrogen to insure that no restriction.
Jan 04, 2008 | Sanyo 24KS62R Cool Mini Split Air...
Heating & Cooling Logo
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen