Furnace blower fan stays on
Fan that moves hot air into house stays on after burner has reached temp
    Master:
  • 946 Answers
Gotta have some info..............is It a gas furnace?What brand?Model?
Fan switches do get stuck ON. Is it blowing ALL the time,cool air? don-ohio
Posted on Dec 31, 2016
1999 Goodman down draft natural gas furnace. It starts as normal, the burners fire and it warms up, but the blower doesn't start, after a couple minutes the burners shut down and the blower immediently...
IT SOUNDS LIKE THE FAN CYCLE RELAY OR BOARD IS NOT MAKING THE FAN COME ON WHEN IT SHOULD THE BURNER SHUTS OFF PROBABLY BECAUSE IT REACHES THE HIGH LIMIT.
Feb 03, 2015 | Heating & Cooling
My goodman furnacs says my limit switch is bad blower works but does not ignite .....? its modle gmt070-3 and where is it located
There are several limit switches in the unit there in various places in burner compartment. One on blower housing . One thing that I would try is replaceing your filter and turn the power off to the furnace and try starting the system after power is D/C for 5 minutes.
May 02, 2011 | Goodman GMS90703BXA Heater
Fan runs long after room reaches desired temp. heat goes off and fan continues to blow cold air, have a protech 520 thermostat
Is your 'Heater' you are talking about-- A furnace-- with a burner and a blower?
Either way-- We need to adjust a control that determines WHEN THE FAN RUNS--
Most furnaces have a section where the heated air collects, and there has to be a sensor in that chamber, that senses when that air is warm enough to circulate around--- and when the burner shuts off, the air in that area cools down, and the sensor should shut off the fan-
Can you find the Heated air area?-- and can you find a temperature control in that area?-- Can you adjust the control, so that it shuts off the fan when the air temp drops to 100- to 120 degrees F...
Tell us more about the type of furnace/heater we are workig with, so I can better help you-
Tell us more
Mack B
Jan 18, 2011 | Heating & Cooling
Furnace cuts off before reaching set temp.
You can make sure it is not the thermostat by crossing or jumping the R and W terminals (or associated wires) together. This will keep the furnace calling for heat. As it is approaching set temperature, get in front of the furnace and inspect the air filter to make sure it is clean, watch the control module for any error codes that may be turning off the system prematurely.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 07, 2010 | Honeywell Programmable Thermostat Heater
I have a GMP100 furnace and I replaced the control board because the blower fan wouldn't kick off now and then. It all works great but the main blower only stays on about 45 seconds after the burner turns...
Check the board for a set of dip switches. Check against the old board for switch positioning. These control fan on/off times. Ensure you turn power off before changing switch positions. If no dip switches,??
Dec 04, 2009 | Refrigerators
A 1979 Colman RV furnace. Blower shuts off shortly after burner shuts off leaving a hot heat exchanger. After 15 seconds blower comes on again blows for 10 seconds shuts off comes on in 15 seconds blows...
The fan limiting switch is acting up. It should stay running until lower temp is reached. It will cycle until the temp stays below or at the low setting. Limit switches are adjustable.
Jun 09, 2009 | Coleman Propane Forced Air Heater...
I have a comfort zone furnace. If it's 50 degrees in the house, and i set my thermostat to 70 or so,it takes at least 24 hours to reach 70 degrees. The furnace starts up and runs normally for about five...
When the thermostat calls for heat it should run until the room reaches the temperature setting then shut off. Is the blower motor running and can you feel air coming out of the vents? It sounds like the blower is either not running or putting out enough air to keep the furnace heating. The blower moves the heat from the heat exchanger to the room, if it can't remove enough heat from the heat exchanger there is a limit switch that will shut the burner off if it gets to hot and that's what it sounds like is happening.
Apr 25, 2009 | Heating & Cooling
Rheem gas furnace pilot lights, but no burners or fan
If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.
Jan 06, 2009 | Heating & Cooling
Heating & Cooling Logo
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen