On Panasonic CU ABCKP 5 external fan runs continuously when inside unit off. As electrician, have disconnected actives on external/internal units, fault remains. Any assistance gratefully received.
System started to show this fault recently, not apparent before Sorry, this posted in wrong category, it is an air conditioner !
  • David Williams
    David Williams Jan 02, 2017
    Units have terminal strip 1-4. On each 1 is Red, 2 Black from 3 core and 3 is Red, 4 is Black from 2 core. My assumption that reds were active was incorrect. 4 on external was 240V hence fan running. Wiring diag needed please.
kstfas
  • 75 Answers
SOURCE: Friedrich air conditioning - inside unit ice build up
Hi, Reduced air flow, low on freon or being continuously run during cooler weather such as at night. Some people turn their thermostat on 60 thinking that it will help get it cooler faster. They freeze up at night and don't get a chance to thaw during the day. It needs set no lower than 75 or so. The evaporator may be dirty. Don't know a lot about your particular unit but if the outside unit has the compressor and refrigerant lines running to it, The large refrigerant line should sweat all the way to the compressor if its fully charged. Please rate me if I have helped. Good luck kstfas
Posted on Aug 28, 2007
bobotfel
  • 236 Answers
SOURCE: air conditioner
Turn off unit supply and check the blower wheel inside the indoor unit by rotating it manually by your finger if the blower wheel rotates freely then there is something wrong with your fan motor or fan motor capacitor. But if the blower wheel is not rotating freely try to check the fan motor for lubrication or some bushing dried of and no oil
Posted on Dec 31, 2007
  • 59 Answers
SOURCE: Outside Unit Air Conditioner fan not running
probably a bad fan motor. could be a capacitor
Posted on Apr 25, 2009
  • 534 Answers
SOURCE: Panasonic CS/CU-A242KR Air conditioner leaking water
OK lets see what we can help you with here. The condensate drain is clogged. There are a couple of ways to clear this clog so lets give it a try. If you know where the drain for the a/c is located outside (usually by the outside condenser unit) it will be a pipe that is just sticking out of the side of the house, if you find it take a wet/dry vac and place it on this pipe and turn the vacuum on and make a seal with your hand this should unclog the drain. If you don't find this pipe outside the house then go to the furnace and you will see at the bottom of the furnace a pipe (PVC) white, this is the drain for the unit inside. Take the wet/dry vac and have it at the ready in the event the clog is further down the line than at the furnace itself now the fittings on this pipe should not be glued together due to the ability to access for this very purpose. Take the pipe apart at one of the fittings and place the wet/dry vac on the end of the pipe towards the furnace and using your hand make a seal and evacuate the line. Do this to both sides since you don't know where the blockage is. If you are unable to separate the pipe at any fitting you will need to cut the pipe and at the spot of the cut you will need to repair it with a sleeve. Remember that the drain pipe is plastic and is made of pvc so you can get a repair coupling from any home improvement store for this repair.
Hope this helped you some
Dave
Posted on Feb 21, 2010
hvac1960
  • 2133 Answers
SOURCE: LG air conditioner 24awn error code message Ch 6
CH-06 REFERS Indoor unit coil sensor fault. Disconnect from PCB measure resistance. 10 kOhm at 10C and 4 kOhm at 30C. if not replace sensor. THANKS.
Posted on Dec 13, 2010
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
2002 4 ton Bryant air conditioner shuts off, fan still runs but not cooling is problem in the controls in the attic or in the AC unit or both?
With a non heat pump it is a simple 24 volt AC control circuit. In the attic there is a relay that is actuated via the fan control wire directly from the thermostat. On the thermostat there is an auto/man switch that controls the fan. Manual the fan runs all the time. Auto fan turns on and off with the outside compressor.
If the system is not calling for cool and the fan continues to run the fan relay is sticking. common problem. Sometimes after running for several days the relay will stop sticking if not, replace relay.
If the system is calling for cool and the compressor stops I would still expect the fan to run until thermostat tells the A/C to off. Some compressor units include a safety switch or high-pressure cut-out switch A blocked internal valve bad control board or external fan in outside unit defective no air flow in outside unit.
High pressure cut out not good,
Suggest turning temp max cool and observe. If acceptable cool and the compressor runs without interruption all is good, except for the blower in the attic. Safely check relay in attic blower circuit.
Hope this helps.
Jun 28, 2017 | Bryant Heating & Cooling
My Panasonic split air conditioner has stopped cooling - model:CU-W18DKR. The internal unit and internal fan operate normally. The external unit fan does not run like normal and no compressor sounds f
Sounds like a faulty outdoor controller board. If you are in Australia, call Prime Electronics or Statewide Appliances for spares.
