Checked pressure switch because I got 3 flashing lights indicating a pressure switch stuck opened.I blew thru the tube and it worked for a minute and now the igniter glowed for a few seconds & nothing
  • Heating & Co... Master
  • 3,087 Answers
Needs a new pressure switch , you could try cleaning the tube connection with a small drill bit .
Posted on Jan 01, 2017
Coleman Evcon Furnace. Why do I keep getting three flash code?
You might try viewing this YouTube video which shows a way to unstick the pressure switch. https://www.youtube.com/watch?v=Wc_oFIL2aRY
Nov 28, 2015 | Heating & Cooling
Armstrong air furnace
Have you checked the flue inlet and outlet to see if it doesn\'t have a wasp nest or bird nest or rocks. check the hose that is attached to the pressure switch and the port on the collector box or inducer fan motor to see if it is clear. if you take the switch off and lightly suck or blow into the port it that will close the switch. If you have a manometer you can check the pressure differential. On the pressure switch it will say what pressure in will close at ...Example .52" WC. or 1.25"WC You would attach your manometer to the tube attached to the pressure switch and start the combustion blower to read the pressure. If you have over the reading and the switch didn\'t make you will need to replace the switch. if you have less than you have to make sure the flue is open. You can check the flue with a simple trick by unhooking the flue pipe from the combustion blower and then check the pressure and you may have to unhook the air intake also. If that doesn\'t work you could have a plugged secondary heat exchanger...... Good Luck.
Nov 12, 2013 | Heating & Cooling
My furnace stopped working. It'd start up shut down start up shut down all in the matter of seconds. Then would fire up and work. it did this maybe once every couple days then it stopped all together. ...
Replace pressure switch. If you blow any air into the pressure switch it has been damaged,check air ports for debris by looking never ,never blow on air switch they work on a very small pressure or vaccum,where your breath is to much pressure and also loaded with unwanted humidity.
boilerman56
Mar 04, 2011 | Goodman GMS90703BXA Heater
My ducane furnace gives 3 flashes which indicates pressure switch problems, low line voltage, clogged flue, but I have replace the switch, checked the flue and voltage... all are ok... what else could it...
Hello, check the small tubing that goes from the pressure switch to the inducer motor, sometimes water can drain back into it preventing the pressure switch from closing also make sure the tubing is clear of any restrictions.
Feb 01, 2011 | Heating & Cooling
Hi, the lights on my circiut board are flashing the one on the left is on all the time and the one to the right of it flashes two times and then waits and then flashes two times again
Error Codes
A green LED indicates system faults
Steady On: System OK
Steady OFF: Board control fault or no power applied
1 Flash: Ignition failure (control in one-hour lockout)
2 Flashes: Pressure switch fault, fails open (switch is
stuck open)
3 Flashes: Limit switch open (main or auxiliary)
4 Flashes: Pressure switch fault, fails closed (switch is
stuck closed)
A yellow LED indicates flame status
Steady on: Normal flame is sensed
Flashes: As flame weakens, frequency of LED flashes
increases
hope this is helpful.
Dec 21, 2010 | Ruud Central System Air Conditioner
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
Armstrong upflow,unit works intermittent problem,call for heat nothing happens,error code of 5 blinks then 6 blinks. i have no manuel, and the panels dont have the codes on them. anyone have access to the...
Armstrong
FAILURE CODES
LED Status Fault Description
Off
No Power to the System Control
Steady Flash (11 or more flashes with no pause)
Normal Operation (Standby or call for heat)
2 Flashes
Pressure Switch Closed When It Should Be Open
3 Flashes
Pressure Switch Stuck Open 30 Seconds or Longer After Call for Heat (System in 5-minute delay mode before next call for heat). On/off switch in "off" position during a call for heat will generate this code.
4 Flashes
Open Limit Switch or Limit Switch Circuit
5 Flashes
Flame Sense Signal Sensed Out of Proper Sequence
6 Flashes - pause - 1 Flash (see Note 1)*
Soft Lockout Type 1 (Failure to light within 4 trials for ignition)
6 Flashes - pause - 2 Flashes (see Notes 1 & 2)*
Soft Lockout Type 2 (Flame sense lost during run)
6 Flashes - pause - 3 Flashes (see Notes 1 & 2)*
Soft Lockout Type 3 (Pressure switch opened during run)
6 Flashes - pause - 4 Flashes (see Notes 1 & 2)*
Soft Lockout Type 4 (Limit or limit circuit opened during run)
6 Flashes - pause - 5 Flashes (see Note 1)*
Soft Lockout Type 5 (Flame has gone away after Error Code 5)
6 Flashes - pause - 7 Flashes (see Note 1)*
Soft Lockout Type 7 (Self-check failure)
10 Flashes* - SV9520H8034 only
Line Input Voltage Polarity Reversed
Dec 12, 2009 | Coleman Heating & Cooling
Meaning of rudd furnace trouble codes
Error Codes
stuck open)
stuck closed)
increases
Dec 12, 2009 | Heating & Cooling
Weathermaker 8000 furnance flashing code 31 blower comes on for 90 sec .. then shuts off .. then other fan goes on.. don't see any flames or lighting goin on can you help?
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than five minutes,
inducer shuts off for 15 minutes before retry. Check for: - Excessive wind
- Inadequate combustion air supply - Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used) - Restricted vent
If it opens during blower on-delay period, blower will come on for the selected blower
off-delay.
Nov 04, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...
Furnace won't kick on
Downstream of your fan discharge there is a little plastic assy. most likely that will have a pickup tube and a piece of vinyl or latex tubing attached. First check to make sure that the pick up tube and/or tubing does not have a restriction. If it is clean use an ohm meter to read resistance across the switch to verify it is operating.
Nov 15, 2008 | Intertherm Heating & Cooling
Heating & Cooling Logo
26 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen