Question about Coleman Mach III Air Conditioner
How many amps do these unit draw - Coleman Mach III Air Conditioner
  • 2,359 Answers
There are TWO different models of Mach III.
A/C cooling only model
  • Amps Cooling 14.9
A/C cooling WITH HEATING
  • Amps Cooling 14.9
  • Amps Heating 16
Just check the control panel and see does it has the heating option.
If you're not sure then please ADD the exact model of THIS comment page.
I will follow up on it later.
Posted on Jul 23, 2009
How many fet tranistors are in this unit and what is its max amp draw.?
There are 5 transistors in that unit that you are asking about. The amperage draw is about 50 amps
May 23, 2013 | Palomar Redman Cb Stop LD 450-fet LD Low...
WHAT IS THE MAX AMP DRAW?
Max amp draw refers to the total amp draw of a unit , example : Compressor RLA 25 Amp, blower motor FLA 5 Amp, and condenser fan motor FLA is 1.5 amp , you add all three and get 31.5 Amps
which is your max amps, this is used in determining wire gauge and breaker size for unit.
This should help.
Jul 27, 2011 | Heating & Cooling
What is L.R.A. for a samsung SK1A1C-L2W ?
A rule of thumb for lock rotor amps is 5 times the running load amps. That unit probably draws 3-4 amps max when running so lock rotor probably 15- 20. If its drawing lock rotor amps try a hard start, if that wont do it unit is bad
Jun 22, 2011 | Refrigerators
Dead, has power going into wiring, but wont do anything no lights or nothing could it be the thermal fuse?
It is almost definitely the thermal fuse. However, you also need to determine why it blew the thermal fuse. This fuse is in place to protect the Control Unit from overheating cause by to high of an amp draw from the motor, the heating element, or a dead short in one of the solenoids.
Replace the thermal fuse, which is located on the Control Unit, behind the Control Panel. After replacing the thermal fuse, start the dishwasher and using an amp meter, test the amp draw of the unit at the supply connection.
During the water fill, you should only see 0.1 to 0.2 amps at the most, and possibly could show 0.0 amps. Once the wash motor turns on, you should see somewhere between 1.2 and 1.8 amps. If the amp draw goes over 2.0 and stays there, you have a bad wash motor.
The best way to check the amp draw of the heater is to put the unit into a field diagnostic mode. To do this, cancel the cycle and wait for the unit to shut down (standby mode). In this order, press "HI TEMP WASH - AIR DRY - HI TEMP WASH - AIR DRY". Air Dry could also be labeled No Heat Dry or something similar. All of the LEDs will light up momentarily and the heat element will be turned on briefly. The amp draw of the heat element can read from 5.5 amps to 7.0 amps. If the amp draw of the heat element goes above 7.5, chances are that your heat element is bad and needs to be replaced.
Apr 17, 2011 | Dishwashers
What size breaker and wire do i need to the disconnet box 30 amp 240 volt
30 amp requires #10 wire. Your disconnect should be 1.25 times the rated amps of the unit. Typically if the unit draws 22 amps in the literature they will rate it for 30 amps (22 x 1.25). Put a 30 amp disconnect on it. But check the rating plate first for amp draw!
Feb 18, 2011 | Ruud UBHC Air Conditioner
My church has a roof top ac unit, model # GP-1360H41BA. The ratings plate has the following ratings: RLA 26.4 AND LRA 134. What is the KW draw of this unit 1. At startup 2. After startup?
RLA ( rate load amps/current) is the rate of unit ( usually about 65% against Max. load current < FLA/FLC>)
LRA ( Locked rotor amp/current)
Seems your AC use Y or Delta starter, so at start the current draws will between : 3X ( 26.4 to (26.4(1 +35%). And After start up the current draws will drop to 26.4 to 26.4(1+ 35%) in normal operation.
Remember, that the current draws also depending to the condition of your ac.
Nov 03, 2010 | Goodman Heating & Cooling
Duo therm brisk air ,does not blow cold air fan works but when condenser trys to turn on it draws 76 amps please help
You don't say what size unit you have. Does it draw 76 amps and then go to about 10 or 12 and you can hear the compressor running or does it draw 76 amps and the breaker trips. I suspect it draws 76 amps until the breaker trips. Confirm that the capacitor is niether shorted nor open. It may be worth your time to replace the capacitor, if you have one of the correct size available. If this does not get your unit running, it sounds like you are drawing Locked Rotor Amps, which means your compressor has physically siezed. There are a couple other posibilities, but looks like its time for a professional.
Jul 20, 2010 | Heating & Cooling
What is the amp draw on a Liebert A/C Unit (FH245AUA00 - 480V 3 Phase) ?
amp draw will be 6.9 amps per leg cutout switch will be rated for 30 amp locked rotor per leg fan runs 5 amp draw continuous here is the web page it's pdf format. Liberty A/C Unit (FH245AUA00 - 480V 3 Phase http://www.rvii.com/bspdf/20x20x38.pdf.
Mar 17, 2010 | Heating & Cooling
Drawing current but not producing any heat.
I am assuming this is an electric wall mount heater, if the unit is drawing current then it should relate to heat as 3.41 btu is = 1 watt.
take the voltage reading and the amp draw and mutiply them to determine the wattage eg; 240 volts x 20.8 amps = 5000 watts = 17,050 btu. if the unit is fan assited and you are drawing 1 to 2 amps this would indicate the fan is runnning without the heat element being energized hope this helps
Nov 04, 2009 | Fahrenheat (FFH1614) Wall Mounted Panel...
Model 6994f230600325 watts required to run and to start up? Have an 8kw generator. Is that enough to start up and run one of these units. 30 amps?
To find the wattage of the unit running, multiply the voltage (220?) by the amp draw (marked on unit) The problem I am seeing is the initial amp draw is prob. going to be close to 60 amps, and I am not sure if your generator is capable of this. Hope this helps
Aug 19, 2009 | Heating & Cooling
Coleman Mach III Air Conditioner Logo
380 people viewed this question
Top Coleman Heating & Cooling Experts
Bill Long
Paul Carew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others