Part number: NPCWA743383
• To make a diagnosis
1. Timer LED start to blink and the unit automatically stops the operation.
2. Press the CHECK button on the remote controller continuously for 5 seconds.
3. "- -" will be displayed on the remote controller display.
Note: Display only for "- -". (No transmitting signal, no
receiving sound and no Power LED blinking.)
4. Press the "TIMER" or button on the remote controller. The code "H00" (no abnormality) will be displayed and signal will be transmitted to the main unit.
5. Every press of the button (up or down) will increase abnormality numbers and transmit abnormality code signal to the main unit.
6. When the latest abnormality code on the main unit and code transmitted from the remote controller are matched, power LED will light up for 30 seconds and a beep sound (continuously for 4 seconds) will be heard. If no codes are matched, power LED will light up for 0.5 seconds and no sound will be heard.
7. The breakdown diagnosis mode will be canceled by pressing the CHECK button continuously for 5 seconds or without any operation the remote control for 30 seconds.
8. The LED will be off if the unit is turned off or the RESET button on the main unit is pressed.
Or better yet, get a tech to check first.
Feb 10, 2015 | Panasonic Single Split System - Wall...
No heat but fan keeps running
If the air conditioner compressor runs all the time the main control board might be defective. The main control board provides the voltage to the fan motor and compressor. These boards are often misdiagnosed. Check all other components to be certain this is the cause of the problem.
Nov 25, 2013 | LG LAN186HV / LAU186HV 18,000 BTU 15 SEER...
My ac unit outside runs when the tempeture gets above what it is set on, but the fan blower keeps going on and off. I switched the theromstat fan to on from auto and it does the same thing, on and off in...
the fan control is not for the fan on the top of your outdoor unit. that is for the blower, you have 2 fans. Im guessing you have a split system, 1 unit inside and 1 outside?? Does the outdoor fan continually run??
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
Feb 06, 2018 | Ingram GMS90904CXA Heater
We have a msz-ga80va split cycle, indoor unit runs for about 5 minutes without cooling then cuts out, outside unit doesn't kick in at all
Just had the same thing happen to us with the same model (right on Xmas day).
Checked the circuit breaker is on in the fuse box. Power is on to the external unit. Filters are clean.
Internal unit activates... both indicator lights on. After 5 minutes blowing air it stops and the right indicator light goes out and the left indicator light blinks constantly.
The troubleshooting guide inside the internal unit (under the outer cover you open to clean the filters) suggests that 14 blinks is an abnormality with the external unit and refer to service manual.
Think we'll be calling a technician.
Dec 26, 2010 | Mitsubishi Heating & Cooling
Fan does not turn off even after disconnecting
Are you referring to the fan on the external mechanism, or the internal air handling fan?
The external fan is not controlled by the internal thermostat. it is controlled by the thermos-witch of the compressor. The external fan may or may not run when the motor is operating. it depend totally on the temperature of teh compressor, and not the internal thermostat.
It the internal air handling fan is running continuously,it may be a a problem with the fan setting. check if the fan is set to 'ON' instead of 'AUTO', and correct it.
Incidentally the fan operation I described, is for modern, energy efficient heat systems. This is a energy saving design incorporated in all heating systems including automobile radiator fans.
Jan 31, 2010 | Goodman Heating & Cooling
Panasonic air conditioning model no cu-v9ckp5 inside unit switches on but no fan operation outside unit starts then after approx 1 min whole thing shuts down again
The outside unit has a fan capacitor and it must be faulty!!! thae capacitor tells the fan to rotate and if the fan does not work then the compressor will shut down due to a high head pressure and temperture!! change the capacitor located in the electrical section of the outside unit and it should work fine...
Sep 10, 2009 | Heating & Cooling
Mitshubishi split muh-18nvand inside msh-18nv
-Start the unit.
-Press EMERGENCY OPERATION switch.3-minute time delay works.Test run operation operates for 30 minutes.
-Check voltage to terminal block of outdoor unit.Is there 12V DC between 2-1?
-If voltage is presenet check the wiring, compressor contactor outdoor fan motor and compressor.
-If no voltage check voltage to terminal block of indoor unit.Is there 12V DC between 2-1?
-If if voltage is present re-connect the continuity of indoor and outdoor unit connection.
-If no voltage replace the indoor electronic control P.C.
board.
-But also check the coil thermistor sensor and room air thermistor if this two is out of range it can cause the tripping of out door unit. It has the resistance of 8 to 10 k ohms at 25 deg c temp.